    I have downloaded the requirements for our local metro, to register the systems we install, apparently it is a long slow process. So I need to read the guidelines and understand the requirements. This is going to be the interesting part.

    I have a ECSA registered engineer who has also completed the solar courses so he is green card certified. I am an MIE with 40 years hands on experience in the elctrical industry in everything from large scale industrial sites like Alsusaf, Mondi, RBM, even pharmaceutically labs, down to commercial building, banks and shopping centre, hospitals, theatres, and even down to plugs in light in a domestic installation. I think between the 2 of us we should have enough qualifications
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

    Comment

    • Justloadit
      Diamond Member

      • Nov 2010
      • 3518

      #17
      Originally posted by Isetech
      To add to the panel requirements -

      11/ Earthing for the panels, I see some people feel the rails can be used and you only need to fit 1 earth lug.

      12/ Earthing back to the inverter.

      13/ Earth spikes.

      14/ Bonding it all together.

      15/ All the accessories for the earthing and bonding.
      Note that the PV frame earth, and DB electrical earth must not be connected. Each must have it's own earth path. The PV frame earth should be the shortest path to earth, and to the earth spike with a minimum of 6mm copper wire. This is to protect the system from a lightning strike on the roof or frame. You want to guide the electrical energy strike to earth, not to the house electrical earth. The earth on the inverter and electrical system is for the safety of the user in the case of a Live fault, in which the ELU will then disconnect the supply from the load/fault.
      Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
      Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

      Comment

      • Justloadit
        Diamond Member

        • Nov 2010
        • 3518

        #18
        Originally posted by Isetech
        Apparently the 8.8 kva doesnt have a heat sink, but rather fans on the side, we will look into that, one day when I get one to tinker with.
        The 8kVa does have a heatsink similar to the 5.5kVA, however because of the extra energy it has to contend with, it has a set of fans to help cool the heatsink when required.
        Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
        Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

        Comment

        • Isetech
          Platinum Member

          • Mar 2022
          • 2274

          #19
          Originally posted by Justloadit
          The 8kVa does have a heatsink similar to the 5.5kVA, however because of the extra energy it has to contend with, it has a set of fans to help cool the heatsink when required.
          You just cant see them to due to the design and cover over the back. Which makes me wonder about the chimney effect, why are the fans on the side of the unit and not the top, do the fins go from side to side. Anyone have a picture of Sunsynk units with the heat sinks exposed. I am learning about these systems so please bear with me, like everything I do, I start right at the bottom and make sure I understand "everything", it requires some really dumb question in the beginning but at least by the time I engage with customers or other installers I am not fool on site with a mouth full of teeth when being audited .
          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

          Comment

          • Isetech
            Platinum Member

            • Mar 2022
            • 2274

            #20
            I see the 8.8 kva doesnt have the same mounting plate as the 5 kva, making the installation a little more challenging if you dont use the bolts provided and dont get the holes 100 % in line. I will make an ally template with the holes so I can just put the level on top and drill through the holes, then use either the HUS3-A6 or P6.

            The fact that we dont need to worry about cooling up through the heat but rather side to side, means we can mount our panel directly to the bottom of the unit and not worry about restricting the air flow.

            I would have thought there would be vents at the top on the unit, heat rises, but maybe that was taken into to consideration while designing the covers.
            Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

            Comment

            • Dave A
              Site Caretaker

              • May 2006
              • 22810

              #21
              Originally posted by Isetech
              I would have thought there would be vents at the top on the unit, heat rises, but maybe that was taken into to consideration while designing the covers.
              You don't want vents at the top as this would be an easy route for dust and small objects to fall into the unit.
              Participation is voluntary.

              Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

              Comment

              • GCE
                Platinum Member

                • Jun 2017
                • 1473

                #22
                Originally posted by Isetech
                Then we need a solar calculator. I see there calculators, if we get more than 10 installs (6 so far, 4 to go) , then I will get a paid version.



