City Power breaker tripping
  • Andrew_van_Zyl
    • 131
    Guys, what would cause a City Power breaker to trip randomly?
    It goes for several hours and trips around twice a day at different times.
    Single phase 80A breaker.
    Amps pulled way way under spec - 34A.
    House DB not tripping.
    Customer is postpaid.
    Have disconnected the feed cable from CP and the DB and Meggered it - all good. No cable fault. CP was in attendance but didn't have an insulation tester.
    Any ideas?
    • 1761
    Faulty breaker.
      • 1761
      Those random times you were referring to is probably when the geyser or some other heavy load kicks in and the faulty breaker then trips.
        • 1761
        Take the back end of your screwdriver and tap that breaker lightly on it's side. If it then trips, it's shot.
        This is a trick that my tutor taught me in the 70's and it has been usefull on many occasions throughout the years.
        • Andrew_van_Zyl
          • 131
          Thanks Brother. Good suggestion. The breaker stood up to some quite enthusiastic tapping but stayed on. CP replaced the cb recently. Out of ideas here
          Sent from my SM-A226B using Tapatalk
            • 1483
            Been thinking on this one - Do you have an isolator or CB as mains in the DB
            If city power is 80Amp - I would put a 60 amp in the DB on mains to see if that trips first
            My gut tells me you have a cable fault that is tripping when it blows clear which is why your megga test does not pick up an issue - An hour or so later once water has got back into the problem area it will sit and short until it blosws again
            Test after and hour or 2 of being on.
            Had similar on 2 x 120sqmm in parallel - Cable must have been damaged years ago and took almost 15 years before the fault become a complete nuisance - It was under a concrete yard and we were just lucky that while we were standing there we saw wisp of smoke come out between concrete joints - dug down and found the cable fault.
            • Andrew_van_Zyl
              • 131
              Good suggestion GCE - Thank you. Weirdly the problem has gone away and the client is less noisy. I will re-visit this if and when.
              Lol at wisps of smoke - generally a sign of trouble!