The Electrical Certificate of Compliance explained

Collapse
This is a sticky topic.
X
X
 
  • Time
  • Show
Clear All
new posts
  • GCE
    Platinum Member
    • Jun 2017
    • 1483

    #136
    Hi Sean

    I am basically trying to say that make sure you don't just issue a COC for a building that has recently been built , past 10 years or so ( since 1992) , as it is possible that the installation was not done by a registered electrical contractor.
    The copy of the original COC should be available and you should just be issuing a retest , supplementary COC .
    By ticking existing installation and issuing a full COC you basically become the owner of the installation and the previous hidden funny's and contractor ride off into the sunset never to be bugged again.
    The original COC should be a live document that just keeps getting added to - It also takes the guessing out of the date of installation and amendments that apply.

    Comment

    • SeanM
      Bronze Member

      • Mar 2018
      • 120

      #137
      Morning GCE

      Thank you and agreed, It would be really good if we had more electricians on the same page.

      Comment

      • Opro
        Email problem
        • Feb 2019
        • 1

        #138
        I am buying a farm. Eskom has been disconnected. The electrical installation in the house is chaos. I don't want to re-connect Eskom. I am willing to accept the house as voetstoots (as is) without electricity. How do I legally go about to buy the farm without a valid COC?

        Comment

        • GCE
          Platinum Member
          • Jun 2017
          • 1483

          #139
          Hi

          If the is no supply then there can be no COC issued for the farm
          If there is a generator that is used to power the installation then you will need a COC with the generator as the point of supply

          It is possible for the seller to hand over the responsibility of obtaining the COC to the buyer - If the written acceptance is sent in with the transfer it seems that it is accepted.
          We had a similar case recently on a commercial building

          Comment

          • ELECT 1
            Full Member

            • Dec 2013
            • 78

            #140
            COC"s who is who in the zoo.
            We have short and easy to fill in and then long and complicated , where you have to state the same
            stuff multiple times for what....This DOL form was designed by who ???
            I think the designers should sit down with the guys that have to fill in the form
            and get rid of some of the nonsense.
            If you install just one plug, you have to go through a form thats a mission to fill in....there has to be
            a simplified version .Click image for larger version

Name:	IMG_20190520_130447.jpg
Views:	1
Size:	54.1 KB
ID:	265658
            Now i got that off my chest

            Comment

            • GCE
              Platinum Member
              • Jun 2017
              • 1483

              #141
              Via the grapevine , I hear that there is a one page version coming along that will make life easier for the small jobs.

              Comment

              • Rosem
                New Member
                • May 2019
                • 3

                #142
                Thank you Sparks!

                Originally posted by Sparks
                I hope this will help the non-electrical trade people who pop in to try make sense of the COC:

                Unfortunately, confusion reigns as many people simply do not understand the law, and many more have an opinion on the matter that have no credibility as to the facts. In order to clarify the issues I will attempt to go back to the basics and explain the requirements.

                Where do you start?

                When you contract an Electrician ask him for a copy of his Wireman's Licence, and a copy of his DOL Registration Certificate, don’t let him just show some paperwork that in any event will mean nothing to you. When you have these copies phone your national office of the DOL and CHECK that you are dealing with a Registered Electrician. Most important is to check the electrician’s credentials before any work is undertaken on your property.

                How does someone become a Registered Electrician

                When the Electrician has passed his (NTC 3), he would then be allowed to do his trade test.

                If successful the Electrician would then be known as “Qualified”, but he would not be a Licensed Electrician. To become Licensed Electrician, a Qualified Electrician would have had to write and pass an exam on “Electrical Installation Regulations”.

                When all this is done and the Electrician has served the appropriate time and passed all the examinations and Trade test the Qualified Electrician will be issued with a Licence from the Department of Labour.

                If the now Qualified and Licensed Electrician wants to work as an Electrical Contractor he must further register with the DOL as a Registered Person. Please note that this registration must be redone every year.

