Neutral earth bonding on backup systems.

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Isetech
    Platinum Member

    • Mar 2022
    • 2274

    #1

    Neutral earth bonding on backup systems.

    It seems there little confusion amongst electricians with regards to when you should do neutral earth bonding and when you shouldn't, types of earthing systems and which are used and when.

    Some say you have to permanently bond an inverter and others believe a relay must be used to prevent circulating currents and other.

    Some cant tell the difference between a generator and a UPS and wiring configuration required for each.

    A generator doesn't have an internal changeover switch so an external changeover over switch is required. It all by law doesn't require islanding mode, but does require mechanical isolation to prevent both supplies running together.

    An inverter/UPS on the other hand is different beast, with all sorts of complex electronics, bi-directional flow on the input, a built in changeover switch and required by law to go into islanding mode when the grid power switches off.

    What are your thought on earth neutral bonding for a generator and a UPS, is it the same thing?

    Do you feel a relay should be used to bond the neutral/earth or permanently bonded on the output of the inverter.

    Do you feel the SANS regs adequately cover this topic.

    But most important do you understand the different earthing systems feeding the property and why you actually require a neutral/earth.

    When a neutral/earth bond is dangerous.

    What are the implications of neutral earth bonding on the property if the earthing system a TN-S

    Can you go from a TN-C to a TN-C-S to a TN-S all in one elctrical installation.

    Who thought this could become so complicated, add a bidirectional hybrid inverter with a generator and a few solar panels and boy do we have a mix.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.
  • Dylboy
    Gold Member

    • Jun 2020
    • 777

    #2
    100% this is not covered enough and also not at all.

    There are a lot of things I agree. TN-C-S can be dangerous, so knowing if yo use a relay or permanent bond is important, also will it ever change.

    With inverters is it an appliance so bonding the output permanent will it matter ?

    There is so so much to learn and to try and learn is very difficult.

    Not enough training of what matters as most who install don't even know what the Earth is for other than a draw wire...

    Sent from my CPH2197 using Tapatalk

    Comment

    • GCE
      Platinum Member
      • Jun 2017
      • 1495

      #3
      Originally posted by Dylboy

      With inverters is it an appliance so bonding the output permanent will it matter ?

      There is so so much to learn and to try and learn is very difficult.

      Not enough training of what matters as most who install don't even know what the Earth is for other than a draw wire...

      Sent from my CPH2197 using Tapatalk
      We are listening to too much noise being create by so called Solar experts that have never studied or worked in the electrical industry , picked up scraps and trying to make it sound like there are no regulations so they can continue without abiding by any rules .

      An inverter is not an appliance . ( That is solar talk for I don't have to be an electrical contractor or issue a COC to install an inverter.)

      An inverter is " electrical equipment " as per definition in SANS 10142-1

      3.32
      electrical equipment

      item or any combination of items, including wireways, which is used for the
      generation
      , conversion (such as of voltage or frequency), transmission or
      distribution of electrical energy


      and is part of the electrical installation as per definition 3.33 and definition 3.16

      3.33
      electrical installation

      machinery, in or on any premises, that is used for the transmission of electrical
      energy from a point of control (see 3.56) to a point of consumption
      (see 3.55) anywhere on the premises, including any article that forms part of
      such an installation
      , irrespective of whether or not it is part of the electrical
      circuit, but excluding


      3.16
      consumer

      person who is supplied (or who is to be supplied) with electricity by a supplier
      (see 3.77); or a person who supplies his own electricity



      Now if you now start thinking electrical and check regulations for Electrical the rest becomes str forward .

      An inverter is treated the same way as a generator - 7.12

      7.12 Alternative supplies
      NOTE Alternative supplies include but are not limited to low-voltage generating sets,
      photovoltaic (PV) installations, gas generators, diesel generators, wind turbines and
      hydropower plant.


      Reset the mind- forget all the Solar talk noise from people who are trying to convince themselves and clients , that it is not electrical.

