I had my second fault on one of our installations, since we started installing solar.
F23 - AC leakage current is trans over current Leakage current fault
1.Check the PV module and inverter cables.
2.You may have a faulty PV panel (earth short)
3.Restart inverter
12.00 midday, click it went into a fault condition the red light started flashing and you could see on the app that the solar had shut down (went to zero) after about 4 minutes it the red light switched off and the solar started producing power again.
I reduced the solar to 1 kw and let it run until the following day.
I went to site the next day and carried out a number test, including L-N, L-E, N-E with all the switches off just the panel input, nothing seemd out of the ordinary, I also tested the voltage on the the SPD which I thought might be faulty.
Everything seemed normal, so I reset the sytem and cranked up the solar power to 8500 watts (slightly less than it was set prior to the fault). It has been running fine for the past 3 weeks. Returned to site a couple days ago, opened the DC control and checked the voltages again, it seemed fine.
I am wonder if it wasnt because the power was set to the inverter limit.
One thing I did find a bit strange, when I switch on the isolator on the side of the inverter, the voltage between N-E was constant at 247 Vdc however the L-E was fluctuating and then settled, it kept doing this every time put the test lead son the terminals.
I have read that it could have something to do with the MPPT adjusting itself.
Anyone else experienced this?
F23 - AC leakage current is trans over current Leakage current fault
1.Check the PV module and inverter cables.
2.You may have a faulty PV panel (earth short)
3.Restart inverter
12.00 midday, click it went into a fault condition the red light started flashing and you could see on the app that the solar had shut down (went to zero) after about 4 minutes it the red light switched off and the solar started producing power again.
I reduced the solar to 1 kw and let it run until the following day.
I went to site the next day and carried out a number test, including L-N, L-E, N-E with all the switches off just the panel input, nothing seemd out of the ordinary, I also tested the voltage on the the SPD which I thought might be faulty.
Everything seemed normal, so I reset the sytem and cranked up the solar power to 8500 watts (slightly less than it was set prior to the fault). It has been running fine for the past 3 weeks. Returned to site a couple days ago, opened the DC control and checked the voltages again, it seemed fine.
I am wonder if it wasnt because the power was set to the inverter limit.
One thing I did find a bit strange, when I switch on the isolator on the side of the inverter, the voltage between N-E was constant at 247 Vdc however the L-E was fluctuating and then settled, it kept doing this every time put the test lead son the terminals.
I have read that it could have something to do with the MPPT adjusting itself.
Anyone else experienced this?