    Guys, what would cause a City Power breaker to trip randomly?
    It goes for several hours and trips around twice a day at different times.
    Single phase 80A breaker.
    Amps pulled way way under spec - 34A.
    House DB not tripping.
    Customer is postpaid.

    Have disconnected the feed cable from CP and the DB and Meggered it - all good. No cable fault. CP was in attendance but didn't have an insulation tester.

    Any ideas?
  • Derlyn
    Platinum Member

    • Mar 2019
    • 1748

    #2
    Faulty breaker.

    Comment

    • Derlyn
      Platinum Member

      • Mar 2019
      • 1748

      #3
      Those random times you were referring to is probably when the geyser or some other heavy load kicks in and the faulty breaker then trips.

      Comment

      • Derlyn
        Platinum Member

        • Mar 2019
        • 1748

        #4
        Take the back end of your screwdriver and tap that breaker lightly on it's side. If it then trips, it's shot.

        This is a trick that my tutor taught me in the 70's and it has been usefull on many occasions throughout the years.

        Comment

        • Andrew_van_Zyl
          Bronze Member

          • Mar 2022
          • 131

          #5
          Originally posted by Derlyn
          Take the back end of your screwdriver and tap that breaker lightly on it's side. If it then trips, it's shot.

          This is a trick that my tutor taught me in the 70's and it has been usefull on many occasions throughout the years.
          Thanks Brother. Good suggestion. The breaker stood up to some quite enthusiastic tapping but stayed on. CP replaced the cb recently. Out of ideas here

          Sent from my SM-A226B using Tapatalk

          Comment

          • GCE
            Platinum Member

            • Jun 2017
            • 1473

            #6
            Been thinking on this one - Do you have an isolator or CB as mains in the DB

            If city power is 80Amp - I would put a 60 amp in the DB on mains to see if that trips first

            My gut tells me you have a cable fault that is tripping when it blows clear which is why your megga test does not pick up an issue - An hour or so later once water has got back into the problem area it will sit and short until it blosws again
            Test after and hour or 2 of being on.

            Had similar on 2 x 120sqmm in parallel - Cable must have been damaged years ago and took almost 15 years before the fault become a complete nuisance - It was under a concrete yard and we were just lucky that while we were standing there we saw wisp of smoke come out between concrete joints - dug down and found the cable fault.

            Comment

            • Andrew_van_Zyl
              Bronze Member

              • Mar 2022
              • 131

              #7
              Good suggestion GCE - Thank you. Weirdly the problem has gone away and the client is less noisy. I will re-visit this if and when.

              Lol at wisps of smoke - generally a sign of trouble!