    Hi guy's
    I am in desperate need of some logic to my problem.

    We are using 95mm Wesbraid soft jumpers, from the one panel jumping across the room to another panel VIA a open cable tray, the jumpers are about 6 metres long, we have two of these jumpers in parallel for each phase.

    Now for my problem.
    The RED PHASE each jumper is carrying 250 Amps.
    The WHITE PHASE each jumper is carrying 250 Amps.
    The BLUE PHASE NOW THERE'S MY ISSUE,
    The one jumper is carrying 500 Amps.
    The other jumper is carrying sometimes 1 Amp,
    Sometimes 5 Amp and sometimes 125 Amp,
    Never more than that.

    We looked and the lug to see for over heating and NO the insulation tape still intact.
    We followed the jumper mm by mm to for burning and still intact.

    The jumpers are same length.

    Unfortunately the is a hospital and it's on the ESSENTIAL supply we have taken infrared scans and it is alarming we have on that STUBBY over 110 degrees.

    We are making plans with new jumpers to replace the overheated one and the one that's giving us this issue.

    IF ANYBODY OUT THAT MIGHT AN EXPLANATION IT WOULD BE GREAT.

    THANKS
    FRENCHIE
  • ians
    Diamond Member

    • Apr 2010
    • 3943

    #2
    Do the jumpers go through individual metal holes or do they all go through the same hole?

    Measure the voltage between the top terminal of the blue phase and the bottom terminal of the blue phase on main switch and circuit breaker in that circuit...and test the voltage on the other phases ...to check if it is the same.
    Comments are based on opinion...not always facts....that's why people use an alias.

    Comment

    • Justloadit
      Diamond Member
      • Nov 2010
      • 3517

      #3
      It sounds to me that there is a break in the cable, or one of the terminals not crimped properly, or the Busbar or bolt or.... something is mechanically wrong.
      Swapping the physical positions of the terminations on one side then do a current measurement. If the reading changes then the cable is at fault, if the same position cable shoes the low reading then it is the point of termination that is the issue.

      Some pictures of the connection & terminations will help to see if there is anything visual that may be picked up.

      Only way to find out is to remove the said cable and to do a visual check.
      Unfortunately once it is out of circuit, you may not detect the break with using a simple resistance tester, and may require a destructive removal of the plastic of the cable and inspect to see where the break is.
      Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
      Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

      Comment

      • Rifrug
        Full Member

        • Nov 2019
        • 70

        #4
        That sounds like a bad crimped lug, if the copper wire is not making good contact with the lug it could give up and down readings as it heats and cools. Or the bolt are not tight. Thats my guess.

        Comment

        • FRENCHIE
          Junior Member
          • Jul 2019
          • 19

          #5
          Thanks Justloadit & Rifrug.
          But Ian yes they are going through individual holes with plastic glands on a aluminium gland plate, and when you said that I must check across the main switch, which because the cables being in parallel I wouldn't get a different reading, but then I realised why there is no sign of a burning faulty crimped plug, is if you agree with me and would be the answer of my problem, is that you take a bus-bar which has a 1000amp going through it and you take a 1.5mm wire from the beginning of the bus-bar and you try and flash to the other end of the bus-bar it will not flash because the current is already going through the bus-bar and not through the 1.5mm wire, if what I am saying makes sense, please tell me what you think.
          Eish sorry for the late call, this issue has had us spinning that we couldn't see any evidence of the fault.

          Comment

          • Dave A
            Site Caretaker

            • May 2006
            • 22812

            #6
            To find the point of resistance in the faulty jumper using infrared scanning, you are going to have to disconnect the good jumper (the one that is taking the 500 amps). Obviously this will need some thought on how to load the faulty jumper without causing knock-on effects...

            Without current, the point of resistance isn't going to generate enough energy to show up.
            Participation is voluntary.

            Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

            Comment

            • ians
              Diamond Member

              • Apr 2010
              • 3943

              #7
              The first thing you must do is get rid of the aluminum gland plate...and replace it with a non metalic plate.

              I do the main switch/circuit breaker test to check for bad connections inside the units... when i do thermal inspections and i dont find issues with the actual lug or terminations the next step is to do a voltage test ...i normally compare the reading top to bottom (line to load)...of each phase... and if 2 are 0.54 volts and 1 is 15 volts... i know straight away that the switch is faulty and there is an internal bad connection...or a problem with a point to point cable.

              You can make a up a long tail and do the test at various point in the panel and between panel to pin point bad connections...the beuty about this kind of test ...it can be done without switching off the power.
              Comments are based on opinion...not always facts....that's why people use an alias.

