    When doing Inspection and Testing for a CoC for a domestic Installation for a house that used to have a three phase supply now with single phase through a TP MCB. is this legal and what Reg can I use to support this.
  • Dave A
    Site Caretaker

    • May 2006
    • 22810

    #2
    What you need to pay attention to in particular is 6.9.2.2.

    With a 3 phase installation, the disconnecting device need not disconnect the neutral in a TN system.
    With a single phase system, both the live and neutral must be disconnected.
    Participation is voluntary.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

    Comment

    • washayag
      New Member
      • Aug 2015
      • 7

      #3
      Well that is a good point. Thanks Dave A

      Comment

      • AndyD
        Diamond Member

        • Jan 2010
        • 4946

        #4
        Originally posted by Dave A
        What you need to pay attention to in particular is 6.9.2.2.

        With a 3 phase installation, the disconnecting device need not disconnect the neutral in a TN system.
        With a single phase system, both the live and neutral must be disconnected.
        Would the regs forbid using a t/pole MCB to do this?
        _______________________________________________

        _______________________________________________

        Comment

        • washayag
          New Member
          • Aug 2015
          • 7

          #5
          I haven't seen anywhere in the regs where it specifies that you cannot use a TP for a single phase, but in most cases you find that, most sparkies would not consider protection of the cable etc.