    I feel that if we had to take responsibility for the whole electrical installation of the property I would never install a plug... or a plug install will be mighty expensive and take a hell of a lot longer haha.

    I take it as we take responsibility for the electrical installtion of what was installed only.

    But glad this discussion is happening.

    Sent from my SM-N960F using Tapatalk

    Comment

    • Leecatt
      Silver Member
      • Jul 2008
      • 409

      #17
      Originally posted by Dylboy
      I feel that if we had to take responsibility for the whole electrical installation of the property I would never install a plug... or a plug install will be mighty expensive and take a hell of a lot longer haha.

      I take it as we take responsibility for the electrical installtion of what was installed only.

      But glad this discussion is happening.

      Sent from my SM-N960F using Tapatalk
      This is the reason that I don't do installation work.

      Sent from my SM-A705FN using Tapatalk
      To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

      Comment

      • ians
        Diamond Member

        • Apr 2010
        • 3943

        #18
        This is the kind of thing I deal with all the time ... how do you install a circuit breaker in this DB or should I say how do you issue a COC once you have fitted your circuit breaker in this DB and run the wire to the machine ?


        Click image for larger version

Name:	bad DB.jpg
Views:	1
Size:	80.5 KB
ID:	266112
        Comments are based on opinion...not always facts....that's why people use an alias.

        Comment

        • Derlyn
          Platinum Member
          • Mar 2019
          • 1765

          #19
          Originally posted by Leecatt
          I would say that
          "in any part of the electrical installation"
          speaks for itself.

          Further,
          2.8.2 Sub-regulation 2
          A registered person may issue a certificate of compliance accompanied by the
          required test report only after having satisfied himself or herself by means of
          an inspection and test that-
          (a) a new electrical installation complies with the prov1s1ons of
          regulation 5(1) and was carried out under his or her general
          control; or
          (b) an electrical installation which existed prior to the publication of
          the current edition of the health and safety standard
          incorporated into these Regulations in terms of regulation 5(1 ),
          complies with the general safety principles of such standard; or
          (c) an electrical installation referred to in paragraph (b), to which
          extensions or alterations have been effected, that-
          (i) the existing part of the electrical installation complies with
          the general safety principles of such standard and is
          reasonably safe, and
          (ii) the extensions or alterations effected comply with the
          provisions of regulation 5(1) and were carried out under
          his or her general control.

          It is my understanding that the only way to comply with part C of the above is to do an inspection of the entire electrical installation.
          It has always been my understanding that by issuing a certificate of compliance for an additional plug one takes responsibility for the entire electrical installation.

          Sent from my SM-A705FN using Tapatalk
          I sort of agree.

          That is why I insisted, about 2 weeks ago, on seeing the original COC for a property that had recently been transferred before issuing a supplementary for the add on's that I did.

          The COC presented to me was a supplementary and I rejected it.

          When the initial COC was presented, I gladly issued a supplementary to the original.

          Here comes the part that I think is the reason for the supplementary COC being there.

          I take responsibility for my add on's as described in the supplementary.

          The electrician who issued the original takes responsibility for the rest.


          Peace out ... Derek


          Edit: I have searched but cannot find anything in either SANS10142 or OHSA that mentions the word " supplementary COC "
          It might be helpful if, in future versions of same, some guidelines could be included pertaining to Supplementary COC's as it seems as if at the moment each electrician follows their own interpretation of what the procedure is, myself included.

          If one had to issue an initial coc for adding a plug, my question then is ... why the need for a supplementary coc ?
          Last edited by Derlyn; 19-Dec-21, 12:49 PM.

          Comment

          • ians
            Diamond Member

            • Apr 2010
            • 3943

            #20
            I found this...


            Do I need a CoC when I do alterations to the electrical system on my property?

            Yes. A CoC must be issued when any alterations are done to an electrical installation. For example, if traditional lighting is replaced by downlights, the electrical contractor must ensure that a valid CoC is issued for that work. Where any addition or alteration has been done to an electrical installation for which a CoC has already been issued, the user or lessor of that electrical installation must get a supplementary CoC for the addition or alteration. Both CoCs must be kept together in a safe place.
            Comments are based on opinion...not always facts....that's why people use an alias.

            Comment

            • ians
              Diamond Member

              • Apr 2010
              • 3943

              #21
              The safety of the electrical installation is not the electrical contractors responsibility ... so if you are smart you ... you complete your socket outlet installation and advise the customer that they need to get an Initial certificate for the electrical installation ... which will include your new socket outlet

              For anyone renting a property ... this is why it is so important for you as the tenant to make sure that the owner hands you all the relevant documentation when you move into the property ... the day you move into the building ... the safety of the electrical installation becomes your responsibility.

              Do renting agencies make sure the property has a valid certificate ?

              I know in some of the buildings my customers rent ... I insist on a COC prior to the relocation ... some of the property management agencies also carry out a thermal inspection for insurance purposes ... lets not go there ... but at least they try.
              Comments are based on opinion...not always facts....that's why people use an alias.

              Comment

              • ians
                Diamond Member

                • Apr 2010
                • 3943

                #22
                I also found this ....

