COC for PV installation
    • 1495
    At the moment you do not need an engineer to sign off on Solar installations , unless you get to the really big ones that are being dealt with under REIPPP programs .
    At the moment the biggest you can go is 1MV privately and I stand corrected.
    In my opinion the Solar industry has been hijack to some extent by those that see it as a quick buck.
    Some are also quick to say that they regulations, SANS 10142-1 do not cover DC/PV even though the Introduction in the book clearly states that it does (pasted in Red below) .
    There is also misconception that the circuits between panels are control circuits when they are in fact power circuits.
    An Electrical contractor cannot sign off on a job unless he was in general control.
    The whole solar regulation is being looked at again and it has not been decided yet if it will continue forming part of SANS 10142-1 or if a different set of regulations, SANS 10142-3 may be created.
    To me the biggest problem is that the majority of people are not taking into account the various bylaws ( Fire , Structural , Municipal ) when installing and future maintenance.
    Introduction
    In this edition an attempt has been made to move towards the IEC codes:
    extra low voltage (below 50 V) and d.c. applications (up to 1,5 kV) have been
    introduced as new requirements owing to the extensive usage of, and
    increased fire risk that result from, high load currents. This part of
    SANS 10142 does not intend to cover the LV control circuits of machinery or
    system components that are external circuits between separately installed
    parts of the machinery or system components.
    This part of SANS 10142 includes certain provisions which are for
    information and guidance only. These provisions do not use the word "shall"
    and they can be found in the text, in the notes and in the informative
    annexes. Except in tables, notes are always for information only.
    The aim of this part of SANS 10142 is to ensure that people, animals and
    property are protected from hazards that can arise from the operation of an
    electrical installation under both normal and fault conditions. An electrical
    installation has to provide protection against
    • Smiley
      • Oct 2018
      • 26
      Originally posted by GCE
      At the moment you do not need an engineer to sign off on Solar installations ...
      If you connect to the grid, from the docs I read, you have to have a engineer sign it off, after getting a CoC.
      If the inverter is not on the CoCT inverter list you have even more complications. Until SABS starts "approving" stuff again ... but they are not doing it anymore I read somewhere.
      A whole lot of people bought UPS with a MPPT and promptly connected it to their DB boards. This is a huge thing as UPS / Generator to DB board connections have off-the-shelf-stock-standard-regulations. All being flaunted. Therein I think CoCT, forced by NERSA, is acting now. Deadline is 28 Feb 2019 to register all solar systems. It is a HUGE opportunity for existing electricians.
      And this is not only CPT, but JHB, DBN ... all over. Everyone has the regulations in place, or are waiting on CoCT to see what transpires. Jhb the most costly for grid tied as your charges increases substantially if you connecting solar to a DB. CoCT is just the first one to enforce it publicly. If your supply is from Eskom and not a municipality, then a whole new world of challenges opens up. And if your Municipality does not have regs yet, they are coming. NERSA is behind it if you ask me. That minister did not just mention "taxes" and "solar" in that one speech with no long play in mind.
      Only part where a engineer is not required is if you have a off-grid setup. For that you need to submit a wire diagram with the application to "prove" such, electrician enters the fray again. Therein me choosing to go grid-tied, cheaper, in CoCT, and you can use a pre-paid meter. Or, feed back, but that requires a meter change (+-R8500), a daily charge, lower kwh rate and a rebate at Eskom rates, ex VAT and you must not be in credit after 12 months, as it is illegal to sell power. Unless you go big. So for home users, the deck is stacked.
      The first few quotes I got for off-grid signoff was a flat R10k+ included engineering fees. The R10k+ was based on there are NO DB board fixes required. Some tests are needed as per the form. Took the time to "train" these reputable solar installers that no, you are wrong, off-grid needs no engineer. Obviously they ignored the feedback.
      A registered electrician is wot, R485 ph, give or take. Use the word "solar" in any sentence and it becomes R800 per hour minimum.
      I'm persistent and kept asking for quotes, prices got better, but also more unsure the answers. I have emailed CoCT about the fiasco brewing, it has been noted.
      SANS10142 is being flaunted around quite a bit, like it is used to justify installing new wires, breakers and fuses to give a CoC on the panels, yet I cannot find anything that says clearly "Solar Panel DC CoC".
