    Coc question Regarding Earth for other services.

    Good day all.
    Can anyone shed some light on the earth required for other services that's on the COC now, where should it be installed in a domestic and industrial application.?

    I got told in the roof for domestic home etc.
    There is an article in the new sparks magazine showing how this is overlooked but practically what is actually required for install?
  • DieterT
    Bronze Member

    • Oct 2014
    • 126

    #2
    Good day Jasond

    In the roof space is the most popular place, normally either not from from roof space entrance or close to the DB board up pipes into roof space.

    Where there is not ceiling space available it can be installed close to the DB board or outside in a box.

    I tend to use an S15 weaterproof box with an label on it saying "earthing for other services" and if not close to DB I put a label on the DB saying where earthing terminal for other services is located.

    Most "other services" installers don't even know about this earthing box nor do they tend to earth their installations.

    Take for example an DSTV dish. Most CoCs I have done we where required to earth the DSTV dish as the "accredited" installer never done so. Also the splitter units they use are supposed to be used (not concerning the CoC thou)

    Also with alarm systems and CCTV systems they require to earth their cables which gets rarely done. I have seen quite a few surge arrestors for IP cams used on the RJ45 cables with the earth cable tied to the copper pipes... at least they didn't just leave it hanging...

    I normally run an 10mm earth cable (green/yellow) on an 16mm supply up into the roof space connected to the main earth bar in the DB board. This is then connected to a neutral bar that is mounted to a backplate installed in the S15 box.

    This earthing terminal for other services has been in the CoC for quite a while now, but you are correct in saying it is overlooked by many. Not life or death, but shows how many sparkies out there signing CoCs without knowing what they are certifying.

    "I used to have a lot of anger issues, now I just have a passion for justice"

    Comment

    • ians
      Diamond Member

      • Apr 2010
      • 3943

      #3
      Where it is easily accessible to other services without having to access the electrical installation.
      Comments are based on opinion...not always facts....that's why people use an alias.

      Comment

      • Jasond MIE
        Junior Member
        • Sep 2014
        • 15

        #4
        Thank you so much, and personally I have never ever seen any such earth in any installation so it's good practice for future installs.

        And I agree with your statement regarding DSTV and alarm installers etc, not common practice for them to earth their systems, I'm hoping that they in future will need to certify their work too.

        Regards

        Comment

        • Dave A
          Site Caretaker

          • May 2006
          • 22810

          #5
          Originally posted by DieterT
          This earthing terminal for other services has been in the CoC for quite a while now, but you are correct in saying it is overlooked by many. Not life or death, but shows how many sparkies out there signing CoCs without knowing what they are certifying.
          Is it required to be in place if you are issuing a S9.2.b CoC - i.e. on an existing installation where the CoC being issued is only to the "reasonably safe" standard?
          Participation is voluntary.

          Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

          Comment

          • DieterT
            Bronze Member

            • Oct 2014
            • 126

            #6
            Hi Dave

            I am unsure what a S9.2b CoC is, but inregards to a test & inspection CoC for an existing installion, yes it is required to be in place.

            "I used to have a lot of anger issues, now I just have a passion for justice"

            Comment

            • Dave A
              Site Caretaker

              • May 2006
              • 22810

              #7
              Originally posted by DieterT
              I am unsure what a S9.2b CoC is, but inregards to a test & inspection CoC for an existing installion, yes it is required to be in place.
              We're talking about the same thing then.

              That means the starting point is Section 5 of SANS 10142-1. The earthing terminal for other services requirement is under 6.11 and isn't referenced from Section 5 at all (as I recall)
              Participation is voluntary.

              Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

              Comment

              • DieterT
                Bronze Member

                • Oct 2014
                • 126

                #8
                Originally posted by Dave A
                We're talking about the same thing then.

                That means the starting point is Section 5 of SANS 10142-1. The earthing terminal for other services requirement is under 6.11 and isn't referenced from Section 5 at all (as I recall)
                Yes it would seem so

                I am not sure what you mean by the starting point being Section 5 and yes the supply of earthing terminal for other services requirement can be found under section 6.11.5 of SANS10142-1

                6.11.5 A readily accessible earthing terminal shall be provided for the
                bonding of other services such as a telephone, an audio or a video system,
                and the like, to a building. Such an earthing terminal shall be bonded to the
                consumer’s earth terminal by a conductor of at least 6 mm2 copper or
                equivalent, and shall be identified by the earth symbol
                Amdt 6; amdt 8
                NOTE Providers of services other than the electrical power services should not
                access the distribution board or other parts of the electrical installation. Amdt 6

