    [Question] Cooler/freezer room

    Good day all
    I have a question regarding cooler room in a butchery.
    It is wired with a 4mm cable and has a 30amp mcb in db. Should it have a switch-disconector also or is it fine as is? Its protected also by th elcb .

    Thanx
  • AndyD
    Diamond Member

    • Jan 2010
    • 4946

    #2
    The cold room would be classed as a fixed appliance so I'd say it should have an isolator switch at the condensing unit unless the MCB in the DB is close enough and qualifies.
    _______________________________________________

    _______________________________________________

    Comment

    • Eskom
      Full Member
      • Sep 2015
      • 26

      #3
      This butchery has also a 3phase cold room and it is not protected by a ELCB. The client has spoken to his friend in JHB that is a MIE and he said it does not need to be protected by a ELCB. Is this true? I just need to confirm this,rather safe than sorry. Thanx for your input Andy

      Comment

      • bergie
        Email problem

        • Sep 2010
        • 308

        #4
        it does not have to be protected by earth leakage relay. if it was plugged in to a socket outlet then it would need to be on earth leakage relay.