      Comment

      • GCE
        Platinum Member
        • Jun 2017
        • 1495

        #4
        The earthing

        When a generator is connected to an installation and you running off mains you may not earth the neutral ( 6.1.6 ) - when mains fails and the generator supplies power you must earth the neutral - This is why you use a D/pole change over or 4 Pole change over

        Same story with an inverter - The mains is fed directly to the output during mains on - When mains fails then the relay switches and you feed power from the Inverter/Battery side of the relay .
        Some units automatically bridge neutral earth others you need to do the bridge .
        To find out if it has an automatic bridge , carry out loop test , if the readings are crappy then it does not have and you need to make a plan .
        On a generator you would open the terminal box on the genset and install a bridge wire . On an inverter you would need to open the unit trace the circuits , find the relay and install a bridge on the correct side of the relay. Electricians fingers are to big to work inside those little boxes and warranties could become a problem along with grid tie circuits so it is easier to just install a relay/contactor on the output of the inverter that will do the bridging where our big fingers can work in peace.
        If the inverter has an output to operate that relay , easy , if not then use the mains to power the relay and when mains falls away the bridge between earth and neutral happens through the relay/contactor.

        I have had one of my guys get that confused look with a relay until you explain it is a light switch , just has burst of power to change the state of it , not a finger.

        If you think it is not covered in the regulations then look at 7.16.4
        When Mains fails then the inverter becomes the supply and you need to ensure that it passes the tests

        Remember that a test report needs to be done for mains supply and for alternative supply when it is on .

        If you listen to solar talk - They say tick alternate supply , job finished - A BIG NO - Tick alternative supply then another test report needs to be attached to the COC ( 8.6.1)

        The regulations are there , they explain most of what needs to be explained just don't get confused with Solar talk


        8.6.1 General
        NOTE Conduct all tests and complete a copy of the test report for each distribution
        board and supply (normal and alternative supplies). Amdt 1



        6.1.6 The neutral conductor shall not be connected direct to earth or to the
        earth continuity conductor on the load side of the point of control except as
        allowed in 7.16.4


        7.16.4 Neutral earthing
        7.16.4.1 Whereas TN-C systems may be implemented along the distribution
        system backbone, the individual service connections at every distribution
        kiosk shall be TN-S.
        7.16.4.2 From the point of supply to each user or part of a communal
        installation, the neutral and earth conductors shall be separate conductors.
        7.16.4.3 Wherever the neutral is connected to the earth, a warning notice
        shall be fitted to the outside of each distribution kiosk in the distribution
        system, indicating "Neutral earthed inside".
        7.16.4.4 A clear notice shall be fitted at the combined neutral-earth
        connection inside each distribution kiosk in the distribution system, that
        prohibits the removal of this connection while the supply is alive, or might
        become alive.
        7.16.4.5 The neutral shall not be earthed beyond any earth leakage unit.
        7.16.4.6 A TN-S system shall not be converted to a TN-C system.

        Comment

        • Isetech
          Platinum Member

          • Mar 2022
          • 2274

          #5
          Didn't you do PV training?

          Originally posted by Dylboy
          100% this is not covered enough and also not at all.

          There are a lot of things I agree. TN-C-S can be dangerous, so knowing if yo use a relay or permanent bond is important, also will it ever change.

          With inverters is it an appliance so bonding the output permanent will it matter ?

          There is so so much to learn and to try and learn is very difficult.

          Not enough training of what matters as most who install don't even know what the Earth is for other than a draw wire...

          Sent from my CPH2197 using Tapatalk
          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

          Comment

          • Isetech
            Platinum Member

            • Mar 2022
            • 2274

            #6
            The biggest concern is safety.

            If you bond the neutral earth, while in grid mode, would circulating current become a danger?

            IF you fit a relay and it fails, what are the dangers, the system voltage becomes unstable the N-E voltage increases to dangerous levels?

            Do you think that P1 or P3 is applicable for Annex P. P3 seems more suitable for inverters. Considering P1 indicates an external changeover, however an inverter is more like a UPS?
            Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

            Comment

            • Dylboy
              Gold Member

              • Jun 2020
              • 777

              #7
              Originally posted by Isetech
              Didn't you do PV training?
              No not yet, still want to but not yet, mostly I want to sit with the tech people at the big inverter companies and really learn the inner workings of each one. Each inverter has its proprietary things and knowing that will help a lot.

              Sent from my CPH2197 using Tapatalk

              Comment

              • Dylboy
                Gold Member

                • Jun 2020
                • 777

                #8
                GCE you right, lots of noise and talk...

