Re setting a prepaid meter

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Derlyn
    Platinum Member
    • Mar 2019
    • 1761

    #1

    Re setting a prepaid meter

    Morning

    During the last spate of load shedding, I was called out on a number of occasions for prepaid meters not switching on again after load shedding.

    When this happens, the display is normal, showing the units available, but the internal contactor has not energised. Don't know why this happens.

    Here is the solution without having to contact the supply authority.

    On Conlog meters, type in the following code: 5649 3153 7254 5031 3471
    For ALL other meter types, type in the following code: 0000 0000 0001 5099 7584

    The above codes trip and reset the meter a couple of seconds later and the contactor will then energize.

    The above scenario seems to occur more with Conlog meters as all these callouts have been to Conlog meters.


    Important:

    Should the meter be of the type with a battery powered remote unit, the meter can still be tripped using the above codes, but it will not
    switch on automatically after a few seconds. The code needs to be punched in a second time to switch the meter on again.
    Make sure the batteries in the remote unit are good otherwise it ain't gonna work.

    Hope this helps.
  • Isetech
    Platinum Member

    • Mar 2022
    • 2274

    #2
    A handy bit of info, thanks.

    I see some of the prepaids venders are offering smart meters, have you you installed any of them, if so how smart are they ? Do they offer a daily total like the CBI and sonoff units?

    By the way the crimper has busy with many 35 mm battery cables.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

    Comment

    • Derlyn
      Platinum Member
      • Mar 2019
      • 1761

      #3
      No. Vodacom apparantly have their own installers for the smart meters. Here they are using Hexing. No meter base. The meter itself is fixed to the wall with hilty's. No anti tamper mode. If the cover is removed, a tamper flag is sent to the service provider.

      Comment

      • Lesiba325
        New Member
        • Sep 2022
        • 2

        #4
        Hi there I've been searching for hours for a solution... I tried the above codes and the conlog one seems to reset but the machine as it flashes and starts showing all sorts of numbers but doesn't restore electricity.
        I've got a landis gyr meter

        Please help.🙏

        Comment

        • Derlyn
          Platinum Member
          • Mar 2019
          • 1761

          #5
          Is there a smiley face showing on the display ?

          Comment

          • Lesiba325
            New Member
            • Sep 2022
            • 2

            #6
            Originally posted by Derlyn
            Is there a smiley face showing on the display ?
            No it still shows sad face and a broken circuit

            Comment

            • Derlyn
              Platinum Member
              • Mar 2019
              • 1761

              #7
              That meter has been tampered with. It's in tamper mode. A tamper coupon is required from the administrators of the meter. No other way.

              Comment

              • Kurt1983
                New Member
                • Sep 2022
                • 1

                #8
                Hi. My hexing 110 p show a smile face and open circuit we have tried the code and it switch the power on and then after a while it goes of again. There is enough credit loaded.
                Any Ideas?

                Comment

                • Dylboy
                  Gold Member

                  • Jun 2020
                  • 777

                  #9
                  Is their and inverter installed in the house ? It may be backfeedind and then shutting down the meter

                  Sent from my CPH2197 using Tapatalk

                  Comment

                  • acprinsloo
                    New Member
                    • Oct 2022
                    • 2

                    #10
                    Good evening . I've got a conlog prepaid meter. When I'm cooking on my stove if I switch on the kettle my prepaid meter trips is there anyway I can adjust the load limit on meter so can draw more appliances at once

                    Comment

                    • Derlyn
                      Platinum Member
                      • Mar 2019
                      • 1761

                      #11
                      Originally posted by acprinsloo
                      Good evening . I've got a conlog prepaid meter. When I'm cooking on my stove if I switch on the kettle my prepaid meter trips is there anyway I can adjust the load limit on meter so can draw more appliances at once
                      The administrator of the meter will have the codes to set the tripping current.

                      What size is your main breaker ?

                      If it's a Municipal meter and there are more than one meter on the erf, then the tripping current is reduced by them.

                      Comment

                      • acprinsloo
                        New Member
                        • Oct 2022
                        • 2

                        #12
                        Originally posted by Derlyn
                        The administrator of the meter will have the codes to set the tripping current.

                        What size is your main breaker ?

                        If it's a Municipal meter and there are more than one meter on the erf, then the tripping current is reduced by them.
                        Thanks will make a turn by municipal regards

                        Comment

                        • Raolane Thabo
                          New Member
                          • Dec 2022
                          • 2

                          #13
                          Hi. I have a conlog meter, it's on tempering mode since the last loadshedding schedule. I tried resetting but still can't engage. What more can I try.
                          Thanks
                          Your help is appreciated

                          Comment

                          • Derlyn
                            Platinum Member
                            • Mar 2019
                            • 1761

                            #14
                            Only the administrator of the meter can assist with resetting a tamper.

                            Municipality, Eskom or private administering company, whichever is relevant.

                            Comment

                            • Linnels29
                              New Member
                              • Apr 2023
                              • 1

                              #15
                              Originally posted by Derlyn
                              Morning

                              During the last spate of load shedding, I was called out on a number of occasions for prepaid meters not switching on again after load shedding.

                              When this happens, the display is normal, showing the units available, but the internal contactor has not energised. Don't know why this happens.

                              Here is the solution without having to contact the supply authority.

                              On Conlog meters, type in the following code: 5649 3153 7254 5031 3471
                              For ALL other meter types, type in the following code: 0000 0000 0001 5099 7584

                              The above codes trip and reset the meter a couple of seconds later and the contactor will then energize.

                              The above scenario seems to occur more with Conlog meters as all these callouts have been to Conlog meters.


                              Important:

                              Should the meter be of the type with a battery powered remote unit, the meter can still be tripped using the above codes, but it will not
                              switch on automatically after a few seconds. The code needs to be punched in a second time to switch the meter on again.
                              Make sure the batteries in the remote unit are good otherwise it ain't gonna work.

                              Hope this helps.
                              Hi there. My prepaid electricity meters keypad is not working. Some keys don't work at all. Others when I press them all that comes up is an 8. I have been trying for a month to get eskom out to see if it can be repaired but I haven't heard back from a single person and I am running out of units and unable to put more in.

                              My box is a Landis+Gr, Sabre type 10-SA012, single phase. It shows a happy face. No error codes. The keypad just won't work. Any ideas on how to maybe fix it? Thanks.

                              Comment

                              Working...