Thank you so much! I know I have mentioned this before... In my case, I bought a pre-assembled board from the supplier with the Deye 8kVA and associated breakers, fuses etc. already mounted and connected. After I received it, I pointed out a number of things that didn't look right, however, the supplier said that if we change anything on the board then they won't honour the warranty. The problems I see with board are: exposed AC wiring (ok, the wires are insulated but not in a conduit/duct etc everywhere), no provision for grounding the neutral when off grid, inline breaker of 32 amps (~7.36kW) which is less than the 36.4 amps rated output current (~8 kW) for the inverter and only two thirds of the 50 amp max continuous pass-through rating when connected to the grid. They don't seem to agree that the inverter power is added to the grid power when grid-tied for a total of 50 amps - which would be maximum load of 11.5 KW at a PF = 1.
Neutral earth bonding on backup systems.
Collapse
X
-
There is a poll on social media, which indicates that more than 70% of inverter installations in SA have permanent bonds and only around only 30 % have a relay.
I stand to be corrected but I believe the majority vote on this platform is to install a relay.
Did someone mention grey areaComment
-
I know where to get a T-shirt if I need one
What is important is to understand the operation of the inverter. Make sure you are aware if an internal relay is used and if it has fail safe protection.
As pointed out by GCE, isolated from the grid/mains.
Some inverters like Victron and Deye/Sunsynk have built in relays.
Older Axpert type inverters dont have a relay. Axperts are branded many other names, like Meccer, Kodak, MCE, RCT and many others.
Must inverters I ahve worked with dont have relays.
Growatt, Schnieder I am not familiar with this product, maybe someone can share.Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.Comment
-
GCE, tell us more about being permanently isolated from the grid/mains.
An Axpert unit for example is not permanently isolated from the mains/grid. It would be like an online UPS which doesnt switch, instead it is isolated from the mains power via the internal components to product a clean pure sinewave ?Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.Comment
-
GCE, tell us more about being permanently isolated from the grid/mains.
An Axpert unit for example is not permanently isolated from the mains/grid. It would be like an online UPS which doesnt switch, instead it is isolated from the mains power via the internal components to product a clean pure sinewave ?
With an Earth loop on mains and you get good readings then the isolation is not there - If it is isolated your readings will not comply and the neutral will be " floating"Comment
-
From the little knowledge I have of Victron, the relay is integrated with the control of the inverter, which has fail safe protection for the relay, the power to the inverter switches off.
The way I understand the Deye/Sunsynk has relays in certain models (I dont know if they have built in fail safe protection) and the rest have a signal to a relay. The concern is what happens if the relays fails? What is the worse thing that can happen, or should I say what are the safety implications of a failed relay? The neutral will float creating a high touch voltage, making the installation dangerous ? If the neutral - Earht voltage exceeds 25 V , the installation should be shut down ? If you connect a device to monitor the neutral to earth voltage, if it exceeds 5 V it switches the power to the inverter off, problem solved and everyone is happy or not ?
Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.Comment
-
If an inverter is isolated from mains it will normally tell you in the manual alternatively you will pick it up when you test with earth loop tester.
With an Earth loop on mains and you get good readings then the isolation is not there - If it is isolated your readings will not comply and the neutral will be " floating"Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.Comment
-
I want to add the Victron has the E N relay but it is not good, it is delayed and causes havoc with the earth leakage. Installers now install their own contactor... Basically their is a time delay before it operates and that is what causes the issue.
Also Sunsynk, of you use the signal thing it is also delayed and causes havoc, so again install contactor that switches with grid.
Sent from my CPH2197 using TapatalkComment
-
The concern is what happens if the relays fails? What is the worse thing that can happen, or should I say what are the safety implications of a failed relay? The neutral will float creating a high touch voltage, making the installation dangerous ? If the neutral - Earht voltage exceeds 25 V , the installation should be shut down ? If you connect a device to monitor the neutral to earth voltage, if it exceeds 5 V it switches the power to the inverter off, problem solved and everyone is happy or not ?
If you have a D/Pole CB feeding the inverter and a D/pole out of the inverter and the relay does weld close and mains comes back then the D/pole CB will trip if the current draw on the neutral is excessive.
If you are using the normal open on the relay it will always close if the relay coil fails
Those measure should protect you , as the installer,Comment
-
I want to add the Victron has the E N relay but it is not good, it is delayed and causes havoc with the earth leakage. Installers now install their own contactor... Basically their is a time delay before it operates and that is what causes the issue.
Also Sunsynk, of you use the signal thing it is also delayed and causes havoc, so again install contactor that switches with grid.
Sent from my CPH2197 using TapatalkVictor - Knowledge is a blessing or a curse, your current circumstances make you decide!
Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.zaComment
-
Hi GCE :when mains fails and the generator supplies power you must earth the neutral - This is why you use a D/pole change over or 4 Pole change over .are we talking about earthing of the neutral of the gen here? Any possibility of a drawing pleaseComment
-
An inverter neutral earthing arrangement ?Comment
-
If you have a D/Pole CB feeding the inverter and a D/pole out of the inverter and the relay does weld close and mains comes back then the D/pole CB will trip if the current draw on the neutral is excessive.
If you are using the normal open on the relay it will always close if the relay coil fails
Those measure should protect you , as the installer,
If it fails it becomes a permanent bond ?
Which is why I ask, is it really that dangerous either way, if it was the DOL would have already stepped in and cleared up the confusion and manufacturers wouldnt selling units in SA with and without relays.
I have had so many different responses from so many different people at all levels (from electrical engineers to electricians).
The AIA have threated court cases, I am so looking forward to them living up to their promises. It been 40 years in this industry and I still havent seen any light at the end of a very dark tunnel. I have tried been a member of associations for more than 10 years, dealt with technical advisers and all I see is a crippled industry with so many loop holes that the ship is going down just as fast as the bankrupt energy producer.Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.Comment
-
Please feel free to correct me on the above.Comment