                It is a generator.

                It takes me a full week plus some to do an inverter, I know guys doing them in 2 days... The amount wrong in them all is plenty. They get in a spark to do the DB and they mount pretty looking invertes on a wall that fail a lot of things

                Sent from my CPH2197 using Tapatalk

                Comment

                • Isetech
                  Platinum Member

                  • Mar 2022
                  • 2274

                  #9
                  Why is everyone referring to an inverter as a generator and not a UPS? It looks like a UPS, it has batteries like a UPS, it converts DC to AC like a UPS, It even has the same output voltage reading as a UPS, it has a display like a UPS, it must be a UPS.

                  If it looks like .... , it smells like .... it must be ....

                  Originally posted by Dylboy
                  GCE you right, lots of noise and talk...

                  It is a generator.

                  It takes me a full week plus some to do an inverter, I know guys doing them in 2 days... The amount wrong in them all is plenty. They get in a spark to do the DB and they mount pretty looking invertes on a wall that fail a lot of things

                  Sent from my CPH2197 using Tapatalk
                  Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                  Comment

                  • GCE
                    Platinum Member
                    • Jun 2017
                    • 1495

                    #10
                    Originally posted by Isetech
                    The biggest concern is safety.

                    If you bond the neutral earth, while in grid mode, would circulating current become a danger?

                    IF you fit a relay and it fails, what are the dangers, the system voltage becomes unstable the N-E voltage increases to dangerous levels?

                    Do you think that P1 or P3 is applicable for Annex P. P3 seems more suitable for inverters. Considering P1 indicates an external changeover, however an inverter is more like a UPS?
                    The biggest problem with bonding earth and neutral while on mains is that if the star point at the minisub comes loose your star point could be the point for the complete minisub .
                    That 6sqmm or 4sqmm wire could look like a glow plug if you become the star point on an 800KVA minisub

                    A double pole CB feeding the inverter should then trip with the neutral currents

                    It is why 6.1.6 was written and why the municipalities all have it written into the bylaws

                    If you don't earth neutral when running without mains then no protection will work in the event of an earth fault .
                    Last edited by GCE; 04-Nov-22, 07:31 AM.

                    Comment

                    • GCE
                      Platinum Member
                      • Jun 2017
                      • 1495

                      #11
                      Originally posted by Isetech
                      Why is everyone referring to an inverter as a generator and not a UPS? It looks like a UPS, it has batteries like a UPS, it converts DC to AC like a UPS, It even has the same output voltage reading as a UPS, it has a display like a UPS, it must be a UPS.

                      If it looks like .... , it smells like .... it must be ....
                      It is easier to describe as a generator being fitted into the regulations and the fact that you normally have to check earth neutral bond , 4 pole switches , sync with mains , and it converts one form of energy into electricity , on a PV inverter anyway.

                      UPS is pretty standard fit into the installations due to the design

                      Comment

                      • Isetech
                        Platinum Member

                        • Mar 2022
                        • 2274

                        #12
                        The way I see it, in a normal domestic installation you should never have the generator connected to he mains while the grid connected. The inverters on the other hand are connected together with the grid and only when in islanding mode will it be disconnected/isolated from the grid.

                        When you connect a generator, it has mechanical interlocks which can be manually or automatically switched, but should never be connected at any point, hence the break before make contacts.

                        This is where I believe the confusion arises, when the grid and inverter are operating together, we were taught (right or wrong, that we can discuss another time) that you never bond the neutral/earth after the "point of supply" or at 2 points in an electrical TN-S installations.

                        While your essential supply (output of the inverter) is connected to the grid, there should never be a bond between neutral and earth.

                        The only time there should be a bond between neutral and earth is when the inverter is in islanding mode (disconnected from the TN-S system) at which point you create a TN-C before the essential DB, (output from the inverter) , at the essential DB, you would then create a TN-S system and at not point after the DB, should the neutral earth be bonded again.
                        Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                        Comment

                        • Isetech
                          Platinum Member

                          • Mar 2022
                          • 2274

                          #13
                          I believe the confusion is also created by annex P, P1 clearly indicating that all neutrals must be bonded to together and clearly indicating a completely separate unit, with a a combined a neutral/earth bond at the star point of the generator and an earth spike (another discussion for another discussion for another day)

                          However if you look at P3 which I see as representing an inverter, but is is not that simple because P1 is 3 phase and P3 is single phase and compared to a UPS would be feeding dedicated socket outlets which dont require earth leakage protection.