                If you know of any good free calculators, let us know.
                Try this one - Works well and allows you to customize settings to suit

                OpenSolar provides class-leading solar design accuracy, customer proposals and end-to-end tools to manage and grow your solar business, free.

                Comment

                • GCE
                  Platinum Member

                  • Jun 2017
                  • 1473

                  #23
                  Originally posted by Justloadit
                  Note that the PV frame earth, and DB electrical earth must not be connected. Each must have it's own earth path. The PV frame earth should be the shortest path to earth, and to the earth spike with a minimum of 6mm copper wire. This is to protect the system from a lightning strike on the roof or frame. You want to guide the electrical energy strike to earth, not to the house electrical earth. The earth on the inverter and electrical system is for the safety of the user in the case of a Live fault, in which the ELU will then disconnect the supply from the load/fault.
                  I have to disagree with your statement
                  The PV panels and frame work is part of the electrical installation and needs to be earthed through the normal wiring back to the inverter and D/Board.

                  The PV panels and frame work cannot be part of a Lightening protection design - The lightening protection design and install would be a separate earth using the shortest route along with lightening rods effectively above the panels to keep the panels out of a lightening zone.

                  I would regard the PV panels etc similar to say Stadium lighting - You would earth the light fittings as per normal SANS but then install a separate lightening protection rod above the light fittings with a earth conductor directly into the ground below the mast.

                  Pasted from SANS what I feel is relevant

                  7.12.7 Additional requirements for photovoltaic (PV) and similar
                  installations that provide a supply as an alternative to the main supply
                  7.12.7.6 If applicable, all exposed conductive parts may require earthing as
                  prescribed in 6.12.3.


                  6.12.3 Earthing of exposed conductive parts
                  6.12.3.1 The following conductive parts shall be earthed:
                  a) all exposed conductive parts of an installation other than those described
                  in 6.12.3.2;
                  NOTE Metal enclosures on PVC conduit should be earthed if they can become live
                  and can be touched.
                  b) all conductive cable sheaths and armouring, wireways and catenary wires;
                  c) the earthing terminal of a socket-outlet;
                  d) the secondary winding of a transformer if it is not a safety transformer;
                  e) earthing terminals of all permanently connected electrical equipment and
                  appliances;
                  f) conductive parts of discharge luminaires and equipment that need special
                  earthing arrangements; and
                  g) all class I equipment.

                  6.12.3.3 Metallic frames and metallic enclosures of electrical equipment shall
                  be made electrically continuous
                  .

                  Comment

                  • Isetech
                    Platinum Member

                    • Mar 2022
                    • 2274

                    #24
                    Originally posted by Dave A
                    You don't want vents at the top as this would be an easy route for dust and small objects to fall into the unit.
                    Have you looked at the dust cover on the side of your inverter I keep telling people, please clean your dust cover on the fan, top or side they still collect dust.
                    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                    Comment

                    • Justloadit
                      Diamond Member

                      • Nov 2010
                      • 3518

                      #25
                      Originally posted by GCE
                      I have to disagree with your statement
                      The PV panels and frame work is part of the electrical installation and needs to be earthed through the normal wiring back to the inverter and D/Board.

                      The PV panels and frame work cannot be part of a Lightening protection design - The lightening protection design and install would be a separate earth using the shortest route along with lightening rods effectively above the panels to keep the panels out of a lightening zone.

                      I would regard the PV panels etc similar to say Stadium lighting - You would earth the light fittings as per normal SANS but then install a separate lightening protection rod above the light fittings with a earth conductor directly into the ground below the mast.

                      Pasted from SANS what I feel is relevant

                      7.12.7 Additional requirements for photovoltaic (PV) and similar
                      installations that provide a supply as an alternative to the main supply
                      7.12.7.6 If applicable, all exposed conductive parts may require earthing as
                      prescribed in 6.12.3.