                As a Registered Person this Electrician can now issue Electrical Certificates of Compliance (CoC). No other person other than a Registered Person is allowed to issue Certificates of Compliance.

                There are three categories of a Registered Person.

                A. Electrical Tester, who can work on a Single Phase installation Basically a normal house supplied with 220 Volt electrical supply
                B. Installation Electrician who can work on a Three Phase installation. Normally buildings and factories supplied with 380 Volt three phase supply
                C. Master Electrician for Hazardous Locations, basically petrol stations, mines, flammable areas.

                An Electrical Tester cannot issue a (CoC) for a Three Phase installation. An Installation Electrician can issue a (CoC) for a single phase installation but not a Hazardous Location, and a Master Electrician can issue a (CoC) for any of the above installations.

                You now know what a Registered Person is. He is not simply someone that has a good idea of what to do, and he is certainly not a “Handyman” that professes to be a “Jack of all Trades”

                What are “Electrical Installation Regulations?”

                As stated before, part of the qualification process is that an Electrician must pass the exam on “Electrical Installation Regulations” these regulations are actually the “Bible” relative to how an electrical installation shall be installed.

                These regulations are the “Code of Practice” for Electrical Installations namely, The South African National Standard SANS 10142 - for The Wiring of Premises.


                SANS 10142 is concerned with the basic safety of Electrical Installations. To ensure the protection of people, animals and property and the proper functioning of a fixed electrical installation, the aim is to ensure that protection from hazards that can arise from the operation of an electrical installation under both normal and fault conditions.

                An electrical installation has to provide protection against

                - Shock Current
                - Over Current
                - Fault Current
                - Over voltage
                - Under Voltage
                - Excessive Temperatures
                - Electric Arcs

                If any of the above arises, the protection should automatically disconnect the supply or limit currents and voltages to safe values. In the case of under voltage, the protection should ensure that dangerous situations due to the loss and restoration of supply (for example to a motor) or due to a drop in voltage cannot occur.

                The code only covers the electrical installation and the circuits feeding fixed appliances, but does not cover any appliances, for example stoves, geysers, air conditioning and refrigeration plant.

                What makes the Electrical Installation Regulations Law

                The Occupational Health and safety Act, 1993 (Act No. 85 of 1993) (OHS Act), which is administered by the Chief Inspector of Occupational Health and safety of the Department of Labour, requires that electrical installations comply with the requirements of SANS 10142. It also requires that a registered person, as defined (Master installation electrician, installation electrician or electrical tester for single phase), will issue a Certificate of Compliance together with a test report.

                The certificate shall be in the form of the Certificate of Compliance published in the Electrical Installation regulations, and the test report shall be in the form of the test report published in the Electrical Installation regulations.``


                What is a Certificate of Compliance

                The Certificate of Compliance (CoC) is a declaration by the registered person that the electrical installation has been carried out in accordance with the requirements of the Occupational Health and Safety Act, 1993 and the regulations hereunder.

                It is important to note that if you have a valid (CoC) it must be kept at the premises that the (CoC) relates to .In many cases they end up with Estate Agents, Conveyancing Attorneys or Banks.

                If the (CoC) is valid and work is done to the system after the (CoC) was issued, a new (CoC) must be issued BUT only for that part of the installation where additional work was done to the electrical system. The additional (CoC) must be filed with the original and kept on hand if and when required by any inspection authority.

                If any part of an electrical installation does not comply, the registered person cannot issue a (CoC)

                No alterations are permitted on a (CoC)

                Only a registered person may issue a (CoC)

                What is a Test Report

                The Test Report contains all the specific details of the electrical installation. It is a comprehensive record of exactly what forms part of the installation inclusive of specific tests in relation to readings and test instruments used. The test report should further contain diagrams and if necessary photographic evidence of the installation as tested.