                Certificate type
                Indicate whether this CoC is:

                A new CoC for this installation, tick ‘Initial Certificate’, indicating that this CoC constitutes the complete and whole document, or
                An additional CoC to an existing one, tick ‘Supplementary Certificate’, which indicates that this is a partial document only, and it must be read together with an ‘Initial Certificate’ and possibly other ‘Supplementary Certificates’ for it to be valid.
                If this is an initial CoC, enter ‘N/A’ in all three spaces on the next line, or
                If this CoC is Supplementary, enter the number (1st, 2nd, 3rd etc), and the number and date of issue of the ‘Initial Certificate’.
                Comments are based on opinion...not always facts....that's why people use an alias.

                Comment

                • Derlyn
                  Platinum Member
                  • Mar 2019
                  • 1765

                  #23
                  @Ians

                  Where did you find that ?
                  That should be in SANS10142 or OHSA.

                  Derek.

                  Comment

                  • ians
                    Diamond Member

                    • Apr 2010
                    • 3943

                    #24
                    Google
                    Comments are based on opinion...not always facts....that's why people use an alias.

                    Comment

                    • ians
                      Diamond Member

                      • Apr 2010
                      • 3943

                      #25
                      Another one in my favourites collection ... would you issue an initial certificate for your part of the installation ?

                      Click image for larger version

Name:	db.jpg
Views:	1
Size:	76.4 KB
ID:	266113
                      Comments are based on opinion...not always facts....that's why people use an alias.

                      Comment

                      • ians
                        Diamond Member

                        • Apr 2010
                        • 3943

                        #26
                        At least lightning protection was installed ... it must have been when the regs changed a few years ago and everyone got into a flat spin over lightning protection ...sales went through the roof.

                        It makes you wonder about regulations changes ... a family member or friend has an idea to invest in a product ... they invest a few million and suddenly there is a new regulations which forces everyone to use a specific product ... nothing would surprise me.

                        Load shedding ... generators ... solar ... inverter ... battery sales go through the roof ... I recall when the first round of load shedding started ... this kind of stuff makes you think.
                        Comments are based on opinion...not always facts....that's why people use an alias.

                        Comment

                        • ians
                          Diamond Member

                          • Apr 2010
                          • 3943

                          #27
                          This is an example of why random checks should be done on all COC's ... and you as a customer have to ask yourself ... all these rules and regs ... associations and legal documents and thing is the crap we have to accept ... this by the way is not some semi skilled ... picked up at builders or on the street corner ... this is a property run by a property management group using a registered electrical company ... issuing COC's

                          I was called out because my customer move into this property ... the earth leakage was tripping ... this is what I found ... the bare earth connected to a piece of red wire connected to the mcb ... with red tape wrapped around it.

                          I dont blame the semi skilled dumped on site ... I blame the person/people who are playing all day while their teams are working on site with no supervision ... it boils down to bad management or should or should I say the lack of it.



                          Click image for larger version

Name:	earth live.jpg
Views:	1
Size:	62.3 KB
ID:	266114
                          Comments are based on opinion...not always facts....that's why people use an alias.

                          Comment

                          • Derlyn
                            Platinum Member
                            • Mar 2019
                            • 1765

                            #28
                            Originally posted by ians
                            Google
                            Thanks. My garden boy uploaded it, so don't take it too seriously.

                            Comment

                            • ians
                              Diamond Member

                              • Apr 2010
                              • 3943

                              #29
                              These pics are the top row of the same DB in the pic below ... would you be happy adding a supplementary certificate to this Initial certificate ? I knw we are talking about no original COC ... does it help getting an original.

                              As a customer ... what do you do ... trust the electrical industry to test and issue a COC ... who do you trust ... DOL ... AIA ... ECA ... ECB or any other ass. ?

                              Then you have the insurance industry ... let me rather just leave it right here ... anyone who tried to claim will know why.

                              I am tired of being the Ahole in the industry ... the one who use to waste time reporting ... sits in meeting so that people cant baffle customers with bullshyte ... its about time whoever is the big chief of the electrical industry grows a set of balls and actually starts cleaning up the mess

                              Click image for larger version

Name:	hot spot 1.jpg
Views:	1
Size:	56.3 KB
ID:	266115

                              Click image for larger version

Name:	hot spot 3.jpg
Views:	1
Size:	55.4 KB
ID:	266116

                              Click image for larger version

Name:	hot spot.jpg
Views:	1
Size:	63.1 KB
ID:	266117
                              Comments are based on opinion...not always facts....that's why people use an alias.

                              Comment

                              • ians
                                Diamond Member

                                • Apr 2010
                                • 3943

                                #30
                                Derek ... I am not joking ... I went to google ... I typed in what I was looking for ... copied and pasted it here. I couldnt even tell you which site I got it ... I dont take note where I get the info ... maybe I should with all the new rules and laws ... it could get me into trouble.

                                Originally posted by Derlyn
                                Thanks. My garden boy uploaded it, so don't take it too seriously.
                                Comments are based on opinion...not always facts....that's why people use an alias.

                                Comment

                                Working...