      It is annoying when one thinks that most of the equipment comes with clear instructions on what fuses to use, what cable sizes and lengths (DC side), voltage drops and temp effects. Solar parts have clearly statet limits, max volts / amps / VA. Ignore that or do not fuse it properly, and their is a matter of smoke being released.
      ... various bylaws ( Fire , Structural , Municipal )
      If your panels are protruding above a certain high above the highest point of ones roof, you have more costs yes. But how was your panels mounted, DIY or using a knowledgeable roof person?
      Municipal regs for CoCT are quite clear. The interpretation thereof has a huge cost factor, which is not right.
      Fire ... have not read one word about how to handle that. If your house is on fire with a roof full of panels and the firefighters arrive. In the USA the regs and parts required is quite clear, and their firefighters are also trained on how to work in and around solar panels. You cannot "switch" a panel of, you short them wires and it can cause impressive results. Solar panels can burn. You can cover them, that will "switch" them off.
      Attached the form for CoCT, to be completed if you want to grid-tie.
      Here is CoCT info: https://savingelectricity.org.za/pv-renewables/
      Other cities have same, or it is pending.
      It makes sense to register all solar systems as it saves taxpayers money to identify who is not following the basic safety standards. Day someone is killed because of a DIY connection, they will throw the book at the person. There is obviously also the "other side" ito potential taxes coming to a future near you - if too many people start to use solar and some gov department decides it is losing income.
      • Smiley
        • Oct 2018
        • 26
        Here is some more information on some of the regulations I found for JHB, DBN and NERSA.
        Eskom:
        http://www.eskom.co.za/Whatweredoing/Documents/GAU_SMG_ FAQs.pdf
        Eskom generates electricity by transforming inputs from the natural environment – coal, water, wind, nuclear and liquid fuels. Together with power generated by independent power producers (IPPs) and imports from neighbouring countries, the electricity is supplied to a wide range of customers, thereby supporting economic growth and improving the quality of life in South Africa and the region.
        JHB: https://portal.segensolar.co.za/rese..._Standards.pdf
        Durban: http://www.durban.gov.za/City_Servic...n-Process.aspx
        NERSA: http://www.nersa.org.za/Admin/Docume...s/Consultation Paper-Rules for Registration of SSEG.pdf
        Business Insider: https://www.businessinsider.co.za/dr...istered-2018-5
        If you ask me, this is a golden opportunity for electricians all over South Africa, as they "have" the clients already. Just take that one step further and make the regulations meet the physical side.
          • 3517
          In the USA, they are demanding a firman's switch for solar panels. Solar panels do not burn on their own, as they are made from silicon and glass. There have been instances in which a cell fails and can get hot due to the current flowing through it, but this only happens on very large PV systems in which hundreds of amps are being produced by the grid. Arrays should be isolated with diodes from each other when placed in parallel, to prevent this type of failure occurring.
          Arcing, because of the DC during a disconnect under full load, could cause inflammable material close by to catch alight. Correctly installed systems will not be prone to this. Proper earthing is required in the case of lightning.
          However an interesting fact about misunderstandings on solar panels.
          A Solar panel is known as a current source. A grid or a battery is known as a voltage source.
          The difference off each is as follows :-
          Current source. Irrespective of the load, provided it is with in the source voltage supply range will have a constant current from maximum load to a short circuit.
          In other words a PV panel rated at 265W at midday, will provide 8.3A from 30V to 0V(short circuit). Placing a 10A fuse in series with the load, will not protect anything, as the current is constant. Off course the current is directly linked to the amount of solar radiance.
          Voltage Source. Loading a voltage source will attempt to maintain the same voltage irrespective of the load, to the point that the internal impedance of the load will affect the maximum current that the voltage source can supply. This means that as the load impedance goes lower in impedance, the current will increase until something fails, such as a burning cable causing fire, or smoke coming out of your load. To protect against this failure requires an inline fuse or a circuit breaker.
          Connecting mains directly on to a PV panel, will cause immediate destruction of the solar panel, and blow the mains supply fuse or circuit breaker. However properly designed equipment will never allow this situation to occur even under catastrophic failures.
          • Smiley
            • Oct 2018
            • 26
            Solar panels do not burn on their own, as they are made from silicon and glass. There have been instances in which a cell fails and can get hot due to the current flowing through it, but this only happens on very large PV systems ...
            I once touched a solar panel where the diodes where already burnt out. Panel was melting hot.
