    Another thing to consider. Whasing is done in the mornings and ironing in the afternoon, with tumble drying between washing and Ironing.

    Lets say 8am to 10am washing
    11am - 1 pm tumble drying
    2pm-4pm Ironing.

    Above is a tipical day. As you can see, I overstated some durations above. I omitted tumble dryer 2's specs above, as I do not have it. It can be ignored.
    ~Expenses will eat you alive! - My first Boss~

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4946

      #47
      A couple of observations to start with, the washing machine current draws are lower than I would have expected for commercial machines, are they being supplied with pre-heated water? If they're heating their own water I think their maximum load should be higher durng the heating cycle than during the spin cycle.

      Secondly the tumble dryer with it's short peak of 13A,is this the motor start current or is the duration of this peak longer than a second or two?

      Also can you define the overlap between the washing and drying and ironing where two of the operations are taking place simultaneously or even all three operations?
      _______________________________________________

      _______________________________________________

      Comment

      • IMHO
        Email problem

        • Jan 2012
        • 540

        #48
        are they being supplied with pre-heated water?
        No, we wash cold water only. I only measured spin cycle, due to this reason. I can use hot water, but that is supplied via the hot water tap, from the geyser. I will test again when they use the machine again. BTW, it is not commercial machines, it is the normal household big Whirlpool and SpeedQueen machines, +-12kg

        Secondly the tumble dryer with it's short peak of 13A, is this the motor start current or is the duration of this peak longer than a second or two?
        No, a second or two. If you do not watch closely, you will miss it.

        Also can you define the overlap between the washing and drying and ironing where two of the operations are taking place simultaneously or even all three opera
        I cross questioned the staff and my wife on this today. Seems like there is no overlapping. Washing is done early morning when they are still cleaning rooms. Then when the tumble drying start, it is to uncomfortable in the room to do ironing. I realize that saves me a lot. I will just have to make it law that there is to be no overlapping, even as an exception, and install an alarm type buzzer that warns when the threshold is reached or tripping out at a safe amp-age cutoff?
        ~Expenses will eat you alive! - My first Boss~

        Comment

        • IMHO
          Email problem

          • Jan 2012
          • 540

          #49
          The bulk of the laundry, namely the sheets, is send to someone else to wash and Iron. We do only a little bit of that, if we get our planning wrong. Our biggest loads is towels and pillow cases, plus clothing.

          PS. I have just been informed we do a fair amount of sheets ourselves now as well, as the laundry in town can not keep up. But we stick to the hours mentioned.
          ~Expenses will eat you alive! - My first Boss~

          Comment

          • bergie
            Email problem

            • Sep 2010
            • 308

            #50
            i think the top loaders should all have a separate hot water connection and the front loaders have a built in element,with no hot water connection. i speak under correction.

            Comment

            • IMHO
              Email problem

              • Jan 2012
              • 540

              #51
              You are right bergie, it is top loaders.
              ~Expenses will eat you alive! - My first Boss~

              Comment

              • wynn
                Diamond Member

                • Oct 2006
                • 3338

                #52
                I am waiting for the battery that will be produced by young master Musk and the PV cells to be produced by a factory being constructed in the ELIDZ.
                Right now the estimate is that one can completely go off the grid with 10Kw 24/7 for about R80,000.oo and that this price will come down in the future as competition in the market increases. Or what?
                "Nobody who has succeeded has not failed along the way"
                Arianna Huffington

                Read the first 10% of my books "Didymus" and "The BEAST of BIKO BRIDGE" for free
                You can also read and download 100% free my short stories "A Real Surprise" and "Pieces of Eight" at
                http://www.smashwords.com/books/view/332256

                Comment

                • Justloadit
                  Diamond Member

                  • Nov 2010
                  • 3518

                  #53
                  Elon still has to build his factory, expected completion date 2017.
                  Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                  Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                  Comment

                  • AndyD
                    Diamond Member

                    • Jan 2010
                    • 4946

                    #54
                    Originally posted by Justloadit
                    Elon still has to build his factory, expected completion date 2017.
                    That's still several years before Medupi is likely to be on-line
                    _______________________________________________

                    _______________________________________________

                    Comment

                    • wynn
                      Diamond Member

                      • Oct 2006
                      • 3338

                      #55
                      Here is a link to an article in the M&G about just this battery

                      Elon Musk thinks batteries suck, but this didn't stop his customers from buying the entire supply of the Tesla Powerwall in a matter of days.
                      "Nobody who has succeeded has not failed along the way"
                      Arianna Huffington

                      Read the first 10% of my books "Didymus" and "The BEAST of BIKO BRIDGE" for free
                      You can also read and download 100% free my short stories "A Real Surprise" and "Pieces of Eight" at
                      http://www.smashwords.com/books/view/332256

                      Comment

                      • AndyD
                        Diamond Member

                        • Jan 2010
                        • 4946

                        #56
                        “The issue with existing batteries is … that they suck.”

