I had my second fault on one of our installations, since we started installing solar.
F23 - AC leakage current is trans over current Leakage current fault
1.Check the PV module and inverter cables.
2.You may have a faulty PV panel (earth short)
3.Restart inverter
12.00 midday, click it went into a fault condition the red light started flashing and you could see on the app that the solar had shut down (went to zero) after about 4 minutes it the red light switched off and the solar started producing power again.
I reduced the solar to 1 kw and let it run until the following day.
I went to site the next day and carried out a number test, including L-N, L-E, N-E with all the switches off just the panel input, nothing seemd out of the ordinary, I also tested the voltage on the the SPD which I thought might be faulty.
Everything seemed normal, so I reset the sytem and cranked up the solar power to 8500 watts (slightly less than it was set prior to the fault). It has been running fine for the past 3 weeks. Returned to site a couple days ago, opened the DC control and checked the voltages again, it seemed fine.
I am wonder if it wasnt because the power was set to the inverter limit.
One thing I did find a bit strange, when I switch on the isolator on the side of the inverter, the voltage between N-E was constant at 247 Vdc however the L-E was fluctuating and then settled, it kept doing this every time put the test lead son the terminals.
I have read that it could have something to do with the MPPT adjusting itself.
Anyone else experienced this?
F23 - AC leakage current is trans over current Leakage current fault
1.Check the PV module and inverter cables.
2.You may have a faulty PV panel (earth short)
3.Restart inverter
12.00 midday, click it went into a fault condition the red light started flashing and you could see on the app that the solar had shut down (went to zero) after about 4 minutes it the red light switched off and the solar started producing power again.
I reduced the solar to 1 kw and let it run until the following day.
I went to site the next day and carried out a number test, including L-N, L-E, N-E with all the switches off just the panel input, nothing seemd out of the ordinary, I also tested the voltage on the the SPD which I thought might be faulty.
Everything seemed normal, so I reset the sytem and cranked up the solar power to 8500 watts (slightly less than it was set prior to the fault). It has been running fine for the past 3 weeks. Returned to site a couple days ago, opened the DC control and checked the voltages again, it seemed fine.
I am wonder if it wasnt because the power was set to the inverter limit.
One thing I did find a bit strange, when I switch on the isolator on the side of the inverter, the voltage between N-E was constant at 247 Vdc however the L-E was fluctuating and then settled, it kept doing this every time put the test lead son the terminals.
I have read that it could have something to do with the MPPT adjusting itself.
Anyone else experienced this?

I am sure they are ready for the next wave, water tanks and booster pumps, if you are not already on this bus, you missing out. If not, you must be in the rock and stone industry, coining it, so much money to be made and I hear people complaining that work is quiet, really, which rock are you sleeping under, you need to wake up and make the dash for the money, it feels like we living a mad max movies, look for the opportunities and give it horns.