Generator connection
  • ACEsterhuizen
    • Mar 2012
    • 165
    #46
    Its Friday....
    True Story...
    • Sparks
      • Dec 2009
      • 909
      #47
      Yes it is, all day. Let's clear the air. Rohann van Zyl is actually Afrikaans, that explains some of his post. The rest of my comment still stands however. If a person does not know the reason the ELCB tester does not trip the ELCB then I have no choice other than to doubt their credentials. In light of this there is no way that I will assume that the "mains supply" which he refers to is from a 20A circuit breaker, especially when specific reference is made to "mains supply". Rohann as well as any other Afrikaans speaking people are welcome to search for "eresme" on Skype if they wish to converse in Afrikaans which will certainly eliminate misunderstandings caused by translation.
      • DieterT
        • Oct 2014
        • 126
        #48
        So all in all I feel this discussion of DYI should be made into a new thread as it is a very important aspect to discuss and to be clear about. If only our country could have created a DYI regulation as what NZ has done and to say where the client needs to get a registered person. Anyways back to generators.
        • DieterT
          • Oct 2014
          • 126
          #49
          Are we all in agreance of the fact that a generator connection requires a switch over that breaks phases and neutral with indication on db boards supplied by generator.
          Also that a neutral earth bridge is required at generator point of connection and properly labeled as such.
          Further more a circuit breaker on generator supply in order to protect against short circuit and overload conditions.
          Also a valid CoC for the installation of alternative supply.
          A application form seems to be only required by certain manucipalities, maybe some of you could elabirate more on that.
          Further more with plug in generators for us the registered electricians. This is not some law in the OHSA nor in the SANS10142-1
          This is something I believe in and from many conversations with other professionals "ECSA registered engineers" and the electrical inspector for Gauteng I feel and it should be required of us professionals to best possible advise the client and also not to leave the client in a position that he can cause possible harm or damage to property or harm to himself or other persons.
          This having been said due to the plug in generator, since the generator plugged in is CoC'd as its feeding the load as alternative supply thus the load must be compliant with the supply and vice versa (PSCC, loop impedance etc.)
          Now the client buys a new generator or that generator is serviced, maybe rewound some changes come due to this then this is used again as alternative supply since the plug in point is provided.
          It could cause problems which the client is not aware of or who ever comes after him. This then is the responsibility of the professional to make sure that this could not happen.
          There for in my opinion and take it only as that, that a connection must be installed where the generator is physically connected to with the earth/neutral bridge inside, thus when generator is removed or replaced an electrician needs to come and do so then also with new generator or rewound/repaired generator do new CoC.
          Thus having to use a tool to remove and connect generator is then within regulations as a layman is not allowed to do so just as with any other connection, but with plug in point that changes completely...
          Any sound advise or comments on this is welcomed and please don't come with bullshit like "then its the client's own responsibility" and " the regulations protect me from responsibility"
          At the end of the day I don't want any one's death on my hands, nor law suits at my back. I believe it is my responsibility as an professional even thou the regulation can so be munipulated to edemnify me from responsibilty, that I must ensure the safety of human beings, animals and protection of property against fire and short circuit damage.
          Excuse my spelling mistakes as I am laying in hospital awaiting a back opp and not using google spelling mistake correction.
          I look forward to other opinions on this and also for everyone to offer clarity on generator connections and installations.
          • Sparks
            • Dec 2009
            • 909
            #50
            I agree Dieter, unfortunately there are way too many "electrical assistants/appys'" running around making hot connections along with DIYers. Many sparkies put their client's safety above the buck but unfortunately once again the clients are more concerned about saving the buck. I refuse to sign off any COC unless I am satisfied that the installation is either compliant or safe as applicable. All the best with your back op.
            • DieterT
              • Oct 2014
              • 126
              #51
              Thnx Sparks. Yes and that is the attitude all sparkies should carry around. Don't sign the certificate if it does not comply. But unfortunetly there are a lot of desperate sparkies out there who would turn the blind eye for some extra cash in his pocket.
              • SilverNodashi
                • May 2007
                • 1197
                #52
                And quite often they're more expensive as well!
                • Matt_k
                  • May 2015
                  • 3
                  #53
                  Hi Guys,
                  Most of you seem rather knowledgeable, so I'd like to garner your opinion regarding grounding of a portable generator.
                  I recently purchased a Kipor IG2600 (2.6Kva) Digital Inverter gennie as I want to power things like our entertainment system, or my desktop PC etc. Now I have tested it and it all works swimmingly well. The Digetal Inverter type generators cost quite a bit more than your builders 'special' generators, and have AVR, Overload etc. I would like to believe that they quality of the components is of a good quality since I paid a bit of a premium. Other than the quality aspect, main reason that I bought it is because I stay in a complex and noise is an issue so wanted the quietest (within budget) generator available as so not to disturb my neighbours.
                  Now my main question I have for you brainiac's is what options do I have regarding grounding of my generator? I have read about ground spikes etc, but info is a bit slim online in SA, and parts for that matter as well. Also since I have a new house in a complex, building rubble is abundant in my garden, so driving a 2.4m copper rod into the ground might prove somewhat challenging...