            On Google there are pictures of panels being destroyed / burning. Maybe it is the roof structure that produces the flames? Therein my incorrect use of "panels can burn". Melt is more accurate?
            Question: A electrician and a engineer both mentioned that earthing panels for lighting is not such a good idea, as you are supposed to use the same earth as the DB and that is just another path for some of the lightnings power, before the cable disintegrates, to get into the house. What is your take?
            However an interesting fact about misunderstandings on solar panels. A Solar panel is known as a current source. A grid or a battery is known as a voltage source.
            Thank you for that.
            Fuses on PV cables are to protect the wire, in case there is a short of whatever cause, correct? I prefer fuses on Pos and Neg.
            Have had a 10amp fuse installed on the wires to the panels. It burnt out when the panels reached full potential. Had to upgrade to 15amp fuse promptly, as the installer though 10amp is ample on 3 x 310w panels in series. It was a good solar day. :-)
            I have read somewhere that you get MPPT inverters that are mounted per panel sending 220v down the wires to the central unit, which in turn is grid tied.
            Back to the question I was aiming for: Where do homeowners with grid tied solar systems stand ito of a CoC for the DB install, being AC?
            Is there is CoC needed for the DC side ito panel installs?
            A normal electrician cannot give on, if I read the other posts correctly.
            Batteries are straight forward, you have to have a fuse and a quick disconnect. As I want to be able to move the battery bank, it is on wheels:
            Would Brad Harrison connectors (same as at the Anderson connectors) be acceptable?
            Hands are protected from the spark if you disconnect under load.
              • 3517
              Solar panels when operating at full potential can exceed temperatures above 60 degrees centigrade, and touching the surface is a sure way of burning your skin. This is one of the reasons that PV panels should have an air gap of no less than 100mm from the back of the frame to the roof. It then allows convection cooling to take place.
              If you could cool the panels down to less than 25 degrees then you will get another 10% more of energy out of it. Unfortunately there is no inexpensive way to do this, so we live with the reduction of energy with the heating of the cells.
              That is not good practice. If lightning strikes your PV panels, and you have a grid tie system, or any other system that may be running, the potential difference between the 2 earthing points could be a few thousand volts, due to the induced energy in the earth between the 2 earthed points. If you happen to be touching one of the copper water pipes, then the earth leakage is not going to save you.
              Also the PV panels being on your roof, increases the risk of lightning affecting your installation.
              My take on this is an earth strap from the PV panels to the shortest path to a earth via an earth spike. Then join an earth wire from the earth point on the PV panel and take it to the DB earth star point. This way there can be no potential difference between the two points, as invariably all water pipes in the house are connected to this earth, usually at the geyser position. If lightning strikes the roof or panels, it will immediately be directed to earth via the shortest path.
              By joining the two earths, with a minimum of a 6mm square multi strand wire, or preferably a flat strap, then you negate this earth potential difference across the two points.
              A brand new panel will always provide more energy that the label states, and after the first few months of operation it will drop a few watts and come close to the PV panel label. Manufacturers do this to ensure that the panel performs according to the label.
              A 315W panel will produce approximately 8.75Amps at 36V on a normal day, but if there has just been a bit of rain, which has now cleared the atmosphere of dust, and dropped the temperature a bit, it causes tinny droplets in the upper atmosphere which act as little lenses, and refract and increase the sun radiance some what, with the lower temperature of the cells, you could get another 20 or so watts out of the panel, and push the current up higher, and that could be close to the fuse rupturing point.
              I have seen this happen as well on a cool crisp winter morning around 10H00, by measuring the power of the panel, I was getting the full panel rating.
              Grid ties inverters have galvanic insulation between the panel and mains supply, so that takes care of the isolation.
              If the panel side is below 50V, then no COC is required. However the grid ties inverter must have a SANAS approval for it to be accepted as usable equipment, and installed according to the legislation, will allow the electrician to issue a COC.
              All battery banks should have a suitably rated "DC" isolator, in order that you can disconnect the battery in case of a problem. Using an "AC" isolator or circuit breaker is extremely dangerous, as they self distruct and catch fire if the circuit is disconnected under load due to the arcing of the contacts during the disconnection. Do a google search "AC breakers in DC circuits"" to see some frightening you tubes on the failures
              ANderson connectors are good, provided they are rated for your installation.