                The test report must accompany the (CoC)

                Who must have a Certificate of Compliance

                According to Regulation 7 (1), of the Occupation Health and Safety Act, 1993, every user or lessor of an electrical installation, as the case may be shall have a valid (CoC) accompanied by a test report, in respect for every such electrical installation.

                In simple terms every property owner or alternatively person renting a property must have a valid (CoC), furthermore should an inspector of the Department of Labour or supply authority or approved inspection authority request the (CoC) a valid (CoC) must be produced.


                Selling Property and the role of the Certificate of Compliance

                The (OHS) Act goes further to state that no machinery (an electrical installation is defined as machinery) may be sold unless it complies with the prescribed safety requirements. The (CoC) is the only accepted and endorsed proof of that compliance.

                The Occupational Health and Safety Act has always determined under Section 22 that a property cannot be offered for sale unless a valid (CoC) is in place.

                Section (5) of the new Electrical Installation Regulation (R242) 6 March 2009, further states that the validity of a (CoC) cannot exceed (2) two years, therefore it is the responsibility of the User or Lessor of an electrical installation to ensure that the (CoC) is not older than two years.

                The (CoC) document has been formulated by the SABS, with stakeholder input, and accepted by the Department of Labour as being indicative of the safety standards to be applied. For this reason, the majority of property sale agreements stipulate that a seller must provide the buyer with a valid certificate of compliance.

                A seller doing so can be comfortable that the electrical installation is safe and compliant, in turn giving the buyer comfort and assurance that all is well with the electrical installation. It’s to the advantage of the agent as well to know that there will be no delays in processing the offer to purchase and transfer documentation.

                It is recommended that an inspection of the property be carried out before buying or selling process to ensure there are no surprises later on. A seller may claim that no alterations were done to the electrical installation and that their (CoC) is valid, but the truth is that even minor electrical work such as fitting a ceiling fan, new oven, extractor fan, new light fittings or replacing faulty plugs can render an existing (CoC) null and void.

                A home buyer or a lessor can now insist on seeing a valid (CoC) upon their viewing a property for sale or rent and before they sign any agreements or Offer to Purchase.

                Department of Labour should be cracking down on AGENTS and SELLERS who contravene the law.

                Sectional Title Property and the Certificate of Compliance

                When a person buys into a sectional title property the buyer needs to additionally establish if a valid (CoC) is also in place for the “common” property, covering, lights, gate motors, pool pumps and any other electrical equipment that forms part of the “common” property.

                Should the “common” property not have a valid (CoC) the Body Corporate can be held criminally liable should there be any incident related to the electrical system on the “common” property.

                Rental Property, Lodges Hotels and Caravan & Camping Sites

                It is a legal requirement that if you are renting any property that encompasses an electrical installation that such an installation must have a valid (CoC).

                Letting agents are known to “slip in” clauses that make the electrical installation the responsibility of the tenant. Please be aware of this and read your contract carefully.

                When it comes to Lodges, Hotels, Caravan and Camping Sites the facility concerned must have a valid copy of the (CoC) for each room or site, the tenant or guest is entitled to request a copy of the (CoC) prior to taking occupation of the room or site.
                Advertising and or marketing of an establishment that is non compliant, will be in breach of Section 22 of the Act.
                There is a possibility that The Tourism Grading Council as well as AA Recommended Destinations will have to be re accredited taking the requirements of The Occupational Health and Safety Act into account.

                Requirements relative to Certificate of Compliance and Selling Property

                Regulations should have a huge implication on the Real estate industry. It should mean that AGENTS seeking mandates from property sellers will have to request an up-to-date (CoC), if they want to stay on the right side of the law.

                Nobody including agents may market a property that does not have a valid (CoC)

                Sellers and Buyers would be well advised to use their own registered electrician to supply a (CoC)

                The Buyer is able to report both the Agent and the Seller to the authorities if the property is being marketed without a certificate.

