    Originally posted by GCE
    No - not quite - What it does mean is that the OHSA definitions now stand for single phase tester which means any installation with a point of control that is single phase may be worked on by a Single phase tester no matter what is after the point of control eg , solar unless it is a " specialised electrical installation " eg hospital , petrol etc

    It is a joke - We have gone from an SPT only allowed to do lights and plugs in a dwelling smaller than 100sqm ( i think 100sqm was the cut off ) and no stove , geyser or low voltage lighting to full blown domestic electrician with absolutely no training on the regulations with regards to DC , loading etc


    Extract from OHSA EIR
    "[I]electrical tester for single phase" means a person who has been registered as an electrical tester for single phase in terms of regulation 11 (2) for the verification and certification of the construction, testing and inspection of electrical installations supplied by a single-phase electricity supply at the point of control, excluding specialised electrical installations;[/I]
    I'm not sure Annex M helped much in that fight (around SPT's doing/not doing DC and solar on single phase systems) anyway.
    Participation is voluntary.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

    Comment

    • Derlyn
      Platinum Member

      • Mar 2019
      • 1748

      #17
      6.9.3.3 b) NOTE 3

      "The removal of a plug from a socket outlet is a means of safe disconnection.
      "

      It seems, as Dave has suggested, that the motivation of the socket outlet on a water heater circuit, if used, having to be of the non switchable type, is to force the removal of the plug as a means of disconnection as per the above NOTE 3.

      It boggles the mind though, as to why the non switchable socket outlet is applicable on water heaters only and not other fixed appliances.
      Here I'm thinking aircons, swimming pool pumps etc.

      Any confusion could have been avoided by adding the words "non switchable" before socket outlet in the NOTE 3 in 6.2.3.3 which would then have meant that should a socket outlet be used as a disconnecting device on ANY fixed appliance, it must be of the non switchable type.

      That, in my humble opinion, would have made more sense, but to single out water heaters makes no sense at all.
      Last edited by Derlyn; 14-Aug-24, 07:40 AM. Reason: Punctuation and spelling

      Comment

      • GCE
        Platinum Member

        • Jun 2017
        • 1473

        #18
        Originally posted by Dave A
        I suggest so that you can't have the power off without also disconnecting the neutral. I expect the concern is people might (quite probably would) switch off at the switch and start working on the element or thermostat, but the neutral was still connected. Rather force the user to unplug first.

        Makes you think a bit about the classification of socket outlets as an isolating device in general application
        Looks like you were on the money with that logic - Just had sight of a document were it was discussed before implemented

        also informed that the was a
        recommendation to remove a switch on the socket-outlet
        next to the geyser and to have an isolator due to safety
        reasons which will break the live and neutral. The WG
        resolved to modify clause 6.16.2.2 as “ Dedicated circuits
        shall be provided for water heaters and there may be more
        than one water heater on each circuit. Where a socket-outlet
        is used, it shall be unswitched.

        Comment

        • GCE
          Platinum Member

          • Jun 2017
          • 1473

          #19
          In the foreword of the document there was a statement made referencing the removal of a clause on external light protection

          Table of Changes Amdt 2

          Amended to update referenced standards and
          the requirements for voltage drop, busbars
          and earthing, to replace reference to an
          association with a reference standard, to
          delete the clause on external lightning
          protection
          , and the annex on authority for
          issuing a test report and a Certificate of
          Compliance.


          This is the actual clause that was deleted

          From SANS 10142-1 Ed3.1
          6.7.7 External lightning protection
          NOTE Where external lightning protection is installed, it should be in accordance with
          the requirements of SANS 10313.


          It would appear that insurance companies were misinterpreting the clause and insisting that Lightening protection must be installed - The removal should sort the problem

          Comment

          • GCE
            Platinum Member

            • Jun 2017
            • 1473

            #20
            Originally posted by GCE
            Looks like you were on the money with that logic - Just had sight of a document were it was discussed before implemented

            also informed that the was a
            recommendation to remove a switch on the socket-outlet
            next to the geyser and to have an isolator due to safety
            reasons which will break the live and neutral. The WG
            resolved to modify clause 6.16.2.2 as “ Dedicated circuits
            shall be provided for water heaters and there may be more
            than one water heater on each circuit. Where a socket-outlet
            is used, it shall be unswitched.
            During discussion in the workshop this morning the first thing that came up was " surely it is more dangerous unplugging on load" and the 2nd point was " do we need to install with euro" as the small undercounter geysers generally come out with moulded plug tops - Will make Isetech start on a tangent

            Comment

            • Derlyn
              Platinum Member

              • Mar 2019
              • 1748

              #21
              Simple solution. Just install an isolator. Here in our valley, unswitchable plugs aren't easy to come by.

              Comment

              • Leonsparky
                Junior Member
                • Aug 2016
                • 17

                #22
                No not exactly.
                Annex M was removed because you aren’t allowed to have regulatory things in standards. But the EIR is quite clear a SPT is for single phase installations only. Solar is not DC.

                And GMR 5 also says explicitly only IE where power is generated.

                Comment

                • GCE
                  Platinum Member

                  • Jun 2017
                  • 1473

                  #23
                  Originally posted by Leonsparky
                  Solar is not DC.

                  .
                  Is this a typo ?

                  Comment

                  • Leonsparky
                    Junior Member
                    • Aug 2016
                    • 17

                    #24
                    OOPS!! !YES DEFINITELY A TYPO!!!!

                    Comment

                    • Leecatt
                      Silver Member

                      • Jul 2008
                      • 404

                      #25
                      Originally posted by Leonsparky
                      No not exactly.
                      Annex M was removed because you aren’t allowed to have regulatory things in standards. But the EIR is quite clear a SPT is for single phase installations only. Solar is not DC.

                      And GMR 5 also says explicitly only IE where power is generated.
                      Please excuse my ignorance but I am not familiar with the following
                      SPT
                      GMR5
                      IE
                      If someone could translate it, it would be appreciated.
                      To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.