                • 1495
                Hi JustLoadit
                I believe your statement - If the panel side is below 50V, then no COC is required - Is incorrect - Read the Introduction to SANS10142-1 as pasted below -
                Introduction
                • Smiley
                  • Oct 2018
                  • 26
                  Jip, totally agree, panels are on frames at a good angle on a near flat roof, so very well ventilated.
                  There where 2 panels at the time, touched both, the one with diodes fried was extremely hot versus the other one very hot, as you rightfully point out.
                  Only reason I mentioned this was that once a panel is damaged, it does not necessarily stop as there are up to a total of 72 cells that can still cause havoc if the panel is not covered or removed ASAP.
                  If lightning strikes your PV panels, and you have a grid tie system, ... touching one of the copper water pipes ...
                  The panels and geysers are quite close to each other, geysers being outside. Would it be an idea to use a earth strap from panel frames to geyser's earth connection?
                  A brand new panel
                  On a good day, days with very high clouds i.e. cloud effect, can result in up to 10% more out of a arrays rated max, my case, even after going on 7 years. So yes, must be very aware of over sizing and using the correct fuse.
                  If the panel side is below 50V, ...
                  My panels are in series, MPPT's are max 150v 35amp.
                  600v max for MPPT's for grid tied systems with panels now made for 405w. See that 355w panels today are quite affordable per watt.
                  Below 50v is becoming very uncommon. My system is max 150v at 35amps.
                  Using an "AC" isolator or circuit breaker is extremely dangerous, ...
                  Jip, used to be a common "mistake" under solar DIY's as way back the DC ones where very expensive, not anymore. Thank goodness for that.
                  Anderson connectors are good, provided they are rated for your installation.
                  Good!!!
                  I prefer a 24v battery bank. The "Anderson" connectors I use are the 50amp ones for the controllers and 175amp ones on the inverter. Can unplug the entire system in seconds. Having paid a lot of school fees being stupid, I decided to do this. Since I went this route, for ME, not a good idea for all, I have "saved" a lot of money see.
                  Have a Victron Multigrid 24v 3000va, CoCT approved using the ESS function from Victron where they quite cleverly balance the system between panels, Eskom and batteries for optimal performance.
                  48v for me only makes sense in a true off-grid situation or when you want to run your entire house during a failure. In my case the batteries are for a select few dedicated circuits only IF there is a power failure.
                  My batts are +-four years old, good for another 4-5 years as I never go below a SOC of 80% (DOD of 20%). Waiting patiently for the lithium banks to mature some more.
                  So, in conclusion, a electrician can sign off the AC side. Sorted.
                  The DC side has regulations that "includes certain provisions which are for information and guidance only", so if one follows the exact specifications of the manufactures ito fuses and cable size, using solar cable from a reputable dealer, then all is supposedly fine, but where to get a CoC for that is still not 100% clear on who can give one. Correct?
                    • 1495
                    I don't understand the confusion of the COC for PV and DC - It is clearly stipulated in SANS 10142- 1 as previously listed above in the post . A Installation electrician or Master Electrician can issue the COC as long as he has been in general control of the installation.
                    If a DIY person does it himself then it cannot be signed off - Only a registered electrical contractor as stipulated under the OHSA can install a PV systems
                    Even the proposal that is on the table at the moment keeps referencing back to SANS 10142-1 even though they now want to call the embedded generation part SANS10142-1-1 Part 1-2 -
                      • 4927
                      .........My take on this is an earth strap from the PV panels to the shortest path to a earth via an earth spike. Then join an earth wire from the earth point on the PV panel and take it to the DB earth star point. This way there can be no potential difference between the two points, as invariably all water pipes in the house are connected to this earth, usually at the geyser position. If lightning strikes the roof or panels, it will immediately be directed to earth via the shortest path.
                      By joining the two earths, with a minimum of a 6mm square multi strand wire, or preferably a flat strap, then you negate this earth potential difference across the two points......
                      I'd strongly suggest this should only be done if the supply to the premises is already confirmed to be PME'd on the side of the supply authority. If the supply is not officially PME, ie just TNCS you could end up with very high fault currents through the PV panels on-route to the new earth spike should the supplier neutral be lost somewhere upstream to your premises.
