    Landis & Gyr 3 ph prepaid meter.

    When power comes on after loadshedding, the meter does not come back on and the display stays blank.

    Now if one bridges the line and load on phase 1 momentarily, it switches the meter on until the next loadshedding, then the meter doesn't switch on again after loadshedding.

    A first for me.

    Any ideas ?
  • GCE
    Platinum Member
    • Jun 2017
    • 1495

    #2
    Almost sounds like line and load has been reversed , or the internal relay wire has been taken from load side instead of line side

    Comment

    • Derlyn
      Platinum Member
      • Mar 2019
      • 1765

      #3
      Found by mistake 🤣 Decided to temporarily bypass the meter so that the restaurant could carry on with business. Turned off all loads and as soon as I put in that first bridge, the meter switched on.

      Anyway, I'll wait for the next loadshedding and open the meter to check connections. What baffles me is that this is a new fault. This meter has been operating perfectly for 2 years.

      Thanks brother. Will give feedback.

      Comment

      • Derlyn
        Platinum Member
        • Mar 2019
        • 1765

        #4
        Bit of feedback. @ GCE, you were 100% correct. Line and load swopped on all 3 phases.

        This is what I found. Thicker wires are line.

        Click image for larger version

Name:	20240110_144211.jpg
Views:	1
Size:	46.0 KB
ID:	266302


        After a bit of investigating it was found that 6 months after the previous tenant moved in 2 years ago was the last electricity purchase.

        The meter was bypassed on the meter terminals. Then shortly before the tenant vacated the premises at end December, he got a buddy to remove the tamper but his buddy got the lines and loads wrong. The landlord is now taking legal action to recoup for the 18 months stolen electricity.

        Never a dull moment.