Solar PV systems
Collapse
X
-
No, not one document, but everything you buy and use have specifications.
Here's an example: https://www.voltex.co.za/wp-content/...ARTH-CABLE.pdf
Check out the installation instructions and the note.
Specifications do not have to be in writing.
When a socket outlet has 4 holes for mounting it, that means the manufacturer is telling you that it should be mounted using 4 screws.
Peace out ... DerekComment
-
Good rising brother.
No, not one document, but everything you buy and use have specifications.
Here's an example: https://www.voltex.co.za/wp-content/...ARTH-CABLE.pdf
Check out the installation instructions and the note.
Specifications do not have to be in writing.
When a socket outlet has 4 holes for mounting it, that means the manufacturer is telling you that it should be mounted using 4 screws.
Peace out ... Derek
Ahhh yes ok I see what you mean.
I didn't have a term for it but I try to practice looking at the documents for the products as much as possible. Some of the okes at work laugh when I ask for the instructions and the packaging but then when I say they doing something wrong and have proof I am the one laughing last.
I started this from watching the overseas okes and speaking of manufacturing instructions and if shit had to hit the fan and it was installed with 3 screws and not 4 then they not to blame and the installer is to blame.
But now I have a cool term to use for this "due diligence"
Sent from my SM-N960F using TapatalkComment
-
Comments are based on opinion...not always facts....that's why people use an alias.Comment
-
A lot of information to process in a weekend ... one thing for sure is the sans 10142 is lacking information ... fortunately getting hands on all the other drafts in the pipe line it will assist to guide me into the new year.
Anyone have a list of the latest standards required for solar installations.
SANS 10142-1 (ed 3.01)
NRS 097-2-1-2017 (which ones are relevant ... I see there are a few)
SANS have published SANS 10142-1-2
The wiring of premises
Part 1-2: Additional special requirements for
low voltage small scale embedded generator
installations connected to THE GRID
This document was approved for publication in November 2021.
The scope of the document appears to contradict itself.
1 Scope
1.1 This standard covers special requirements in addition to SANS 10142-1 for electrical installation
of Small Scale Embedded Generators (SSEGs) rated up to 1 000 kVA intended to supply all or part
of an installation with nominal voltages not exceeding 1 kV AC or 1,5 kV DC.
1.2 This document is applicable to SSEG installations intended to be connected in parallel to an
electrical supply grid or electrical supply authority.
1.3 This document also applies to the installation of the following:
a) Solar PV installations;
b) Energy storage systems;
c) Inverter-based generation;
d) Synchronous generators;
e) Asynchronous/induction generators; and
f) Any combination of the above that are connected to a single point of supply.
NOTE 1 In this standard, the terms Small Scale Embedded Generator (SSEG) and Embedded Generator (EG)
are used interchangeably.
NOTE 2 Embedded generation is also known as Grid tied generation.
1.4 This part of SANS 10142 does not apply to
a) all alternative supplies e.g. Solar PV systems, wind turbines which is covered in 7.12 of
SANS 10142-1: 2021, and
b) stand-alone electrical generating systems.
Comment
-
I found this draft ... has this been published ?
Comments are based on opinion...not always facts....that's why people use an alias.Comment
-
It does contradict itself, says applies to solar pv then last paragraph states it does not apply... they setting them selves up for another 1000 bucks on Amendemmt 1....
We get dragged by the heals in court and clients when get something wrong yet they release a document with more questions than answers ...
Side note I have not been dragged but many an electrician has been brought over the coals when shit hits the fan but our "law book" can have errors....
Sent from my SM-N960F using TapatalkComment
-
I found this draft ... has this been published ?
https://arepenergy.co.za/wp-content/...R-01102018.pdfComment
-
Hi
SANS have published SANS 10142-1-2
The wiring of premises
Part 1-2: Additional special requirements for
low voltage small scale embedded generator
installations connected to THE GRID
This document was approved for publication in November 2021.
The scope of the document appears to contradict itself.
1 Scope
1.1 This standard covers special requirements in addition to SANS 10142-1 for electrical installation
of Small Scale Embedded Generators (SSEGs) rated up to 1 000 kVA intended to supply all or part
of an installation with nominal voltages not exceeding 1 kV AC or 1,5 kV DC.
1.2 This document is applicable to SSEG installations intended to be connected in parallel to an
electrical supply grid or electrical supply authority.
1.3 This document also applies to the installation of the following:
a) Solar PV installations;
b) Energy storage systems;
c) Inverter-based generation;
d) Synchronous generators;
e) Asynchronous/induction generators; and
f) Any combination of the above that are connected to a single point of supply.
NOTE 1 In this standard, the terms Small Scale Embedded Generator (SSEG) and Embedded Generator (EG)
are used interchangeably.
NOTE 2 Embedded generation is also known as Grid tied generation.
1.4 This part of SANS 10142 does not apply to
a) all alternative supplies e.g. Solar PV systems, wind turbines which is covered in 7.12 of
SANS 10142-1: 2021, and
b) stand-alone electrical generating systems.
Sans 10142-1-2 is for systems running in parallel , typical gridtie systems or running generators in sync with supplyComment
-
Ahhh I see GCE, thank you for this.
I feel now not much of great use as I do backup and no grid syncing. However may still be a good read as in the future PV systems can backfeed once all that is ironed out and I understand the process.
so on the Christmas wishlist then haha.
Sent from my SM-N960F using TapatalkComment
-
Hi
SANS have published SANS 10142-1-2
The wiring of premises
Part 1-2: Additional special requirements for
low voltage small scale embedded generator
installations connected to THE GRID
This document was approved for publication in November 2021.
1 Scope
1.1 This standard covers special requirements in addition to SANS 10142-1 for electrical installation
of Small Scale Embedded Generators (SSEGs) rated up to 1 000 kVA intended to supply all or part
of an installation with nominal voltages not exceeding 1 kV AC or 1,5 kV DC.
1.2 This document is applicable to SSEG installations intended to be connected in parallel to an
electrical supply grid or electrical supply authority.
1.3 This document also applies to the installation of the following:
a) Solar PV installations;
b) Energy storage systems;
c) Inverter-based generation;
d) Synchronous generators;
e) Asynchronous/induction generators; and
f) Any combination of the above that are connected to a single point of supply.
NOTE 1 In this standard, the terms Small Scale Embedded Generator (SSEG) and Embedded Generator (EG)
are used interchangeably.
NOTE 2 Embedded generation is also known as Grid tied generation.
1.4 This part of SANS 10142 does not apply to
a) all alternative supplies e.g. Solar PV systems, wind turbines which is covered in 7.12 of
SANS 10142-1: 2021, and
b) stand-alone electrical generating systems.
Nobody appears to have been informed that the document was going to be withdrawn , but there again , nobody was aware that it was due to be published before a final round of objections and comments were sorted out
Will keep an eye out for further developmentsComment
Comment