    Municipal Earthing - Regulatory Guide

    Hi all,

    First time poster here needing some assistance with regards to municipal earthing requirements / by-laws and regulations in place.

    Some context:
    I live in the Germiston area and bought a home a few years ago. The home is relatively old. I would guess less than 20 years old.
    When I purchased the home I received a COC as is required. I had a second contractor validate the COC and go through the home independantly, all was clear and according to regulation. Nonetheless, I was electricuted as a result of incorrect wiring of my gate motor. Told the electrician I would report him to the electrical compliance board if he didn't rectify the issue. Over time a few of these calls were made to the issuing electrician.

    Over the past few years I have been hit by lightning every time there is a lightning storm. I have claimed from my insurer multiple times. After my last claim I received a letter from my insurer stating that I'm a high risk customer and that if any further claims are made to my household cover an excess of R 10 000 will be required. The insurer also advised that I get my property evaluated by an electrician and or to install lightning protection.

    Subsequently I managed to get a third electrician out to the property who within minutes identified that I have no municipal earthing. I was given a specific form to complete and submitted this to the Germiston municipality. As fortunate as I am, I was struck again and a fair amount of damage was done once more, all during the time that my request to the municipality was in progress (regardless to say that the municipality closed the case due to gross incompetence and not even sending an engineer to my home to evaluate the case). I digress....

    I would assume that the electrical supply company would be required by law to ensure that all homes are municipal earthed given that there is a risk of electrical shock due to insufficient earthing?

    Anyway, what do I need help with?
    1. Who can I hold liable here? The COC issuing electrician or the municipality?
    2. What regulations cover municipality earthing if any?
    3. Can I claim damages in this case?
    4. Am i chasing my own tail here trying to hold someone liable here?


    This issue is really starting to affect me so much so that I want to sell the home I have come to love but I really don't believe that is the solution. I want to prove to my insurer that I have taken all reasonable actions to remedy this situation in hopes that my excess and premium costs would go down. Over and above the previous statement I want to be 100% sure that this doesn't and can't lead to serious injury if electrocuted accidentally.
  • grootoog
    New Member
    • Dec 2016
    • 4

    #2
    Can I claim damages in this case?
    I found this in the EKURHULENI*METROPOLITAN*MUNICIPALITY*ELECTRICITY*B Y*LAWS 2008 HERE
    The Council shall not be liable for*any loss or*damage, direct or*consequentially*suffered or*sustained by*a consumer*as a result of or*arising from the cessation, interruption or*discontinuation of the supply of electricity, unless caused by*negligence on the part of the Council.
    And here:
    Irregular supply:
    The Council shall not be liable for*the consequences to the consumer*or any*other person of stoppage, failure, variation, surge or*other*deficiency*of electricity*from whatsoever*cause, provided that compliance with the Electricity Act is maintained.

    Comment

    • Dave A
      Site Caretaker

      • May 2006
      • 22810

      #3
      Do you have any idea as to how and when the municipal earth was lost?
      Participation is voluntary.

      Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

      Comment

      • grootoog
        New Member
        • Dec 2016
        • 4

        #4
        Originally posted by Dave A
        Do you have any idea as to how and when the municipal earth was lost?
        Not at all unfortunately. It does seem like it has never been installed whatsoever.


        Sent from my iPhone using Tapatalk

        Comment

        • AndyD
          Diamond Member

          • Jan 2010
          • 4946

          #5
          If the original CoC was issued by one electrician and validated by another it's highly unlikely both electricians missed the fact there was no main earth. I'd assume, as Dave suggests, it was lost at some stage.

          What earthing arrangement was the installation stated as having on the CoC? Do you know what earthing arrangement the supply authority actually provided before it went missing? There are some earthing arrangements that are the sole responsibility of the property owner such as 'TT earthing'.
          _______________________________________________

          _______________________________________________

          Comment

          • skatingsparks
            Silver Member

            • Mar 2008
            • 375

            #6
            Its not unusual for the the municiple earth to 'go missing'. Of the last 6 domestic rewires we have done - 3 had no incoming earth. Part the reason is the electricians who are sent out by the municipality have nothing more than a multimeter from cash converters and a few screw drivers. They always test between live and earth with a multimeter. When you bring out a loop tester they generally don't know what it is. If the multi meter says 230volts between live and earth they thibk thats fine.

