A 3 ph contactor with the 3 contacts parrallelled works well. The holding or aux contact can be used for indication that the bond has been made successfully.
Neutral earth bonding on backup systems.
Collapse
X
-
Firstly I agree that a relay should be fitted, however we need to understand the facts.
I am sure it has been discussed in great detail, what is rather concerning is how long it has been discussed and still no formal notice from the DOL, like all the other concerns in the solar industry. It seems that it is not that dangerous or important, otherwise it would have been finalized at least a year ago.
The ECA has submitted a document, however there is no formal response or notice from the DOL to verify the information , I hope to see one sooner than later, however from my understanding, the AIA is a "DOL" approved inspection authorities, who should also have a technical team just like the ECA, and who should also be represented on the SANS technical board.
It holds more water than a personal opinion as it comes from an Association that represents electrical contractors and was debated at length with technical reasoning behind it.
ECA will take it to SANS working group
And when I say debated at length , trust me that it was a lengthy and frustrating process
Now to get a statement out on battery placement /safety requirementsComments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.Comment
-
The relay to used should also be highlights and the operation of the inverter if the relay fails or is changed at any stage should be highlighted.
I tried something today, I removed the tick the islanding mode and the inverter normal light switched off and the red light and buzzer started flashing. The inverter didn't shut down or switch off the inverter output. I got message to say the grid setting had been changed. I need to verify that this was why the inverter reacted the way it did.Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.Comment
-
I look forward to this statement, this is a huge problem. People think running a cable to the garage and back is the quick in and out solution, however I believe it creates even bigger problems. Considering everyone is out to make a quick buck, thank goodness the public have tons of cash throw at the solar industry.
You have to ask yourself how 1st world countries have lithium batteries in the loft and even in the toilet, what do 3rd countries know that they dont?
This could explain why certain people threaten installers with court cases, but I we are yet to hear of one.
[QUOTE=GCE;172250
Now to get a statement out on battery placement /safety requirements[/QUOTE]Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.Comment
-
Firstly I agree that a relay should be fitted, however we need to understand the facts.
I am sure it has been discussed in great detail, what is rather concerning is how long it has been discussed and still no formal notice from the DOL, like all the other concerns in the solar industry. It seems that it is not that dangerous or important, otherwise it would have been finalized at least a year ago.
The ECA has submitted a document, however there is no formal response or notice from the DOL to verify the information , I hope to see one sooner than later, however from my understanding, the AIA is a "DOL" approved inspection authorities, who should also have a technical team just like the ECA, and who should also be represented on the SANS technical board.Comment
-
When the inverter goes into islanding mode, does the point of supply change from the installation main breaker to the inverter output breaker ?
If this is not the case, then irrespective of whether the bridge is permanent or through a relay, it still contradicts the regulation that says the neutral earth bridge must not be downstream of the point of supply.Comment
-
When the inverter goes into "Island" mode, a double pole internal relay contacts disconnect the input and output of the inverter.
So the point of supply now becomes the inverter. If there is no Neutral/Earth bond placed on the output of the inverter, then the ELU will not be able to detect an earth fault as it has now lost the 'Earth' path, placing the user in a dangerous environment.
Another reason for this Neutral/Earth connection, is also to ensure that the Inverter Live & Neutral lines to not rise above earth, which is usually the case because the inverter is isolated from the grid supply. This can become a few thousand Volts charging up, and in some cases when the Mains returns, and the inverter then connects the load to the mains, is when there is a discharge damaging the inverter.
It is the same principle, in which the secondary of a supply transformer, Neutral connection is made to Earth. It serves 2 purposes, 1 is used to detect faults, but the second reason which is little understood, is to ensure that the transformer secondary is tied to earth, and not allow the secondary voltage to rise way above earth and causing a discharge to earth during operation.Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.zaComment
-
I take it they have stopped threatening people with court action?
I was threatened with court action by a certain person from the AIA, I am still waiting.
There are too sheep, he said, they said, we said, I said in the electrical industry and not enough skilled electricians, people who can stand up, answer questions and understand why and how they came up with the answer, not just copy and paste information they find in social media groups.
That is why I enjoy this platform, we may not all agree with the answers, but at least we are prepared to thrash it out and offer some form of reasoning for the answer create a bit of banter.
Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.Comment
-
Question.
There are inverters that have an output intended to be used for a relay or contactor for neutral earth bridging purposes.
On these same inverters there's a time delay after the resumption of Eskom power before the inverter switches out of islanding mode. Sometimes about a minute.
My question is ......... at what point in time does the internal relay operate ? Is it on the resumption of mains power, or, is it when the inverter switches out of islanding mode ?Comment
-
The 60sec time delay switching back to grid is a Utility requirement and also gives the inverter time to sync with grid before switching - some inverters can be set to change back with a longer time delay .
We set all of ours above 10min to allow the voltage to settle - If I look at graphs from the inverters and depending on the time , 16h00 to 18h00 and 18h00 to 20h00 , being the worst slots the voltage comes back at 198v and takes around 10 minutes to settle at 220 to 230v
As far as I am aware the neutral earth bond stays for 10sec after connecting back to grid , coming out of islandingComment
-
Thank you my brother.
As an aside, on my house, all plug circuits are fed through a contactor.
The contactor is energised by means of an Ellies Fridge Safe unit that is plugged into a dedicated plug.
On resumption of power after loadshedding, that unit monitors the voltage for 3 minutes before switching on if the voltage is within standards.
So I am protecting all the plugs with one unit, the boere way.Comment
-
I am still learning.
Recently, our brother Justloadit, explained that one of the reasons the one end of the secondary of a supply transformer is connected to earth, is to prevent the secondary from drifting up to dangerously high voltages that can be in the thousands.
This is also one of the reasons that the neutral of an inverter output should be grounded.
My question is. ..... what prevents the output of a safety transformer from drifting upwards ?Comment
-
I am still learning.
Recently, our brother Justloadit, explained that one of the reasons the one end of the secondary of a supply transformer is connected to earth, is to prevent the secondary from drifting up to dangerously high voltages that can be in the thousands.
This is also one of the reasons that the neutral of an inverter output should be grounded.
My question is. ..... what prevents the output of a safety transformer from drifting upwards ?
Another consideration if you should have e/n bonding at your location as well as at the local transformer is that some of the current to your home will always be passing through the earth wire from the transformer since it will be in parallel with the neutral wire from the transformer. The earth wire and things that it may be connected to are not insulated, so any voltage difference (no matter how small) between the wire and 'real' earth (moist soil etc.) will result in corrosion. Remember that for current to pass through a wire, there has to be a voltage difference across it unless the wire's resistance is zero which is not possible. (Ohm's law)Comment