                This is under Section 4 - Inspection and Tests (New and existing installations on the CoC) point number 15. Also the reason being that should there be no earthing terminal installed for other services then the answer on the CoC would have to be "no" Thus as per note on Section 4 : Answer "Yes" or "N/A" The report shall not be issued should any "No" answers be necessary

                Comment

                • Dave A
                  Site Caretaker

                  • May 2006
                  • 22810

                  #9
                  Originally posted by DieterT
                  This is under Section 4 - Inspection and Tests (New and existing installations on the CoC) point number 15. Also the reason being that should there be no earthing terminal installed for other services then the answer on the CoC would have to be "no" Thus as per note on Section 4 : Answer "Yes" or "N/A" The report shall not be issued should any "No" answers be necessary
                  By my understanding, the correct answer in the test only of existing CoC situation if there is no point already in place would currently be "N/A" under the current legislation.

                  The accessible earthing terminal is obviously applicable and the answer must be "Yes" for a 9.2.a CoC (new installation), as in that case the entire contents of SANS 10142-1 is applicable to the entire installation.

                  What is less clear cut to my mind is when it comes to a 9.2.c CoC (addition or alteration to an existing installation). Here the full code is applicable to the alterations and additions, but the section 5 "reasonably safe" standard applies to the existing balance of the installation.
                  Participation is voluntary.

                  Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                  Comment

                  • DieterT
                    Bronze Member

                    • Oct 2014
                    • 126

                    #10
                    Why do you say that on a Test & Inspection for existing installation the answer would be N/A ?

                    Comment

                    • Dave A
                      Site Caretaker

                      • May 2006
                      • 22810

                      #11
                      Originally posted by DieterT
                      Why do you say that on a Test & Inspection for existing installation the answer would be N/A ?
                      Because it is not a requirement of the "reasonably safe" standard.
                      Participation is voluntary.

                      Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                      Comment

                      • DieterT
                        Bronze Member

                        • Oct 2014
                        • 126

                        #12
                        Reasonably safe standard? Please elaborate?

                        Comment

                        • DieterT
                          Bronze Member

                          • Oct 2014
                          • 126

                          #13
                          Are you maybe referring to this :

                          OCCUPATIONAL HEALTH AND SAFETY ACT, 1993 (ACT NO. 85 OF 1993)

                          SCHEDULE

                          ELECTRICAL INSTALLATION REGULATIONS

                          “reasonably practicable safe electrical installation” in relation to an electrical installation that existed prior to the publication of the current edition of the health and safety standard incorporated into these regulations in terms of regulation 7 (1) means that such electrical installation complies with the general safety principles of such standard

                          Comment

                          • Dave A
                            Site Caretaker

                            • May 2006
                            • 22810

                            #14
                            The general safety principles contained in Section 5 of SANS 10142-1, together with such other standards referenced from section 5.

                            As you know, the issuing of electrical CoCs is under the Electrical Installation Regulations (currently R242 of 2009).
                            If you focus on s9.2.b of this regulation, you'll see:

                            9. (1) No person other than a registered person may issue a certificate of compliance.

                            (2) A registered person may issue a certificate of compliance accompanied by the required test report only after having satisfied himself or herself by means of an inspection and test that
                            (a) a new electrical installation complies with the provisions of regulation 5(1) and was carried out under his or her general control; or
                            (b) an electrical installation which existed prior to the publication of the current edition of the health and safety standard incorporated into these Regulations in terms of regulation 5(1), complies with the general safety principles of such standard; or
                            (c) an electrical installation referred to in ...

                            Now read the opening notes to Section 5 of SANS 10142-1.
                            Participation is voluntary.

                            Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                            Comment

                            • Dave A
                              Site Caretaker

                              • May 2006
                              • 22810

                              #15
                              Originally posted by DieterT
                              Are you maybe referring to this :

                              OCCUPATIONAL HEALTH AND SAFETY ACT, 1993 (ACT NO. 85 OF 1993)

                              SCHEDULE

                              ELECTRICAL INSTALLATION REGULATIONS

                              “reasonably practicable safe electrical installation” in relation to an electrical installation that existed prior to the publication of the current edition of the health and safety standard incorporated into these regulations in terms of regulation 7 (1) means that such electrical installation complies with the general safety principles of such standard
                              Yes. (Essentially).