                  Is it possible to ground it to the water pipes perhaps? I know I have a garden tap outside which appears to have a metal pipe running up the wall out of the ground, so was considering this (if the pipe is copper). If possible, I would prefer to try and do the installation myself within reason, as I have gotten some quotes from some electricians in my area for a Manual Transfer switch installed, and the amounts where laughable... One wanted to charge me R7995 for just a switch mounted with a plug right at my DB board in the garage which I'm pretty sure is daylight robbery.
                  I know it won't power the house and as mentioned before it doesn't need to, just would be easier to isolate the circuits I want (LED lights and lounge plugs) for the DB switch. But for now I'd settle just to sort out the Grounding so I know it is safer. I am not an electrician, i'm just a normal guy that likes to do his own DIY.
                  Just a FYI with the generators, in my manual it was quite handy at showing the power loss for the generators at altitude. It stated for every 305 meters above sea level, your gen will lose 3% ( if I remember correctly, will check tonight). Plus then you lose some more for temperature as well, so make sure when buying a Gen, that you have about 20 - 30% in reserve of what you actually need on the highveld because of those losses to be safe.
                  Thanks again,
                    • 4927
                    #54
                    I'd suggest you refer back to the suppliers because I suspect this generator is not suitable for connection to a DB. Page 13 of the manual 'Do not connect the generator to a household circuit. This could cause the damage to the generator or to electrical appliances in the house.'
                    • Matt_k
                      • May 2015
                      • 3
                      #55
                      The manual does mention that it can be connected to the house via a Manual Transfer Switch, but that aside, do you have any thoughts about the grounding of said generator? out of interest, with new complexes these days, what seems to be the norm when it comes to grounding? (in general from your experience)
                        • 4927
                        #56
                        The problem is that with your Eskom supply the neutral and the earth are connected at source. With the AVR output from the generator there is no neutral as such, both output wires are effectively lives and neither are connected in any way the the 'ground' terminal on the generator body or frame.
                        What this means is that if you connect it to your DB via a transfer switch the neutrals of the circuits in your house effectively become live. Just some of the problems this raises are that overload protection devices (circuit breakers) in you DB only protect the live of the circuits, with the generator supplying the installation it's possible to get overload faults on the neutral which won't trip. Also the sockets in your house will only have a switch that disconnects the live of the supply circuit, again this means that the 'neutral' which is now actually another 'live' is not disconnected. Same with applianxces, most on/off switches only control the live not the neutral.
                        TS Bulletin 2013-006.pdf
                        Even the service agents seem to get confused about generator output configurations.
                        The list of problems goes on but the bottom line remains the generator isn't safe to use as a permanently installed back-up supply. If you do connect it to your DB and someone gets injured or killed you'll be the responsible person. Use it as it was intended with extension leads and with the ground terminal on the frame of the generator connected to an earth rod.
                        • Matt_k
                          • May 2015
                          • 3
                          #57
                          Thanks AndyD, yeah I will just use the extension cord then. I have a 25A outdoor cable so it is properly rated for anything that the generator can throw at it.
                          Regarding the grounding, where can I find a ground rod, or is it possible to ground it to the water pipe or something? As mentioned, since my garden has quite a bit of building rubble in the soil the ground rod of 2.4m might be a slight problem.
                          Thanks,
                            • 4927
                            #58
                            You can buy earth rods at any electrical wholesaler but if you use these you'll need to test how effective that earth is after you've knocked them in which is a bit tricky without the proper test equipment. The water pipe bonding isn't ideal, again you'd need to test it first.
                            I'd suggest connecting to the main earth terminal of the house if it's accessible. If the house was recently built there might be an earth terminal above the ceiling or somewhere around the DB which is specially provided for other services.
                            • Paul Sabatier
                              • Jul 2015
                              There is a previous topic http://www.theforumsa.co.za/forums/s...rth-connection
                              • JacquesPN
                                • Jan 2016
                                • 7
                                #60
                                Just to clarify the LAW.
                                Hi Andy,
                                I agree with you on your statement as far as a large generator is concerned however, what we are doing here in Jhb, is installing a 5.5KVA genny, with a manual change over switch, connected to the DB board, BUT, we isolate a number of circuits only which are connected to the generator. Usually lights, fridge circuit and entertainment circuit.
                                Basically during a black out, the user starts the genny via a key switch on the genny, as most 5.5Kva have an electric start, once running, they change the switch manually to genny, have power during the black out, and when the power returns, they simply change over back to mains, switch the genny off and wait for the next one.
                                This makes it safe for any one to use, and due to the simplicity can even be done by the home manager if required during the day.
                                What you are doing is actually in almost every case illegal and very dangerous.
                                Most generators under 12Kva are PNP devices meaning that if you measure between the L-E you will get 115VAC, N-E 115VAC and L-N 230VAC.
                                SANS is very clear that these devices may not be connected to the DB.
                                SANS calls for the earth and neutral to be bonded, and clearly you can not do this on a PNP device as you would make the earth live.
                                All Honda, Briggs, Yamaha and their cheap Chinese duplicates are PNP devices and as such may NOT be connected to your DB. The only legal way to use them is via a lead which the end device is connected to. There one exception is a HONDA EU imported from Europe which is a true NPN generator, for some unknown reason Honda SA does not bring this into SA.