    Good day all
    I was called to a house to COC for a sale, a quick joppie

    The incoming 10mm airdeck cable, buried in the ground, split somewhere under the ground to an adjacent plot???
    The flat twin and earth wires are build into the walls and some are on the surface and plastered over??
    The flat twin and earth wires are in the cavity between the ceiling and corrugated roof. Not sure if there are junctions or not.
    I don't see any protection for the twin and earth that runs over the metal strips on which the ceiling is fitted
    Three and even 4 flat twin and earth wires are pulled into one 20mm conduit
    The DIN rail DB had been enlarged to accomodate a meter or samite breaker or something else
    The list goes on and on.... I had not even started testing the wiring in the building

    My diagnosis is to rewire everything but how do I do it without chasing the walls and open the roof or ceiling
    Will be going back for a few photos a bit later

    Stay safe
  • Derlyn
    Platinum Member
    • Mar 2019
    • 1765

    #2
    From a toppie

    Quote high enough that you do not get the job.

    If you do get the job, you going to make some money.

    That's how I operate and it works.

    Doesn't seem like a quick "jobbie"

    Peace out .. Derek.

    Comment

    • Lourie1251
      Junior Member
      • Nov 2017
      • 11

      #3
      You talk about bad wiring. I went to do a coc, when I put my polarity tester in the plugs every light came on. I thought well this looks like an earth fault problem.
      I tested the db and found I had no reading between live and earth and 220v between neutral and earth.
      A long story short, when the council removed the meter and installed a pre paid meter the electrician
      Had the wires in the wrong terminals and put 220v through the the neutral instead of the live. Saving grace was this is a holiday cottage and no idea how many people had rented this place.

      Comment

      • Derlyn
        Platinum Member
        • Mar 2019
        • 1765

        #4
        Originally posted by Lourie1251
        You talk about bad wiring. I went to do a coc, when I put my polarity tester in the plugs every light came on. I thought well this looks like an earth fault problem.
        I tested the db and found I had no reading between live and earth and 220v between neutral and earth.
        A long story short, when the council removed the meter and installed a pre paid meter the electrician
        Had the wires in the wrong terminals and put 220v through the the neutral instead of the live. Saving grace was this is a holiday cottage and no idea how many people had rented this place.
        Had that before brother. Live and neutral swopped in the roofbox.