Is my circuit overloaded?
Collapse
X
-
-
The wires could be for an internal thermal protective device or maybe even a dynamic brake. Maybe can you give the make and model number of the motor?_______________________________________________
_______________________________________________Comment
-
The plot thickens somewhat...
I tested the current draw and 1.8Kw+ motor only draws 500w when running. Could the loose wires have something to do with the low current draw?Comment
-
Induction motors or squirrel cage motors are generally at their most efficient when they're under full load, if they're free wheeling (no load) they often draw around 25 or even 30% of their full load current even though they're just rotating free and doing no useful work. Likewise the power factor of a motor usually improves as the load increases.
There's no hard and fast formula for off-load current draw, it very much depends on the individual motor but single phase motors have higher inefficiencies. If the saw was not actually cutting anything when you tested it then the power consumption of 500 watts would be expected._______________________________________________