                Insurance

                It must be noted that an insurance claim resultant from a fire or injury caused directly or indirectly by negligence and non compliance to the requirements of the Act, may result in the claim being repudiated.

                Plumbers

                It is advisable to have the plumbing also certified, but that is another domain altogether, however it has been common practice for plumbers to interfere with the electrical wiring when replacing geysers, very often the (CoC) is invalidated by their actions.
                THEY ARE NOT QUALIFIED ELECTRICIANS, IF A PLUMBER REPLACES YOUR GEYSER ASK HIM FOR AN ELECTRICAL CERTIFICATE FOR THE REPLACEMENT OF THE GEYSER


                TV Aerials and Satellite Dishes

                Many people do not know that it is a requirement of SANS 10142 that TV Aerials and Satellite Dishes must be earthed.
                TV Aerials and Satellite Dishes, do form part of the electrical test and should they not be earthed a certificate of compliance cannot be issued.

                Replacement of Lights Fittings and Socket Outlets

                Please remember that when replacing any part of your electrical installation you must ensure that such replacement items comply with the relevant SANS codes, many spares that are available from the large hardware wholesalers are cheap imports that do not comply to South African Standards, light fittings are particularly suspect when it comes to compliance. Ask your supplier for proof that the item complies with South African standards.

                I trust the COC is somewhat less of a mystery now to buyers and sellers alike.


                Hello Sparks, You're the reason I signed up to this forum. I didn't know it existed until I did a search for information on the Certificate of Compliance, and found your excellent post. I wanted to thank you for posting it, so, thank you very much. I have had a nightmare experience since an electrical emergency began late on the 7th May, and much of the blame for my angst can be laid at my door, unfortunately. Before I venture any further, I feel I should ask first if you would be prepared to answer other questions I have relating to my on-going disaster, as it seems that you are an experienced Electrician and I need all the help I can get. If you're not keen, no problem, I will respect your wishes and look elsewhere. Kind Regards, Rosem.

                Comment

                • Rosem
                  New Member
                  • May 2019
                  • 3

                  #143
                  Hello Sparks, I missed the +Reply to Thread at the top left of the page, and was trying to reply to your post using the reply button which didn't work. I then tried the Reply with Quote which allowed me to submit my message, but I don't know if this will have been received by you as I don't see it anywhere in here. Now, back to my message. Sparks, you're the reason I signed up to this forum. I didn't know it existed until I did a search for information on the Certificate of Compliance, and found your excellent post. I wanted to thank you for posting it, so, thank you very much. I have had a nightmare experience since an electrical emergency began late on the 7th May, and much of the blame for my angst can be laid at my door, unfortunately. Before I venture any further, I feel I should ask first if you would be prepared to answer other questions I have relating to my on-going disaster, as it seems that you are an experienced Electrician and I need all the help I can get. If you're not keen, no problem, I will respect your wishes and look elsewhere, but I am at the end of my tether with whom I believe is an unlicenced, pushy Electrician. Kind Regards, Rosem.

                  Comment

                  • Derlyn
                    Platinum Member
                    • Mar 2019
                    • 1761

                    #144
                    There are already one page COC's available like those that are found inside a purchased ready box. Are those worth the paper they are printed on ?

                    Derek

                    Comment

                    • reggy
                      New Member
                      • Jun 2015
                      • 8

                      #145
                      hi Sparks
                      I need to prepare for units standard at a training centre , so do you have some few question papers they normally ask during assessment. if you have please provide

                      Comment

                      • Sparks
                        Gold Member

                        • Dec 2009
                        • 909

                        #146
                        I am afraid you are asking the wrong person🤣the book has been redone twice since I wrote. Feel free to make use of the site search block. The questionaires are regularly provided by people as they do the latest exams.

