Solar PV systems

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Dylboy
    Gold Member

    • Jun 2020
    • 777

    #16
    Originally posted by Derlyn
    My post dissapeared.

    I use 4 sets of rules and regulations that all electrical work must conform to.

    1. Sans 10142
    2. Occupational health and safety act.
    3. Manufacturers specifications for consumables.
    4. Supply authority by laws.

    If anyone has more, feel free to add to the list.

    Peace out .. Derek
    Hello

    Your number 3, is it a document or just the manufactures instructions when you get the item ?

    I did a Google on the wording used and came up with other sort of things.

    Sent from my SM-N960F using Tapatalk

    Comment

    • Derlyn
      Platinum Member
      • Mar 2019
      • 1765

      #17
      Originally posted by Dylboy
      Hello

      Your number 3, is it a document or just the manufactures instructions when you get the item ?

      I did a Google on the wording used and came up with other sort of things.

      Sent from my SM-N960F using Tapatalk
      Good rising brother.

      No, not one document, but everything you buy and use have specifications.

      Here's an example: https://www.voltex.co.za/wp-content/...ARTH-CABLE.pdf

      Check out the installation instructions and the note.

      Specifications do not have to be in writing.
      When a socket outlet has 4 holes for mounting it, that means the manufacturer is telling you that it should be mounted using 4 screws.

      Peace out ... Derek

      Comment

      • Dylboy
        Gold Member

        • Jun 2020
        • 777

        #18
        Originally posted by Derlyn
        Good rising brother.

        No, not one document, but everything you buy and use have specifications.

        Here's an example: https://www.voltex.co.za/wp-content/...ARTH-CABLE.pdf

        Check out the installation instructions and the note.

        Specifications do not have to be in writing.
        When a socket outlet has 4 holes for mounting it, that means the manufacturer is telling you that it should be mounted using 4 screws.

        Peace out ... Derek
        Morning !

        Ahhh yes ok I see what you mean.

        I didn't have a term for it but I try to practice looking at the documents for the products as much as possible. Some of the okes at work laugh when I ask for the instructions and the packaging but then when I say they doing something wrong and have proof I am the one laughing last.

        I started this from watching the overseas okes and speaking of manufacturing instructions and if shit had to hit the fan and it was installed with 3 screws and not 4 then they not to blame and the installer is to blame.

        But now I have a cool term to use for this "due diligence"

        Sent from my SM-N960F using Tapatalk

        Comment

        • ians
          Diamond Member

          • Apr 2010
          • 3943

          #19
          4 screws in a socket outlet ... did you fallout your bed this morning

          Originally posted by Derlyn

          When a socket outlet has 4 holes for mounting it, that means the manufacturer is telling you that it should be mounted using 4 screws.
          Comments are based on opinion...not always facts....that's why people use an alias.

          Comment

          • Derlyn
            Platinum Member
            • Mar 2019
            • 1765

            #20
            Sorry. Should have said installed or fitted otherwise some okes might read it to mean something else.😁😁

            Comment

            • GCE
              Platinum Member
              • Jun 2017
              • 1495

              #21
              Originally posted by ians
              A lot of information to process in a weekend ... one thing for sure is the sans 10142 is lacking information ... fortunately getting hands on all the other drafts in the pipe line it will assist to guide me into the new year.

              Anyone have a list of the latest standards required for solar installations.

              SANS 10142-1 (ed 3.01)

              NRS 097-2-1-2017 (which ones are relevant ... I see there are a few)
              Hi

              SANS have published SANS 10142-1-2
              The wiring of premises
              Part 1-2: Additional special requirements for
              low voltage small scale embedded generator
              installations connected to THE GRID
              This document was approved for publication in November 2021.

              The scope of the document appears to contradict itself.


              1 Scope
              1.1 This standard covers special requirements in addition to SANS 10142-1 for electrical installation
              of Small Scale Embedded Generators (SSEGs) rated up to 1 000 kVA intended to supply all or part
              of an installation with nominal voltages not exceeding 1 kV AC or 1,5 kV DC.
              1.2 This document is applicable to SSEG installations intended to be connected in parallel to an
              electrical supply grid or electrical supply authority.
              1.3 This document also applies to the installation of the following:
              a) Solar PV installations;
              b) Energy storage systems;
              c) Inverter-based generation;
              d) Synchronous generators;
              e) Asynchronous/induction generators; and
              f) Any combination of the above that are connected to a single point of supply.
              NOTE 1 In this standard, the terms Small Scale Embedded Generator (SSEG) and Embedded Generator (EG)
              are used interchangeably.
              NOTE 2 Embedded generation is also known as Grid tied generation.
              1.4 This part of SANS 10142 does not apply to
              a) all alternative supplies e.g. Solar PV systems, wind turbines which is covered in 7.12 of
              SANS 10142-1: 2021, and
              b) stand-alone electrical generating systems.

              Comment

              • ians
                Diamond Member

                • Apr 2010
                • 3943

                #22
                I found this draft ... has this been published ?

                Comments are based on opinion...not always facts....that's why people use an alias.