                        He's not wrong, storing power is inefficient and expensive but it's a necessary evil with load shedding and it's often cheaper and more efficient (and more neighbour-friendly) than the other option which is small generators.
                        _______________________________________________

                        _______________________________________________

                        Comment

                        • blackknight72
                          Full Member
                          • May 2015
                          • 26

                          #57
                          Hello again, Today I found an Axpert 3KW MKS plus 24 volt system in a local shop with a price tag of R7000 Inc Vat. I checked with my contractor if it is okay to purchase that instead of the 48 volt system he chose for my system which was R2500 more expensive. He was vehemently opposed to it and was concerned that it will put a 'lot of strain' in the system 24 volt inverter. The best way he could explain the difference was by making a comparison between performance of a C 180 merc vs C 200! I was certainly not impressed with this rather unscientific explanation but lack of technical knowledge makes it difficult for me to debate on this matter. He also mentioned that I will need a minimum 8 batteries (?) to generate a pure sine wave.

                          I will appreciate if Andy or anyone in the forum can explain the pros and cons of using a 24 volt instead of 48 volt. Again is there any truth in saying that less than 8 cells will not create a pure sine wave?

                          Thanking in advance!

                          Comment

                          • bones
                            Silver Member

                            • Aug 2014
                            • 223

                            #58
                            any solution for hot water that doesnt
                            involve the sun?

                            spoken to many friends some say it
                            works some of the time others say it
                            is sh_t and a waste of money others
                            say gas is also a dead loss in winter

                            what size generator do i need for hot
                            water? got a 7kwatt 25amp generator
                            seek professional help with anything and everything never take advice from me

                            Comment

                            • IMHO
                              Email problem

                              • Jan 2012
                              • 540

                              #59
                              I am changing over to gas. Yes, winter is a bugger, but for 3 months only. I get 30 days on 48kg in winter, 90 days in summer. So you average 60 days on 48kg over a full year.

                              That is for 2 bathrooms, used by 3 adults, plus scullery for the guest house kitchen only. No laundry or guest bathrooms. Highest price during the last year was R1100 and lowest R750 for 48kg. Shop around for gas, some outlets is very expensive. I also heard stories of unscrupulous people filling the cylinder with a percentage water to make up the weight, but I think it is the expensive guys telling the story trying to justify their prices. It is very easy to pick-up afterwards, as the cylinder is stamped with it's empty weight.

                              So when the gas is empty, you weigh the cylinder and see if there is a difference, indicating water. I am yet to find a cylinder with water, but then again, I did not buy from the super cheap guys yet. It is normal to have a kg of gas left and the geyser stops operating. Above is from a Rinnai 21. I now started using Paloma, which so far is far superior in operation. It will be more difficult to judge the gas consumption however, as it is installed on two guest bathrooms and these rooms is not let out very often or consistently. I will have to find a way to monitor.

                              If you go gas, be careful of the cheap units that does not have defrosters build in. (And all the safety gadgets) If your unit freeze in winter, you throw it away. If your municipal water pressure dips to the low side every so often, be aware that you will take cold showers. With the Rennai, I have to set the temp to a comfortable level to shower without mixing in cold water, because if you do, the change in pressure cause the geyser to shut down. My Paloma 21 however does much better in this regard and need much less water pressure.

                              Keep in mind that the units I am referring to use about 55w to operate and you need a UPS to make sure you can shower during a load shed.
                              ~Expenses will eat you alive! - My first Boss~

                              Comment

                              • AndyD
                                Diamond Member

                                • Jan 2010
                                • 4946

                                #60
                                Originally posted by blackknight72
                                Hello again, Today I found an Axpert 3KW MKS plus 24 volt system in a local shop with a price tag of R7000 Inc Vat.
                                That's a good price!!

                                Originally posted by blackknight72
                                I checked with my contractor if it is okay to purchase that instead of the 48 volt system he chose for my system which was R2500 more expensive. He was vehemently opposed to it and was concerned that it will put a 'lot of strain' in the system 24 volt inverter.
                                The output of the inverter is rated in KVA so a 3KVA inverter will produce 3KVA output regardless of the input voltage.

                                The only downside in your case with using a 24v inverter rather than a 48v one is that the battery cables will need to be larger. This is one of the reasons that as the output power increases with the range of inverters so does the input voltage but with a 3kW unit it's still reasonable to use 24v input, hence the fact the manufacturers offer it as an option.

                                Originally posted by blackknight72
                                The best way he could explain the difference was by making a comparison between performance of a C 180 merc vs C 200! I was certainly not impressed with this rather unscientific explanation but lack of technical knowledge makes it difficult for me to debate on this matter. He also mentioned that I will need a minimum 8 batteries (?) to generate a pure sine wave.
                                I don't know how to reply to that, it's the kinda statements I'd expect a wholesaler to come out with but not really an installer

                                The number of batteries is immaterial as long as the inverter has sufficient to supply it with the correct input voltage. A 24v pure sine inverter will always produce a pure sine wave output regardless of the battery configuration as long as it's getting 24 volts from them. The inverter doesn't 'see' the individual batteries as such it just sees a pool of energy at a certain voltage so a 24volt inverter needs a minimum of 2x 12v batteries in series or 4x 6v batteries in series, it makes no difference which.