    My Friday brainfreeze

    Looking at circuit No1.

    10V transformer with centre tap at 5V.
    Lamp 1 has 5V across it. Lamp 2 also has 5V across it. Easy peezy.

    Now looking at circuit No2.

    Same transformer with the lamps connected slightly different.
    What voltage would one expect to get across lamp 1 and lamp 2.

    I've hit a blank.

    Click image for larger version

Name:	Scan_20220715_152314.jpg
Views:	1
Size:	26.2 KB
ID:	269970
  • Isetech
    Platinum Member

    • Mar 2022
    • 2274

    #2
    That is what is referred to as an auto transformer. You would connect the lights as per figure 2

    0V is the ground reference

    A-C -= 10 V

    B-C = 5 V

    We have them on the control circuits for the machines (because it is cheaper).

    Normally 400 V - 230/110/24 V
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

    Comment

    • Derlyn
      Platinum Member

      • Mar 2019
      • 1748

      #3
      What I am finding difficult to understand is that if you have 10V across lamp 1 (A-C ) and 5V across lamp 2 (B-C) then because series voltages are added, you should get 15V across both lamps (A-B) but the transformer is only 10 Volts.

      Comment

      • Derlyn
        Platinum Member

        • Mar 2019
        • 1748

        #4
        Ok. Problem solved.

        Not really a problem.
        Just a complicated way of drawing a simple circuit.

        I have redrawn circuit 2 simpler and found the lamps not to be in series.

        Sorry guys. This is NTC 1 stuff but sometimes one hits a blank.

        Have a lekker weekend.


        Click image for larger version

Name:	Scan_20220716_091001.jpg
Views:	1
Size:	23.2 KB
ID:	266190

        Comment

        • Justloadit
          Diamond Member

          • Nov 2010
          • 3518

          #5
          Just to add into the mix here, what if the winding A-B was inverted, in other words when the transformer was wound, they used 2 secondaries, and then made a connection for the centre?

          Would you measure 5V between A-B and B-C?
          Now what would the voltage be between A-C - 10V or 0V?
          Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
          Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

          Comment

          • Isetech
            Platinum Member

            • Mar 2022
            • 2274

            #6
            Originally posted by Justloadit
            Just to add into the mix here, what if the winding A-B was inverted, in other words when the transformer was wound, they used 2 secondaries, and then made a connection for the centre?

            Would you measure 5V between A-B and B-C?

            Now what would the voltage be between A-C - 10V or 0V?
            Then you would have a V-O-V transformer and it would apply the same as the generators.

            110V - 0V - 110V (A - B - C)

            A-C would be 220V
            Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

            Comment

            • Justloadit
              Diamond Member

              • Nov 2010
              • 3518

              #7
              Originally posted by Derlyn

              [ATTACH=CONFIG]8591[/ATTACH]
              Originally posted by Isetech
              Then you would have a V-O-V transformer and it would apply the same as the generators.

              110V - 0V - 110V (A - B - C)

              A-C would be 220V
              The above picture marked as #1 is a V - 0 - V
              It has all to do with the phase of the voltages being measured.
              A - is the start of the winding, and ends at B
              B - is the start of the second winding, and ends at C.
              When the AC wave goes positive, it is in phase in both windings simultaneously, and you will measure the 10V between A and C

              The scenario I refer to, is that the first winding starts at A, and ends at B
              The second winding starts at C and ends at B.
              So when the AC wave goes positive in the A-B winding, the wave goes negative in the B-C so when you measure from A to C, you will measure 0V.

              Sometimes when a transformer has 2 secondary windings, and we wish to double up on the current, then it is very important to identify the start of each winding when you connect them in parallel, if not then you would be shorting the transformer out.
              Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
              Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

              Comment

              • Derlyn
                Platinum Member

                • Mar 2019
                • 1748

                #8
                @justloadit. Yep. That was a test that the tutor loved giving us as appies.

                We used a battery and an analogue voltmeter. You would flick on the primary with the battery and check which way the needle deflected on the voltmeter connected on the secondary.

                Same test used on 3 phase motors to check the 3 windings for phasing.

                Interesting stuff.

                Comment

                • Isetech
                  Platinum Member

                  • Mar 2022
                  • 2274

                  #9
                  That why it is important to understand if it is a double would or an auto transformer.

                  A 3 phase motor for example can in some cases can be used as a 230 or 400 V 3 phase motor depending on the bridge pieces (star or delta)

                  That is why it is so important to read the name plate and data sheet.