    #196
    Originally posted by Gamatwp
    Good evening all, I have a Coc related question... not sure if this is the right thread.

    I will be issuing my 1st Coc for an installation of a prepaid meter Base and wanted to know:

    If section 2 and 4 needs to be filled in?

    Thanks in advance
    Simple answer ....... No. Sections 2 and 4 do not need to be completed.
    Describe in section 3 the part of the installation covered by your COC.

    You will be issuing a supplementary COC and you have to refer to the existing COC, quoting it's number and date of issue.
    If there is no existing valid COC for the installation, then it is not possible to issue a supplementary COC.

    Cheers and peace out
    Derek

    Comment

    • Leecatt
      Silver Member
      • Jul 2008
      • 406

      #197
      Originally posted by Derlyn
      Hello brother

      Could you maybe inform us what section 9.2.(c).(i) says.

      SANS 10142-1 edition 2 ends at 8.7


      Cheers and peace out

      Derek
      Hi Derlyn, I was not referring to SANS.
      Read my post again

      Sent from my SM-A705FN using Tapatalk
      To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

      Comment

      • Leecatt
        Silver Member
        • Jul 2008
        • 406

        #198
        Originally posted by Derlyn
        Simple answer ....... No. Sections 2 and 4 do not need to be completed.
        Describe in section 3 the part of the installation covered by your COC.

        You will be issuing a supplementary COC and you have to refer to the existing COC, quoting it's number and date of issue.
        If there is no existing valid COC for the installation, then it is not possible to issue a supplementary COC.

        Cheers and peace out
        Derek
        You are almost correct.
        If there is no VALID coc then it is not possible to issue a supplementary vic.
        There is only one way to determine whether an existing coc is valid.

        Sent from my SM-A705FN using Tapatalk
        To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

        Comment

        • Gamatwp
          Junior Member
          • Oct 2015
          • 11

          #199
          Hi

          Is theres is no current COC... very old house.

          Im just adding a Coucil Prepaid Meter Base....

          It will be initial certificate, in this regard is it still fine to leave section 2 and 4? Since the coc is for the base of meter and not for house.

          Comment

          • Derlyn
            Platinum Member
            • Mar 2019
            • 1761

            #200
            Originally posted by Leecatt
            Hi Derlyn, I was not referring to SANS.
            Read my post again

            Sent from my SM-A705FN using Tapatalk
            Hello Brother

            Have read it again but don't know which Electrical Installation Regulations you are referring to, if not SANS 10142-1.

            That's why I enquired.

            Derek

            Comment

            • Leecatt
              Silver Member
              • Jul 2008
              • 406

              #201
              Here it isElectrical Instalation Regulation (1).pdf

              Sent from my SM-A705FN using Tapatalk
              To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

              Comment

              • Derlyn
                Platinum Member
                • Mar 2019
                • 1761

                #202
                Originally posted by Leecatt
                Here it is[ATTACH]7746[/ATTACH]

                Sent from my SM-A705FN using Tapatalk
                Thank you, brother.

                Cheers and peace out

                Derek

                Comment

                • Gamatwp
                  Junior Member
                  • Oct 2015
                  • 11

                  #203
                  Originally posted by Derlyn
                  Simple answer ....... No. Sections 2 and 4 do not need to be completed.
                  Describe in section 3 the part of the installation covered by your COC.

                  You will be issuing a supplementary COC and you have to refer to the existing COC, quoting it's number and date of issue.
                  If there is no existing valid COC for the installation, then it is not possible to issue a supplementary COC.

                  Cheers and peace out
                  Derek
                  HI, thanks i understand that it doesnt need to be filled out.

                  But is it fine that this initial COC wont have section 2 and section 4 filled out.

                  Thanks in advance

                  Comment

                  • Derlyn
                    Platinum Member
                    • Mar 2019
                    • 1761

                    #204
                    Originally posted by Gamatwp
                    HI, thanks i understand that it doesnt need to be filled out.

                    But is it fine that this initial COC wont have section 2 and section 4 filled out.

                    Thanks in advance
                    My brother

                    If there is no existing COC for the installation then you will have to issue an initial COC even although you only installed the meter base.
                    You will have to do inspection & testing of the whole installation and satisfy yourself that it is reasonably safe. You will then have to complete ALL the sections on the test report.

                    Cheers and peace out
                    Derek

                    Comment

                    • SeanM
                      Bronze Member

                      • Mar 2018
                      • 120

                      #205
                      Greetings All

                      I recently went to a customer that had all of their equipment blow due to a surge during load shedding and I mean everything.

                      I repaired and installed surge arrestors in the DB board (note: three phase DB so four surge arrestors). It was a samite DB and with these types of surge arrestors they have an indication light which is green to indicate there status. Normally the surge arrestors with the phases on, the indicator light is on and the neutral surge arrestor light is off (I understand this) in this particular instance all indicator lights are on even the neutral. I have tested the voltage on the neutral and it is 0 volts.

                      Anyone had a similar issue?

                      Comment

                      • ians
                        Diamond Member

                        • Apr 2010
                        • 3943

                        #206
                        Originally posted by SeanM
                        Greetings All

                        I recently went to a customer that had all of their equipment blow due to a surge during load shedding and I mean everything.