                        Comment

                        • ians
                          Diamond Member

                          • Apr 2010
                          • 3943

                          #147
                          Originally posted by Rosem
                          Hello Sparks, I missed the +Reply to Thread at the top left of the page, and was trying to reply to your post using the reply button which didn't work. I then tried the Reply with Quote which allowed me to submit my message, but I don't know if this will have been received by you as I don't see it anywhere in here. Now, back to my message. Sparks, you're the reason I signed up to this forum. I didn't know it existed until I did a search for information on the Certificate of Compliance, and found your excellent post. I wanted to thank you for posting it, so, thank you very much. I have had a nightmare experience since an electrical emergency began late on the 7th May, and much of the blame for my angst can be laid at my door, unfortunately. Before I venture any further, I feel I should ask first if you would be prepared to answer other questions I have relating to my on-going disaster, as it seems that you are an experienced Electrician and I need all the help I can get. If you're not keen, no problem, I will respect your wishes and look elsewhere, but I am at the end of my tether with whom I believe is an unlicenced, pushy Electrician. Kind Regards, Rosem.
                          I believe you did find the correct channels to follow and been to the AIA Mark Palmer and then redirected to the KZN AIA...I hope you manage to get this problem sorted out.

                          Feel free to post your questions...there are numerous members of this platform who are more than capable of answering your questions...posting questions also helps other people who are in the "dark" with regards laws with regards to electrical installations.
                          Comments are based on opinion...not always facts....that's why people use an alias.

                          Comment

                          • Sparks
                            Gold Member

                            • Dec 2009
                            • 909

                            #148
                            Thank you ians for your reply, I agree 100%. My time is limited so it will be much quicker to post questions here, besides, there are a number of members better qualified than myself and with more experience whom I have come to trust here.

                            Comment

                            • jvdh
                              New Member
                              • Aug 2019
                              • 3

                              #149
                              I wonder if somebody can help me. I am an electronic technician and sometimes do control-panels for a business that install water plants. Its mostly control of 24 VAC valves and small pumps (never more than 2 Kw) We did an installation and now the client wants a COC. I am not registered to issue a COC but asked a electrician who is registered, and he told me a COC cannot be issued for a panel. He told me a COC stop at the supply to the panel.

                              My questions now is:
                              - If a COC cannot be issued on a panel, what can I offer the client or must I just tell him a COC cannot be issued?
                              - I did the installation of the two small pumps as well. Do one need to supply a COC on the installation?

                              Thank you in advance!

                              Comment

                              • GCE
                                Platinum Member
                                • Jun 2017
                                • 1483

                                #150
                                I have been asked the same question on numerous occasions and managed to get an answer from the Deputy Director for Electrical at the DOL .
                                I have pasted the question (in red ) and answer ( in Blue) below .
                                Hopefully it will assist

                                Further to the telephonic discussion .

                                I had another call querying the COC in a factory and the Health and Safety officer in the factory insisting that the electrical contractor issue a COC for the Machine , similar to the previous enquiry.

                                We all quote the electrical regulation about the COC stopping at the terminals of the machine.

                                We need to know what the factory owner needs to do to cover himself to ensure that if somebody gets hurt on the machine he can show that he has complied .At the moment besides saying you need to comply to General Machinery Regulations he is still wanting a piece of paper that covers him.

                                The other problem is that when these machines come in from outside of the country – Can the factory owner accept the certificates made out under the IEC codes.

                                This is a problem that is coming up frequently and it would be useful if we could obtain some sort of practice note or guidance from DOL


                                Dear Sir,

                                The electrical installation stops at the supply terminals of the machine. In the case of an unit for a specific purpose, the electrical installation will stops at the the supply terminals for that unit.

                                The competent person in terms of the General Machinery Regulations must take responsibility for the machine. In some cases, we do have specific requirements for machines, such as lifts, escalators, refrigeration plants, etc. where such machinery must comply with specific standards.

                                People like to shift their responsibilities to other people. The employer must do a risk assessment in terms of section 8 when they are using machinery, so as the manufacturer and importer in terms of section 10.

                                Comment

                                Working...