Morning
I see Nersa have published the latest update for NRS-097-2-1 Ed3 which amplifies the ECA stance on Neutral Earth Bonding
Extract pasted below and full document attached
5.4 Neutral to earth bonding when forming an intentional island
5.4.1 To prevent a SSEG neutral connection to the the utility neutral through an earth conductor when the SDU opens, the SSEG shall not have a permanent neutral bonding to earth.
5.4.2 A hybrid system intended to form an intentional island on the load side during utility supply interruption shall open the SDU to prevent unintentional island on the utility side.
5.4.3 Since the SDU opens the neutral on the utility side, the intentional island neutral shall be bonded to earth within 200 ms after the SDU operation using a neutral to earth bonding unit (NEB).
5.4.4 The NEB shall open within a time period of 200 ms before the SDU reconnects the inverter to the utility supply.
5.4.5 The NEB shall consist of an electromechanical switching device rated at the nominal current rating of the inverter
5.4.6 The total clearance between the inverter neutral and earth conductors when the NEB is switched off, shall be equal the clearance of the SDU in its open state or more.
5.4.7 The NEB shall be an internal inverter component or an external device that is activated by a dedicated control port of the inverter.
5.4.8 The inverter data sheets shall indicate that it contains an internal NEB or a dedicated NEB control port for external devices.
5.4.9 Installation requirement: Inverters equipped with the NEB control port only, shall have external electromechanical NEBs installed that are SANS/IEC 60947-1 and SANS/IEC 60947-4-1 certified
I see Nersa have published the latest update for NRS-097-2-1 Ed3 which amplifies the ECA stance on Neutral Earth Bonding
Extract pasted below and full document attached
5.4 Neutral to earth bonding when forming an intentional island
5.4.1 To prevent a SSEG neutral connection to the the utility neutral through an earth conductor when the SDU opens, the SSEG shall not have a permanent neutral bonding to earth.
5.4.2 A hybrid system intended to form an intentional island on the load side during utility supply interruption shall open the SDU to prevent unintentional island on the utility side.
5.4.3 Since the SDU opens the neutral on the utility side, the intentional island neutral shall be bonded to earth within 200 ms after the SDU operation using a neutral to earth bonding unit (NEB).
5.4.4 The NEB shall open within a time period of 200 ms before the SDU reconnects the inverter to the utility supply.
5.4.5 The NEB shall consist of an electromechanical switching device rated at the nominal current rating of the inverter
5.4.6 The total clearance between the inverter neutral and earth conductors when the NEB is switched off, shall be equal the clearance of the SDU in its open state or more.
5.4.7 The NEB shall be an internal inverter component or an external device that is activated by a dedicated control port of the inverter.
5.4.8 The inverter data sheets shall indicate that it contains an internal NEB or a dedicated NEB control port for external devices.
5.4.9 Installation requirement: Inverters equipped with the NEB control port only, shall have external electromechanical NEBs installed that are SANS/IEC 60947-1 and SANS/IEC 60947-4-1 certified



(or approve ones that complies with N/E bonding for alternative supplies as per sans) - in order to force the manufactures of a $$$$$$$ expensive inverter, to comply and fit a decent built in relay WITH a failsafe and warning system should there be issues with N/E bond, unlike now if the contactor fails the bond is lost - no warning)
Comment