              Comment

              • GCE
                Platinum Member
                • Jun 2017
                • 1495

                #8
                Aluminum gland plate is fine as it is non magnetic material and you will not get a heat build up due to eddie currents
                Only happens on magnetic material

                Comment

                • ians
                  Diamond Member

                  • Apr 2010
                  • 3943

                  #9
                  not being an electrical engineer ...when we start getting into this complex stuff... like eddy currents going around the cable and heat build up due to hysteresis ...circulating current along the cable being compounded by harmonics ...cable configurations and earth separation ...draining ... and all that stuff... personally i have only used bakelite to terminate large single core cables... never even considered aluminum.

                  It will be interesting to hear the outcome of this issue.
                  Comments are based on opinion...not always facts....that's why people use an alias.

                  Comment

                  • GCE
                    Platinum Member
                    • Jun 2017
                    • 1495

                    #10
                    We use aluminium especially on the larger generators - You are generally bringing in 120sqmm armour cable ECC which tends to crack Bakelite when there is a bit of movement and at the same time you are bringing in single cores from the alternator. With aluminium you still have earth continuity and a solid base to gland to and the single cores can go through separately without the eddy current problems.

                    Comment

                    • Justloadit
                      Diamond Member
                      • Nov 2010
                      • 3517

                      #11
                      Originally posted by GCE
                      Aluminum gland plate is fine as it is non magnetic material and you will not get a heat build up due to eddie currents
                      Only happens on magnetic material
                      The one property of Aluminium, is that it generates eddie currents with changes in magnetic field, over and above the ability to absorb heat, and the reason that it is used in heatsink material in the electronics industry. Granted the strength of the magnetic field will influence the amount of heat generated by eddie currents. This property is not seen with steel, stainless steel and copper. In fact the steel is a good shielding material for radio waves and magnetic fields, as opposed to aluminium. However in this case that a 4 or 5 core goes through the plate, the sum of all currents in the phases will be zero, and no magnetic field will be created, however with single cable through the gland and the high currents you refer to, it will generate eddie currents. The amount of heat generated may be small enough that it may be ignored as normal operating temperature.
                      Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                      Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                      Comment

                      • FRENCHIE
                        Junior Member
                        • Jul 2019
                        • 19

                        #12
                        Guy's we have managed to get an outage last night and I don't know how to attach the pics from my phone gallery and chat some more.
                        Can someone assist me with doing this attachment.
                        Thanks
                        FRENCHIE

                        Comment

                        • AndyD
                          Diamond Member

                          • Jan 2010
                          • 4927

                          #13
                          Hi Frenchie, are you using a smartphone or a PC?

                          On the very odd occasions that we enter cable conductors through separate holes via a gland plate we usually drill the gland holes in a straight line and then cut a thin slot between them before fitting the glands; this prevents heating occuring from eddie currents. If the current involved is less than 60 Amps we don't generally worry about it to be honest, I've only ever encountered heating problems due to eddie currents with supplies in excess of 200Amps.
                          _______________________________________________

                          _______________________________________________

                          Comment

                          • FRENCHIE
                            Junior Member
                            • Jul 2019
                            • 19

                            #14
                            Hi Andi.
                            I am working on my smart phone.
                            I thought that aluminium not being magnetic it would not carry the field around the conductors, the conductors are +- 50mm apart, but you saying to cut the a thin line between the gland holes sounds the right thing to do.
                            As mentioned previously we did the repairs, but because we were unable to see behind the switch gear, even trying to take pictures that didn't show anything wrong, we took heat scan and it only showed one of the parallel jumpers taking all the current and it was up 110 degrees, and the other had no heat at all.
                            As all the guys on the chat including ourselves one thing came to mind is that their is a loose connection, but because of all the checking we did, we put that on the back burner.
                            Well guys I am happy to say that I/we are very LUCKY still to be here chatting to you guy's ( once I manage to send the pics).
                            A VALUABLE LESSON TO BE LEARNED.
                            When we started to investigate this issue, i had my hands & arms and face hard up and behind the switch gear trying to ascertain the cause.
                            When we replaced the two affected jumpers,
                            The one overheated.
                            The other not carrying the load.
                            We found that the one lug actually slipped off the jumper and slipped back in like slipping on a glove, although it was crimped not correctly ofcourse, that particular lug was not the same as the other lugs on all the other jumpers.
                            Could that have been one of issue that started the chain of events.
                            I would like to give a special thanks to all of you guy's that participated in this discussion, and it did increase my knowledge in this debate.

                            I will send the pics once I get the know.

                            Thanks again
                            FRENCHIE.

                            Comment

                            • SeanM
                              Bronze Member

                              • Mar 2018
                              • 120

                              #15
                              Greetings All

                              I have to rectify a generator installation as the previous contractors install the generator before councils meter.

                              I have to extend the 150mm cable which is armour cable (solid stranded copper) and I want to crimp onto this cable 150mm single core flexible cable ( braided copper cable), does anyone forsee any challenges with this?