Not sure how ECA got to that statement and would be interested as to who made that statement
SANS 10142-1 Ed3.1 Clause 6.12.3.2 (e) is pretty clear that all earth terminals shall have an earth - To make a statement that any fitting above 2,5m does not have to be earthed , in my opinion, means that person has not understood what he read. Feel free to correct me
6.12.3.1 The following conductive parts shall be earthed:
a) all exposed conductive parts of an installation other than those described
in 6.12.3.2;
NOTE Metal enclosures on PVC conduit should be earthed if they can become live
and can be touched.
b) all conductive cable sheaths and armouring, wireways and catenary wires;
c) the earthing terminal of a socket-outlet;
d) the secondary winding of a transformer if it is not a safety transformer;
e) earthing terminals of all permanently connected electrical equipment and
appliances;
f) conductive parts of discharge luminaires and equipment that need special
earthing arrangements; and
g) all class I equipment.
SANS 10142-1 Ed3.1 Clause 6.12.3.2 (e) is pretty clear that all earth terminals shall have an earth - To make a statement that any fitting above 2,5m does not have to be earthed , in my opinion, means that person has not understood what he read. Feel free to correct me
6.12.3.1 The following conductive parts shall be earthed:
a) all exposed conductive parts of an installation other than those described
in 6.12.3.2;
NOTE Metal enclosures on PVC conduit should be earthed if they can become live
and can be touched.
b) all conductive cable sheaths and armouring, wireways and catenary wires;
c) the earthing terminal of a socket-outlet;
d) the secondary winding of a transformer if it is not a safety transformer;
e) earthing terminals of all permanently connected electrical equipment and
appliances;
f) conductive parts of discharge luminaires and equipment that need special
earthing arrangements; and
g) all class I equipment.



.
Comment