    Hi. Where will I find regs pertaining to the positioning of gas stoves relative to socket outlets, isolators etc... The unit has an electric oven so it needs to be plugged in. The gas installer has demanded that the socket outlet in close proximity be blanked off and that the oven be fitted with a stove coupler to utilise the existing stove circuit. The existing stove isolator is however the exact same distance from the nearest flame as the socket outlet he is demanding be blanked off.
    I have decided to blank both socket outlet and isolator off. I will be replacing the stove coupler with a socket outlet and downgrading the 40A CB to a 20A. The oven draws 16A.
    I would still like to know where to get the regs applicable.
  • Dave A
    Site Caretaker

    • May 2006
    • 22818

    #2
    The answer is SANS 10087-1 (2013 edition) for domestic installations.

    Here are the relevant diagrams:

    Typical installation by means of a flexible hose and solid pipe -
    Click image for larger version

Name:	installation with flexible hose and solid pipe.JPG
Views:	1
Size:	49.2 KB
ID:	265307

    Typical installation for gas cylinder directly connected to hob by means of a flexible hose -
    Click image for larger version

Name:	installation with flexible hose and gas cylinder.JPG
Views:	1
Size:	79.1 KB
ID:	265306
    Participation is voluntary.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

    Comment

    • Sparks
      Gold Member

      • Dec 2009
      • 909

      #3
      Thank you Dave. Does this also apply to a free standing gas hob/electric oven unit which is not enclosed?
      I am also wondering about the (No electrical switch)in the cupboard below the hob.
      Does that mean a gas hob may not be situated on top of an electric oven?

      Comment

      • Dave A
        Site Caretaker

        • May 2006
        • 22818

        #4
        Originally posted by Sparks
        Does this also apply to a free standing gas hob/electric oven unit which is not enclosed?
        How is the gas supplied? Ordinarily a gas installation certificate isn't required for a free-standing unit as it isn't a fixture.

        Originally posted by Sparks
        I am also wondering about the (No electrical switch)in the cupboard below the hob.
        Does that mean a gas hob may not be situated on top of an electric oven?
        As I understand it, the concern is for electrical items that cause a spark (no matter how minute) when operated as the spark is a potential ignition source for LP gas.
        Participation is voluntary.

        Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

        Comment

        • Sparks
          Gold Member

          • Dec 2009
          • 909

          #5
          It is a big free standing gas hob with electrical oven. The gas bottle is a 9kg which is for the moment standing next to it.
          The company it was bought from insisted to the buyer that the gas bottle needs to have a cupboard fitted next to the oven and that the bottle be installed by their technician.
          If the regulations regarding electrical equipment proximity are based on the proximity of sparks, how can a gas hob be manufactured and given SABS approval when it has an electric oven as part of the appliance with electrical switches within the proximity limits?
          If a free standing gas appliance is not subject to the regulations, on what grounds may a supplier insist that a registered installer connect the gas bottle and on what grounds may they insist that other existing electrical equipment be removed before the gas certificate is issued?

          Comment

          • Dave A
            Site Caretaker

            • May 2006
            • 22818

            #6
            Originally posted by Sparks
            If a free standing gas appliance is not subject to the regulations, ...
            For the sake of clarity I must point out that's not what I said. The regulations require a certificate of manufacture. It also places duties on various parties...

            Here are the latest gazetted guidance notes to the Pressure Equipment Regulations for you to pick over.

            Originally posted by Sparks
            If the regulations regarding electrical equipment proximity are based on the proximity of sparks, how can a gas hob be manufactured and given SABS approval when it has an electric oven as part of the appliance with electrical switches within the proximity limits?
            My wild* guess is the switches (or the switch area) has an appropriate IP rating.

            *Not to be relied on in any way whatsoever.
            Participation is voluntary.

            Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

            Comment

            • Sparks
              Gold Member

              • Dec 2009
              • 909

              #7
              This I understand, my question pertains specifically to the installation of a free standing(portable) domestic gas fueled appliance in the kitchen.


              Thank you. According to this refillable gas cylinders certificates are kept by the "owner of the cylinder". No reference is made to the actual appliance.


              This responsibility would lie with the manufacturer, however, at a glance it is obvious that the oven switch gear is not in a gas-proof enclosure.


              I fully agree that a safety standard for installation be complied with pertaining to fixed appliances, but when it comes to a free standing appliance there must be a clear indication of what is required. Where does the gas patio grill fit in? What about the gas heater? They are using the same 9kg gas cylinder to which the same pressure regulations apply.
              When the cylinder is empty and needs replacing. Must it be tested for leaks again and be re-certified?
              Last edited by Sparks; 05-Apr-17, 08:06 AM.

              Comment

              • Dave A
                Site Caretaker

                • May 2006
                • 22818

                #8
                Sparks, you should have edit permissions (for 24 hours) to fix your gremlins.
                Participation is voluntary.

                Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                Comment

                • Sparks
                  Gold Member

                  • Dec 2009
                  • 909

                  #9
                  Thanks Dave.