                          I wish more people would get involved in these discussion, because I believe it is very important to understand theses topics, rather than just follow the herd.

                          Just imagine a court case, with so many different opinions. If you could show evidence that you have looked at all the discussion on this topic, it would be difficult for anyone to prove that you have been negligent.

                          Something else you need to consider, you could argue that the manufacturer suggests the use of a relay, some might argue that you need to comply with the SANS regs, but if this discussion is taking place and the responses are so random, how do you decide.

                          I would suggest that someone with the right connections, contact the people who are responsible for the electrical industry, the DOL and request an official statement to clear up the confusion.

                          I am not saying anyone is anyone is right or wrong, my concern is the confusion around this topic.

                          I dont think we need to be too concerned because if either option was dangerous, something would have been done about it by now.
                          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                          Comment

                          • Isetech
                            Platinum Member

                            • Mar 2022
                            • 2274

                            #14
                            J.1 System earthing identification code
                            The first letter of the identification code denotes the relationship of the source of energy
                            to earth:

                            T one or more parts are connected direct to earth; or

                            I all live parts are isolated from earth or one point is connected to earth through
                            impedance.
                            The second letter of the identification code denotes the relationship of the exposed
                            conductive parts of the consumer's installation to earth:
                            T the exposed conductive parts of the consumer's electrical installation are
                            connected direct to earth, independently of the earthing of any point of the source
                            of energy; or

                            N the exposed conductive parts of the consumer's electrical installation are
                            connected direct to the source earth, which, in the case of an a.c. system, is usually
                            the transformer neutral point.
                            The designation TN is further subdivided depending on the arrangement of the neutral
                            and protective conductors. A further letter or letters denotes such arrangement, as
                            follows:

                            C the neutral and protective functions on the incoming supply and in the consumer's
                            electrical installation are combined in a single conductor;

                            S the neutral and protective functions on the incoming supply and in the consumer's
                            electrical installation are provided by separate conductors; and

                            C-S the neutral and protective functions on the incoming supply are combined in a
                            single conductor
                            Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                            Comment

                            • GrahamH
                              Junior Member
                              • Nov 2022
                              • 13

                              #15
                              Neutrals and earthing with Deye 8KW Inverter

                              Originally posted by Isetech
                              The way I see it, in a normal domestic installation you should never have the generator connected to he mains while the grid connected. The inverters on the other hand are connected together with the grid and only when in islanding mode will it be disconnected/isolated from the grid.

                              When you connect a generator, it has mechanical interlocks which can be manually or automatically switched, but should never be connected at any point, hence the break before make contacts.

                              This is where I believe the confusion arises, when the grid and inverter are operating together, we were taught (right or wrong, that we can discuss another time) that you never bond the neutral/earth after the "point of supply" or at 2 points in an electrical TN-S installations.

                              While your essential supply (output of the inverter) is connected to the grid, there should never be a bond between neutral and earth.

                              The only time there should be a bond between neutral and earth is when the inverter is in islanding mode (disconnected from the TN-S system) at which point you create a TN-C before the essential DB, (output from the inverter) , at the essential DB, you would then create a TN-S system and at not point after the DB, should the neutral earth be bonded again.
                              I completely agree with what you are saying, but I'm confused... I have a newly installed Deye 8KW inverter which is working just fine, however, the installation was not done exactly as per the User Guide which says that for South Africa, the neutral must be linked to Earth at the main board which is contrary to what I learnt many years ago. I can imagine many safety risks when there is more than one earth to neutral link along with any uncertainty regarding the quality of my own "local" earth. IE, any significant voltage difference between the incoming neutral from Eskom and "real" earth might cause my earthed devices not to be safe. (Hope I'm making sense)

                              The sample diagram for South Africa in the User Guide also shows that the inverter input and output neutrals are effectively connected together which prevents the output from floating when the grid is off of course. I have tried bridging them and it works fine. If the incoming neutral is connected to earth at the eskom transformer, then bridging the in and out neutrals removes the need to link earth to the output neutral?
                              Attached Files

                              Comment

                              Working...