            Comment

            • grootoog
              New Member
              • Dec 2016
              • 4

              #7
              Hi everyone,

              Apologies for the belated response, needed to go through all the documentation to list what I have.

              @AndyD
              If the original CoC was issued by one electrician and validated by another it's highly unlikely both electricians missed the fact there was no main earth. I'd assume, as Dave suggests, it was lost at some stage.
              I still have no idea how it could go "lost" surely earthing is a permanently fixed cable which needs to go to the DB board? I'm not an electrician so please excuse my ignorance. Nonetheless, I have also pasted the contents of the report HERE so you can have a look. The inspecting electrician did indeed not even pick that up either, I also do not recall providing the issued CoC to the second electrician so the likelihood is that he could have missed this plausible.

              What earthing arrangement was the installation stated as having on the CoC?
              No explicit earthing arrangement was even marked on the CoC, See screenshot 1 for reference.

              Some pics of my DB board, if this helps?
              Click image for larger version

Name:	MainsDB1.jpg
Views:	1
Size:	46.1 KB
ID:	265262 Click image for larger version

Name:	MainsDB2.jpg
Views:	1
Size:	90.3 KB
ID:	265263 Click image for larger version

Name:	MainsDB3.jpg
Views:	1
Size:	87.7 KB
ID:	265264
              Attached Files

              Comment

              • Dave A
                Site Caretaker

                • May 2006
                • 22810

                #8
                Originally posted by grootoog
                I still have no idea how it could go "lost" surely earthing is a permanently fixed cable which needs to go to the DB board?
                ... and all the way back to the neutral point of the mains supply transformer. The causes normally are cable theft, cable damage, tampering and/or corrosion (in no particular order).

                On that COC section 2 you've posted - it's incomplete (and that's putting it mildly).
                I'm also highly suspicious of the PSCC reading supplied. Either the issuer doesn't know what they're doing or they don't have the correct equipment to carry out the test. (Or both).
                Participation is voluntary.

                Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                Comment

                • AndyD
                  Diamond Member

                  • Jan 2010
                  • 4946

                  #9
                  That CoC in the screenshot is appalling, at a glance there's at least 8 omissions on that page. Whoever issued it was half hearted to say the least so I'd also take any info given with a large pinch of salt.

                  I'm also a bit confused looking at the third photo, it looks like it might be a TN S supply that's simply not got the earth connected but it's a bit difficult to tell from the photo. Also not sure what that blue MOV looking device is there for either, I hope that's not someone's idea of lightning protection......
                  _______________________________________________

                  _______________________________________________

                  Comment

                  • RegElec
                    Full Member

                    • Oct 2012
                    • 72

                    #10
                    The COC is unacceptable. I would assume that the PSCC is the fault rating that has been taken from the switchgear rather than a calculated or measured reading of the installation. The main switch is a disconnector and not earth leakage disconnector as stated on the COC. It would also appear that the incoming mains is connected to the load side of the isolator. I am not sure whether CBI allows this on their switchgear but if they do I assume there is no labelling to this effect on the DB.

                    Comment

                    • Lionels
                      Email problem
                      • Nov 2016
                      • 5

                      #11
                      When I saw what was filled out on the COC my first thought was that there was never a loop impedance test carried out, my reasoning being that normally the PSC and loop impedance tests are done with the same meter and if the PSC was thumb sucked, the same happened with the loop impedance.

                      There looks to be an old Heinemann outdoor surge arrestor in the top left of the meter board, and by the looks of the pictures, as far as I can see is there is no earth from the supplier.

