6.9.3.3 b) NOTE 3
"The removal of a plug from a socket outlet is a means of safe disconnection."
It seems, as Dave has suggested, that the motivation of the socket outlet on a water heater circuit, if used, having to be of the non switchable type, is to force the removal of the plug as a means of disconnection as per the above NOTE 3.
It boggles the mind though, as to why the non switchable socket outlet is applicable on water heaters only and not other fixed appliances.
Here I'm thinking aircons, swimming pool pumps etc.
Any confusion could have been avoided by adding the words "non switchable" before socket outlet in the NOTE 3 in 6.2.3.3 which would then have meant that should a socket outlet be used as a disconnecting device on ANY fixed appliance, it must be of the non switchable type.
That, in my humble opinion, would have made more sense, but to single out water heaters makes no sense at all.Comment
-
I suggest so that you can't have the power off without also disconnecting the neutral. I expect the concern is people might (quite probably would) switch off at the switch and start working on the element or thermostat, but the neutral was still connected. Rather force the user to unplug first.
Makes you think a bit about the classification of socket outlets as an isolating device in general application
also informed that the was a
recommendation to remove a switch on the socket-outlet
next to the geyser and to have an isolator due to safety
reasons which will break the live and neutral. The WG
resolved to modify clause 6.16.2.2 as “ Dedicated circuits
shall be provided for water heaters and there may be more
than one water heater on each circuit. Where a socket-outlet
is used, it shall be unswitched.”Comment
-
In the foreword of the document there was a statement made referencing the removal of a clause on external light protection
Table of Changes Amdt 2
Amended to update referenced standards and
the requirements for voltage drop, busbars
and earthing, to replace reference to an
association with a reference standard, to
delete the clause on external lightning
protection, and the annex on authority for
issuing a test report and a Certificate of
Compliance.
This is the actual clause that was deleted
From SANS 10142-1 Ed3.1
6.7.7 External lightning protection
NOTE Where external lightning protection is installed, it should be in accordance with
the requirements of SANS 10313.
It would appear that insurance companies were misinterpreting the clause and insisting that Lightening protection must be installed - The removal should sort the problemComment
-
Looks like you were on the money with that logic - Just had sight of a document were it was discussed before implemented
also informed that the was a
recommendation to remove a switch on the socket-outlet
next to the geyser and to have an isolator due to safety
reasons which will break the live and neutral. The WG
resolved to modify clause 6.16.2.2 as “ Dedicated circuits
shall be provided for water heaters and there may be more
than one water heater on each circuit. Where a socket-outlet
is used, it shall be unswitched.”Comment
-
No not exactly.
Annex M was removed because you aren’t allowed to have regulatory things in standards. But the EIR is quite clear a SPT is for single phase installations only. Solar is not DC.
And GMR 5 also says explicitly only IE where power is generated.Comment
-
-
SPT
GMR5
IE
If someone could translate it, it would be appreciated.To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.Comment