When doing Inspection and Testing for a CoC for a domestic Installation for a house that used to have a three phase supply now with single phase through a TP MCB. is this legal and what Reg can I use to support this.
triple pole breaker for a single phase supply
Collapse
X
-
What you need to pay attention to in particular is 6.9.2.2.
With a 3 phase installation, the disconnecting device need not disconnect the neutral in a TN system.
With a single phase system, both the live and neutral must be disconnected.Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services -
Would the regs forbid using a t/pole MCB to do this?_______________________________________________