                  Comment

                  • mygoggie
                    Full Member

                    • Sep 2015
                    • 76

                    #10
                    Originally posted by Dave A
                    Typical installation for gas cylinder directly connected to hob by means of a flexible hose -
                    Hmmm, Dave your statement might be misleading to the uninformed. A gas cylinder may not be directly connected to a hob with a flexible hose if it passes through a compartment divider. As per Figure 4, Note 1, you need a fixed (metal) bulkhead connector installed in the divider with a flexible hose connected on either side. In reality you need to do this: Gas cylinder > hose > bulkhead connector 1 > divider > bulkhead connector 2 > flexible house > hob. I prefer to see the use of a short length of gas certified copper pipe and brass barbed compression nipples instead of the two bulkhead connectors.

                    On your question as to gas hob + electric stove please read Section 9 and I quote:

                    "9 Electrical equipment and other sources of ignition
                    Where electrical equipment is placed within the safety distance as specified in figures 3, 4 and 6
                    such equipment shall be in accordance with the requirements of SANS 10108.

                    Electrical equipment, such as light switches and plugs, shall be at least 200 mm away from any
                    burner and potential point of gas release. Where it is necessary to install a gas hob together with an
                    electric oven, a three-point plug socket shall not be used to connect the electric oven. A proper
                    isolator switch shall be in place above the level of the hob and it shall have at least 200 mm
                    clearance from the hob.

                    No electrical connection shall be made below the hob. See figures 3 and 4 for further connections."


                    My understanding of the above is the word switch means any isolator, plug or light switch and as long as these are not present you may install an electrical stove below the hob. Personally I would like to see the stove opening permanently ventilated to ensure any possible gas leaks run straight onto the floor and then hopefully to the required ventilation opening at floor level (if ever installed or the 6mm gap below the door frame created).
                    Last edited by mygoggie; 11-Apr-17, 02:14 PM.

                    Comment

                    • Dave A
                      Site Caretaker

                      • May 2006
                      • 22818

                      #11
                      Originally posted by mygoggie
                      Hmmm, Dave your statement might be misleading to the uninformed.
                      I merely quote the Figure 4 diagram label direct from the SANS code as an intro to Figure 4
                      Participation is voluntary.

                      Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                      Comment

                      • mygoggie
                        Full Member

                        • Sep 2015
                        • 76

                        #12
                        Originally posted by Dave A
                        I merely quote the Figure 4 diagram label direct from the SANS code as an intro to Figure 4
                        NP, just wanted to highlight the fact that a flexible hose cannot run through a hole in the divider (still to see one that does not ;-) )

                        Comment

                        • Sparks
                          Gold Member

                          • Dec 2009
                          • 909

                          #13
                          Originally posted by mygoggie
                          Hmmm, Dave your statement might be misleading to the uninformed. A gas cylinder may not be directly connected to a hob with a flexible hose if it passes through a compartment divider. As per Figure 4, Note 1, you need a fixed (metal) bulkhead connector installed in the divider with a flexible hose connected on either side. In reality you need to do this: Gas cylinder > hose > bulkhead connector 1 > divider > bulkhead connector 2 > flexible house > hob. I prefer to see the use of a short length of gas certified copper pipe and brass barbed compression nipples instead of the two bulkhead connectors.

                          On your question as to gas hob + electric stove please read Section 9 and I quote:

                          "9 Electrical equipment and other sources of ignition
                          Where electrical equipment is placed within the safety distance as specified in figures 3, 4 and 6
                          such equipment shall be in accordance with the requirements of SANS 10108.

                          Electrical equipment, such as light switches and plugs, shall be at least 200 mm away from any
                          burner and potential point of gas release. Where it is necessary to install a gas hob together with an
                          electric oven, a three-point plug socket shall not be used to connect the electric oven. A proper
                          isolator switch shall be in place above the level of the hob and it shall have at least 200 mm
                          clearance from the hob.

                          No electrical connection shall be made below the hob. See figures 3 and 4 for further connections."


                          My understanding of the above is the word switch means any isolator, plug or light switch and as long as these are not present you may install an electrical stove below the hob. Personally I would like to see the stove opening permanently ventilated to ensure any possible gas leaks run straight onto the floor and then hopefully to the required ventilation opening at floor level (if ever installed or the 6mm gap below the door frame created).
                          Thank you, in light of this I will now insist that gas/electric combinations be connected by cooker plug or wired directly to the isolator(I have yet to see this)
                          Please confirm the height above a gas hob which may not have electrical equipment.
                          Is this applicable to free standing units as well?(self contained on its own feet, not in a cupboard)
                          Last edited by Sparks; 12-Apr-17, 10:33 AM. Reason: Addition

                          Comment

                          • mygoggie
                            Full Member

                            • Sep 2015
                            • 76

                            #14
                            @Sparks, kindly print the PAINT file to a PDF as I cannot open it on my Mac

                            Comment

                            • AndyD
                              Diamond Member

                              • Jan 2010
                              • 4951

                              #15
                              Sparks image as Pdf and jpeg versions;

                              Free standing gaselectric combo.pdf

                              Click image for larger version

Name:	Free standing gaselectric combo.jpg
Views:	1
Size:	41.0 KB
ID:	265321
                              _______________________________________________