Neutral earthing

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Derlyn
    Platinum Member
    • Mar 2019
    • 1765

    #1

    Neutral earthing

    Been familiarising myself once again with SANS 10142 with regards neutral earthing.

    Couldn't help but had a little chuckle when reading 7.16.4.5.

    Is that regulation really necessary ?
  • Dave A
    Site Caretaker

    • May 2006
    • 22812

    #2
    To save folk looking up the clause:
    7.16.4.5 The neutral shall not be earthed beyond any earth leakage unit.

    I can imagine how that conversation went in the SANS committee:

    Derlyn: Is that regulation really necessary ?

    Cecil: If we don't put it in, some idiot will f. it up and then blame us for their f-up.
    Participation is voluntary.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

    Comment

    • Derlyn
      Platinum Member
      • Mar 2019
      • 1765

      #3
      It's the same as saying .... " the live should not be connected to the neutral or earth anywhere on the installation. 😂😂

      Comment

      • GCE
        Platinum Member
        • Jun 2017
        • 1495

        #4
        Originally posted by Derlyn
        Been familiarising myself once again with SANS 10142 with regards neutral earthing.

        Couldn't help but had a little chuckle when reading 7.16.4.5.

        Is that regulation really necessary ?
        I agree - Sometimes people don't think and bear in mind that some municipalities insist on an Adit unit when the supply is greater than 300KVA - The Adit unit may not pick up the neutral earth bridge due to it being set a lot higher than 30ma

        Comment

        Working...