                      I know that JHB city does not supply an earth, and I am assuming this is installation is in Germiston from the location of the OP, so maybe they did the same as JHB and used the old galvanized water pipes as an earth many years ago and the pipes have since been changed to plastic and so the earth was lost and nobody ever bothered to check it.
                      Last edited by Dave A; 21-Dec-16, 04:32 AM. Reason: edit per poster correction

                      Comment

                      • AbrieD
                        New Member
                        • Sep 2017
                        • 4

                        #12
                        Hi Grootoog,

                        Not sure if your problem was resolved or not?

                        If not, my advice:
                        You are probably living in an area where lightning is very active, I had this problem with several customers.
                        Only way to reduce your damages is by doing proper earthing yourself.
                        The electrical earthing in all our networks, each town and area, are not properly maintained anymore. To rely on the
                        municipal earthing is futile.

                        Get an electrician and tell him to do a crow feet earthing on your main distribution board: To explain: Hit 3 earth spikes fully into the ground
                        in the pattern of a crow's foot. Connect 10-16mm earth wire to all 3 spikes, join them and take 1 wire to your DB. Connect to the earth bus-bar,
                        make sure the bus-bar is a proper type. Now make sure all appliances are earthed and connected to the bus-bar. Finally install a surge protector.
                        Any electrician should know how.
                        Material:
                        1. 3 x Spikes 1.2m - look here to get an idea ( https://www.livecopper.co.za/product...ike-with-clamp )
                        2. 10-20 meter 10-16mm earth cable
                        3. Surge arrestor: 1 x 20kA ( https://www.livecopper.co.za/collect...stor-1p-n-20ka )
                        or 3 phase ( https://www.livecopper.co.za/collect...stor-3p-n-20ka )

                        This should solve your problem. Single phase material cost +- R 996.00

                        Comment

                        • GARY THORESSON
                          New Member
                          • Oct 2017
                          • 2

                          #13
                          Hi All,
                          Don't known if the Lightning problem has been resolved as yet.
                          If not then the following is what is required:
                          1) A Design for a Lightning Protection System, based on an acceptable form of Lightning Risk Assessment (this is a requirement by the SANS 10313 standard);
                          2) Correctly sized and positioned Air Termination system (Risk Assessment will indicate the Level of Lightning Protection required);
                          3) Two or more Down Conductor systems (determined by required Level of Lightning protection);
                          4) Must maintain the correct separation distance between down conductors and other electrical wiring systems
                          5) Earth electrode system, largely determined by the Soil Resistivity in the area;
                          6) Equipotential earth bonding;
                          7) Correctly selected Surge Protective Device (Surge Arrestors), this is determined by the Level of Lightning Protection that is required;
                          8) A Lightning Protection "CoC" (Certificate of Safe Installation) must be issued.

                          Please note that once SPDs (Surge Protective Devices) are installed in the DB board, a revised Electrical CoC must be issued.
                          The Lightning Protection "CoC" should form part of the Electrical CoC and is covered by Annex I of SANS 10142-1 as well as SANS 10313

                          For the Lightning Protection System, recently the Earthing and Lightning Protection Association (ELPA), a non-profit organization, was formed.
                          ELPA is in the process of doing accreditation of Lightning Protection Installers.
                          For more information on ELPA please see the ELPA website www.elpasa.org
                          There are a number of us who have already been accredited as ELPA approved installers, not all will be able to issue a revised Electrical CoC.

                          As to the municipal earthing system, this is a return earth fault current path back to the neutral of the supply transformer, it does not really play a role in the Lightning Protection System.
                          The Lightning Protection System and the normal household earthing and municipal earthing systems must all be inter connected.
                          The municipal earthing system should have been tested during the CoC testing, by doing a Earth Loop Impedance test and an earth resistance test.

                          I hope the above is of assistance to you

                          Comment

                          • Sparks
                            Gold Member

                            • Dec 2009
                            • 909

                            #14
                            In light of the fact that it was reported to the municipality and the required form submitted, I would suggest that they are responsible for the damages caused by the second strike because they were aware of the fault but closed the case through incompetence.