                        I repaired and installed surge arrestors in the DB board (note: three phase DB so four surge arrestors). It was a samite DB and with these types of surge arrestors they have an indication light which is green to indicate there status. Normally the surge arrestors with the phases on, the indicator light is on and the neutral surge arrestor light is off (I understand this) in this particular instance all indicator lights are on even the neutral. I have tested the voltage on the neutral and it is 0 volts.

                        Anyone had a similar issue?
                        A lot of this type of thing happening... the best part is the insurance companies have got wise... they no longer cover power surges caused by neutral bar theft and "Eskom" power surges... Had similar experience were the lightning protection is blown to pieces and others where the lightning protection is in place and electronic components are blown to pieces.
                        Comments are based on opinion...not always facts....that's why people use an alias.

                        Comment

                        • W-TDMI
                          Full Member
                          • May 2013
                          • 39

                          #207
                          Hi SeanM. What procedure dud you follow to determine the 0V on the Neutral. Sometimes the guys make the mistake to test it between N and Earth where you actually will get 0V because indirectly its the same point - star point of the TRF. Did you test from N to external Earth - like one lead in die grass or garden? Normally the must be a flow at least even if its only a deflection but its should show a value.
                          ~INSPECT, TEST, VERIFY, CERTIFY~

                          Comment

                          • Pieter00
                            Bronze Member
                            • Mar 2013
                            • 112

                            #208
                            Where can i get a new annexure 3 to renew my registration at Dept of Labor? the one on their websites are apparently outdated

                            Comment

                            • W-TDMI
                              Full Member
                              • May 2013
                              • 39

                              #209
                              Originally posted by Pieter00
                              Where can i get a new annexure 3 to renew my registration at Dept of Labor? the one on their websites are apparently outdated
                              Hi Pieter you ate more than welcome to download from our website under supporting docs. www.tdmi.co.za All the best.
                              ~INSPECT, TEST, VERIFY, CERTIFY~

                              Comment

                              • ians
                                Diamond Member

                                • Apr 2010
                                • 3943

                                #210
                                I finally figured out why this industry is so F^&*d and people just couldnt be bothered to take steps to sort out illegal COC's.

                                I bumped the back of my van ...because i now only have one vehicle (thanks to owing the tax man a ton of cash ...had to sell the others to pay an outstanding balance) so i contact the insurance company who inform me to take my vehicle to the panel beater for a quote which i did ...i make arrangements with the panel beater to drop off the vehicle and collect it 3 days later (quote for repair R55000.00)

                                Everything is organised prior to the vehicle going in for the repair...right down to an sms confirmation that the window guys will replace the window at a specific time...well 3 days later thinking everyone is on track... i arrive to collect ...the window people (auto boys) didnt pitch up at 8 am like they were suppose to after 8 confirmed calls and an sms...never mind the fact that the window is a pirate part so now the wiper does actually wipe the window for what ever reason

                                Anyway back to the reason... i am at that point with the insurance and panel beaters and glass fitment companies that i actually just dont give a F^&* anymore ...it works i am just gona leave it... the fact that the back door doesnt line up ...the window doesnt fit in the the door properly... the paint job is a mess ...the over spray on the vehicle hasnt been cleaned off... there are parts missing on the door... they have used second hand parts and charged for new... the list just goes on and on ...and we are just talking about a simple back door replacement and spray.

                                The problem is that there are too many people with too many fingers in the claim trying to get their cut... the panel company only sprays the parts ...the insurance company supplies the parts ...the broker has a contact who fits the window... and us as the customer must just suck it up and take the shyte as it comes.

                                I am at that point where i am sure most people get with regards to illegal COC's ..it just becomes too much of a headache and too expensive to claim...so they just leave it.

                                Handling an illegal COC is a lot more complicated than just returning your vehicle to be repaired and there is no cost to me ...YOU PAY TO FIX THE ILLEGAL COC ISSUED AS THE BUYER...so lets get this right...you buy the house and have to foot the bill to get the illegal COC issued with your new home sorted...not only the inspection ...you also have to pay out your own pocket to have it fixed ...then claim it back form the electrical inspector... i am yet in al the year si have been doing this heard of one electrical inspector actually paying out a claim.

                                A word of advice... if you plan to buy a house...wait until the transfer is about to go through ...at this point ...put the transfer on hold until you have had a second opinion (even if the test cost R1000) it will save you thousands if the house is not up to standard ...there are too many "buddies" issuing COC's ...this week again ...another house was purchased the customer noticed a few strange things got an electrician to check it out... it turns out the inspector had not even visited the site ...the COC was not filled in correctly and there are huge repair costs involved.

                                The house i was renting prior to purchasing was sold while i was living there....a person (not even sure that he was a qualified electrician) arrived at the house with a 6 " gallery and handful of nuts and bolts ...he informed me he was there to do repairs and check the house...When i asked about the testing procedure ...i was told the person who issues the COC lived in stanger and couldnt make it ...so the person on site said he would just fix a few thing and check it was ok ...When he was finished he indicated everything was fine and he would tell the person in stanger it was ok to sign off...the test results used would just be the standard ones we normally use to indicate the house is "reasnably" safe.

                                This people is what is going on in this industry... wake up... dont be that fool who blows a million bucks on a property and then have to spend R50 000.00 fixing up all the electrical problems.
                                Comments are based on opinion...not always facts....that's why people use an alias.

                                Comment

                                Working...