                      6.12.3 Earthing of exposed conductive parts
                      6.12.3.1 The following conductive parts shall be earthed:
                      a) all exposed conductive parts of an installation other than those described
                      in 6.12.3.2;
                      NOTE Metal enclosures on PVC conduit should be earthed if they can become live
                      and can be touched.
                      b) all conductive cable sheaths and armouring, wireways and catenary wires;
                      c) the earthing terminal of a socket-outlet;
                      d) the secondary winding of a transformer if it is not a safety transformer;
                      e) earthing terminals of all permanently connected electrical equipment and
                      appliances;
                      f) conductive parts of discharge luminaires and equipment that need special
                      earthing arrangements; and
                      g) all class I equipment.

                      6.12.3.3 Metallic frames and metallic enclosures of electrical equipment shall
                      be made electrically continuous
                      .
                      Note what you have mentioned, however if you look at the construction of a PV panel, there is no way, even a catastrophic failure of the cells that the electrical part of the PV circuit will ever come into contact with the frame, as the cells are encased in a glass and plastic film which is then glued into the frame. It is like saying that you need to connect each window frame in a house to your electrical earth.

                      I agree that adding lightning rods improves lightning protection, however in the majority of cases, the PV frames are below the highest point of the roof, and the earthing that I stated earlier, would be to dissipate any excess energy in the area during the lightning strike.

                      Yes an installer could tie the PV cable to the frame, and some mechanical issue could cause the failure of the PV cable sheath, and the inner metallic cable then could be exposed and shorted to the frame and create an issue.

                      all exposed conductive parts may require earthing as
                      prescribed in 6.12.3.
                      A PV panel by design has no exposed conductive paths unless some one cuts the premade cables and moulded connectors
                      Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                      Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                      Comment

                      • MPAD
                        New Member
                        • May 2023
                        • 5

                        #26
                        Is this type of issue a concern?

                        Click image for larger version

Name:	WhatsApp Image 2023-07-17 at 6.24.53 PM (1).jpg
Views:	1
Size:	46.7 KB
ID:	266278

                        Comment

                        • Isetech
                          Platinum Member

                          • Mar 2022
                          • 2274

                          #27
                          What we have learnt from lightning experiences, no matter what you install, if any part of your installtion is hit by lightning, chances are good that you will be replacing a lot of the components. So best you just make sure that whatever you install is insurance approved, thats all that counts at the end of the day. I read the policiy carefully then decide what route to take with regards to lightning/surge protection.

                          A word of advice, we got a letter from our insurance recently, to notify us that we are no longer covered for surge related damages, only lightning, if you going to claim, make sure you read your policy and verify that there was lightning on the day, trust me the last claim I dealt with, only a small portion of the claim was paid, the broker actually took out his phone checked the date of the claim and pointed out to me that there was no storm on the day.







                          Originally posted by MPAD
                          Is this type of issue a concern?

                          [ATTACH=CONFIG]8786[/ATTACH]
                          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                          Comment

                          • Isetech
                            Platinum Member

                            • Mar 2022
                            • 2274

                            #28
                            With the little experience we have installing inverters, generally we seem to be geting it right, however on some of the sites where I have advised customers to stick to the plan, they have indicated they are happy to do it their way.

                            One of the sites where the customers requested that we dont split the essential and non essential and as expected we got the call for a F54 fault.

                            Another issue we have experienced, with a load that has been split into essential and non essential, we had an F14 fault during load shedding. The lesson to learn from this, if you install a inductive load (no matter how small) on the essential side of the DB, make sure you allow for the startup current or make sure that the inductive load is connected to a VSD or some form of soft start. Examples of this, aircons, booster pumps for water storage, etc
                            Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                            Comment

                            • Isetech
                              Platinum Member

                              • Mar 2022
                              • 2274

                              #29
                              How we have grown since the start of this thread.

                              Was busy searching safe isolation procedure and this popped up.
                              Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.