                      • Smiley
                        • Oct 2018
                        • 26
                        #26
                        I don't understand the confusion of the COC for PV and DCSANS10142-1-1 Part 1-2 -
                        GCE, my apologies. I came barging in on a Electrician side of the forum. Suspect I am asking the wrong questions or maybe in the wrong thread.
                        The buck stop at my door the day the fan and proverbial dark matter meets and the professional has left the building, for I am losing trust in what the "professionals" say as the regulations SEEM to not be 100% clear.
                        AC side I assumed is stock standard, off the shelf home DB setup. Had a qualified electrician, one that has done our entire house in the past, to connect my Multigrid to the house DB.
                        Yet I did not know that:
                        - Only a registered electrical contractor as stipulated under the OHSA can install a PV systems.
                        - Installation electrician or Master Electrician, never knew there is a difference. Electrician is a electrician sorting ones House DB out.
                        The part that is unclear to me, even with the regs you posted (thank you for your efforts), is if I do need a CoC for:
                        - panels to controllers?
                        - batteries to inverter?
                        I.e. the DC side.
                        The first time I heard about SANS 10142-1 was from Rubicon mere hours before I made my first posts here. I asked them about what is this new thing about regulations on cables.
                        Cannot seem to find a copy of that SANS 10142-1 in PDF format, not that it will help. Whom am I to disagree with a electrical professional.
                        Ideal answers I was looking for:
                        - Like CoCT: Inverter must meet NRS 097-2-1 regulations, what they are, no matter, get one on the list and you are sorted.
                        - CoC for AC connection to DB board: Your local sparky can do connect that to DB board.
                        - CoC for panel / batteries, DC side, sparky must have this qualification to give that CoC. Here is the list of regs he must adhere to ...
                        My sincerest apologies if I am wasting your guys time. I just like to understand more, in laymen terms, what I can expect to get for the estimated R10k I am looking at, if I was to believe what I am told.
                          • 3517
                          #27
                          Nice article here giving a good description of PME
                          • Smiley
                            • Oct 2018
                            • 26
                            #28
                            Found a SANS 101421-1:2017 book.
                            On page 355:
                            Type of installation: DC - the part I am questioning.
                            May be installed by: Electrical Contractor or any person under the control of a Installation Electrician or a Master Installation Electrician.
                            Test reports and CoC issuing: Installation Electrician or Master Installation Electrician, both can install DC and give a Test Report and a CoC.
                            Conclusion:
                            - Installation Electrician did my DB board, AC side of the install, so that is perfectly legal for him to do.
                            - I can, if I want, do the DC side and the Installation Electrician can the choose to sign it off, if done under his control.
                            Earthing of the panels:
                            - I'll leave that in the Installation Electricians hands after he has done the necessary testing of the system as required by CoCT docs. Too many different professional views.
                            - Earthing the panels for human safety when there is no AC at all even close to the panels, does not make complete sense.
                            - Earthing the panels for lightning: I am of the opinion that there is no protection whatsoever against lightning, unless you have a thatch roof and the required protection in place.
                            I rather unplug the panel cables from the panels, and pray, if I am around. Otherwise it is an insurance claim, if you have that cover.
                              • 3517
                              #29
                              By not earthing the PV panels, simply the wind on a hot dry day, will build up static in the frame, and due to the capacitance effect of two conducting materials with a dielectric, which is the aluminium frame, and silicon cells the glass and backing being the dielectric, the cells will charge up and at some point will need to discharge themselves into something, either equipment in which the insulation breaks down, or a human who may touch the equipment.
                              Anyone who has done ham radio or has placed wire high up to catch the radio waves will have experienced the static generated in the wires to earth, and this is increased when a storm starts building up.
                              If the panels are not earthed, and lightning strikes the frame, due to the capacitive nature of the PV panel make up, well the energy is going to go somewhere, and what ever is connected to the PV panels will be toast, and if a human is near the vicinity of the equipment, may or may not survive, because the arc is going to jump.
                              By earthing the panels, the energy will be directed to earth, as this will be the path of least resistance.
                              The question should rather be
                              "So are you prepared to take the risk of not earthing?"
                              • Smiley
                                • Oct 2018
                                • 26
                                #30
                                ... simply the wind on a hot dry day, will build up static in the frame, ...
                                ... because the arc is going to jump ...
                                Now that makes sense. Thank you!
                                If the panels and metal roof can be earthed to the geyser earth, it will not even be a problem.