                Comment

                • Dylboy
                  Gold Member

                  • Jun 2020
                  • 777

                  #23
                  Ya i am confused now, is it published or draft ? but also thanks for sharing and sparking more on this convo



                  Sent from my SM-N960F using Tapatalk

                  Comment

                  • Dylboy
                    Gold Member

                    • Jun 2020
                    • 777

                    #24
                    It does contradict itself, says applies to solar pv then last paragraph states it does not apply... they setting them selves up for another 1000 bucks on Amendemmt 1....

                    We get dragged by the heals in court and clients when get something wrong yet they release a document with more questions than answers ...

                    Side note I have not been dragged but many an electrician has been brought over the coals when shit hits the fan but our "law book" can have errors....

                    Sent from my SM-N960F using Tapatalk

                    Comment

                    • GCE
                      Platinum Member
                      • Jun 2017
                      • 1495

                      #25
                      Originally posted by ians
                      I found this draft ... has this been published ?

                      https://arepenergy.co.za/wp-content/...R-01102018.pdf
                      The code has been published but it is quite a bit different to the draft.

                      Comment

                      • GCE
                        Platinum Member
                        • Jun 2017
                        • 1495

                        #26
                        Originally posted by GCE
                        Hi

                        SANS have published SANS 10142-1-2
                        The wiring of premises
                        Part 1-2: Additional special requirements for
                        low voltage small scale embedded generator
                        installations connected to THE GRID
                        This document was approved for publication in November 2021.

                        The scope of the document appears to contradict itself.


                        1 Scope
                        1.1 This standard covers special requirements in addition to SANS 10142-1 for electrical installation
                        of Small Scale Embedded Generators (SSEGs) rated up to 1 000 kVA intended to supply all or part
                        of an installation with nominal voltages not exceeding 1 kV AC or 1,5 kV DC.
                        1.2 This document is applicable to SSEG installations intended to be connected in parallel to an
                        electrical supply grid or electrical supply authority.
                        1.3 This document also applies to the installation of the following:
                        a) Solar PV installations;
                        b) Energy storage systems;
                        c) Inverter-based generation;
                        d) Synchronous generators;
                        e) Asynchronous/induction generators; and
                        f) Any combination of the above that are connected to a single point of supply.
                        NOTE 1 In this standard, the terms Small Scale Embedded Generator (SSEG) and Embedded Generator (EG)
                        are used interchangeably.
                        NOTE 2 Embedded generation is also known as Grid tied generation.
                        1.4 This part of SANS 10142 does not apply to
                        a) all alternative supplies e.g. Solar PV systems, wind turbines which is covered in 7.12 of
                        SANS 10142-1: 2021, and
                        b) stand-alone electrical generating systems.

                        Just been having the discussion on what is covered by what. I originally thought a contradiction, but it has been pointed out that SANS10142-1 excludes alternative supply operating in parallel with the main supply to an installation.( 7.12.1.1 note 2 )

                        Sans 10142-1-2 is for systems running in parallel , typical gridtie systems or running generators in sync with supply

                        Comment

                        • Dylboy
                          Gold Member

                          • Jun 2020
                          • 777

                          #27
                          Ahhh I see GCE, thank you for this.

                          I feel now not much of great use as I do backup and no grid syncing. However may still be a good read as in the future PV systems can backfeed once all that is ironed out and I understand the process.

                          so on the Christmas wishlist then haha.

                          Sent from my SM-N960F using Tapatalk

                          Comment

                          • GCE
                            Platinum Member
                            • Jun 2017
                            • 1495

                            #28
                            Originally posted by GCE
                            Hi

                            SANS have published SANS 10142-1-2
                            The wiring of premises
                            Part 1-2: Additional special requirements for
                            low voltage small scale embedded generator
                            installations connected to THE GRID
                            This document was approved for publication in November 2021.

                            1 Scope
                            1.1 This standard covers special requirements in addition to SANS 10142-1 for electrical installation
                            of Small Scale Embedded Generators (SSEGs) rated up to 1 000 kVA intended to supply all or part
                            of an installation with nominal voltages not exceeding 1 kV AC or 1,5 kV DC.
                            1.2 This document is applicable to SSEG installations intended to be connected in parallel to an
                            electrical supply grid or electrical supply authority.
                            1.3 This document also applies to the installation of the following:
                            a) Solar PV installations;
                            b) Energy storage systems;
                            c) Inverter-based generation;
                            d) Synchronous generators;
                            e) Asynchronous/induction generators; and
                            f) Any combination of the above that are connected to a single point of supply.
                            NOTE 1 In this standard, the terms Small Scale Embedded Generator (SSEG) and Embedded Generator (EG)
                            are used interchangeably.
                            NOTE 2 Embedded generation is also known as Grid tied generation.
                            1.4 This part of SANS 10142 does not apply to
                            a) all alternative supplies e.g. Solar PV systems, wind turbines which is covered in 7.12 of
                            SANS 10142-1: 2021, and
                            b) stand-alone electrical generating systems.

                            It appears that the above document has now been removed from the SANS Store for purchase
                            Nobody appears to have been informed that the document was going to be withdrawn , but there again , nobody was aware that it was due to be published before a final round of objections and comments were sorted out
                            Will keep an eye out for further developments

                            Comment

                            Working...