3 phase loop impedance testing
  • shaneo
    • Feb 2018
    • 13
    Can someone please advise me on the most affordable meters for 3 phase loop/pscc testing. Also which other testers I would need to carry out a Compliance test on a three phase installation. I have the meters for single phase testing.
    Thanks Shaneo.
    • 4927
    You can use a single phase PEFC/PSSC tester, it just means you must make 3 separate tests on the 3 phases and use the highest reading. If you particularly want a 3 phase tester look at brands like Brymen or maybe Uni-t that are good value for money but still decent quality testers.
    • SeanM
      • Mar 2018
      • 120
      Morning
      Just a reminder that if you use a single phase tester for PSC you need to multiply you reading by 1.73 ( square root of 3)
      • shaneo
        • Feb 2018
        • 13
        Thanks to everyone for the advice, I find this forum to be very helpful.