Installation Rules-past papers.

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • cvmostert
    Junior Member
    • Feb 2008
    • 19

    #46
    Hi there, has anyone worked out the question 1 of paper 2 November 2009?

    The figure is as follows:

    (db-220V DC) ----10mCable----(C1-50A)----9mCable----(C2-40A)----8mCable----(C3-30A)----7mCable----(C4-20A)

    If this is not understood i can draw and post also.

    The questions are:
    1. use the figure and calculate the minimum cable size
    2. calculate the voltage drops between the distribution board and the circuits c1 to c3 in each case
    3. prove that the same copper cable was used.

    Tables available: E.1 and 6.4(b)

    I was using the VD = 2 x I x (resistivity x L)/A equation

    Let me know your thoughts, Thanks!

    Comment

    • Godless
      New Member
      • Jan 2010
      • 2

      #47
      Guys I need some help here.

      I'm writing Installation Rules, papers 1 & 2 very soon.
      But I need desparately the following documents:

      SANS 1973-3
      SANS 10198-2
      SANS 10198-1
      SANS 10292

      I have memos and questions papers for both from 2007 that I cann share with anyone in need.
      I also have the following study material.
      OHS Act 85 of 1993.pdf
      OHS Acts, 1993-Construction Regulations, 2003.pdf
      OHS Acts, 1993-Electrical Installation Regulations, 2009 .pdf
      OHS Acts, 1993-Electrical Machinery Regulations 2011.pdf
      SANS-10142-1, 2009.pdf
      SANS-10142-2, 2009.pdf
      Syllabus, 2009.pdf

      Regards
      Loyiso

      Comment

      • AndyD
        Diamond Member

        • Jan 2010
        • 4951

        #48
        At least one of the documents you're looking for is available from wwwdotscribddotcom. I'm not going to go into any more detail in case Dave gets extradited to the US under the new piracy laws..
        _______________________________________________

        _______________________________________________

        Comment

        • cvmostert
          Junior Member
          • Feb 2008
          • 19

          #49
          Originally posted by AndyD
          At least one of the documents you're looking for is available from wwwdotscribddotcom. I'm not going to go into any more detail in case Dave gets extradited to the US under the new piracy laws..
          Just say, Loyiso is sorted on the documents. ;-)

          Comment

          • mikep
            New Member
            • Oct 2011
            • 5

            #50
            Hi Loyiso, Send me a PM and I'll send you old papers for 1 and 2.

            Comment

            • mikep
              New Member
              • Oct 2011
              • 5

              #51
              Loyiso,

              I require copies of SANS 10142 part 1 and 2 documents, as well as OHS Acts documents?

              Regards
              Mikep

              Comment

              • cvmostert
                Junior Member
                • Feb 2008
                • 19

                #52
                I dont think you need part 2, i just did my exams and did not need it.
                you can find an older version of part 1 on scribus.


                Originally posted by mikep
                Loyiso,

                I require copies of SANS 10142 part 1 and 2 documents, as well as OHS Acts documents?

                Regards
                Mikep

                Comment

                • BlueArc
                  Full Member
                  • Feb 2012
                  • 41

                  #53
                  Hi Guys what are you thoughts of having the installation rules exams becoming open book rather than learning parrot fashion style for a couple of weeks then forgetting it after the exam. This is what I am seeing out there. The installation electricians are passing the exams but not applying what they have learnt. My idea behind the open book exam is rather to apply the knowledge.The exams are also far too easy to pass nowaday since the questions are just reapeated from past exams...NO new questions have been formulated...

                  Comment

                  • AndyD
                    Diamond Member

                    • Jan 2010
                    • 4951

                    #54
                    Originally posted by mikep
                    Loyiso,

                    I require copies of SANS 10142 part 1 and 2 documents, as well as OHS Acts documents?

                    Regards
                    Mikep
                    Somebody just uploaded to Demonoid as a torrent the 10142 regs plus the specialised installation codes plus ammendments and they even threw in the UK regs and guidance notes for good measure. Must be your lucky day Mike.
                    h**p://www.demonoid.me/files/details/2857789/41199615/
                    _______________________________________________

                    _______________________________________________

                    Comment

                    • murdock
                      Suspended

                      • Oct 2007
                      • 2346

                      #55
                      need and invite to access...now there is info that i would like to get my hands on...especially the uk regs

                      Comment

                      • AndyD
                        Diamond Member

                        • Jan 2010
                        • 4951

                        #56
                        You shouldn't need to register to get access to the torrents. If you can't come right let me know and I'll email you the torrent file so you can download it.
                        _______________________________________________

                        _______________________________________________

                        Comment

                        • natal21
                          Email problem
                          • Oct 2011
                          • 12

                          #57
                          help

                          I really need the memo for last exams 1 and 2 of 2011
                          can anyone help?

                          Comment

                          • CollenD
                            Junior Member
                            • Mar 2012
                            • 18

                            #58
                            hi guys, my first time here.I am a trade-tested class 1 electrician from Zim working in SA and I wish to register with the DOL as an Installation Electrician.could anyone pliz help me with info as to how do I go about registering for the 2012 Installation Rules exams and which colleges in Jhb offer the subject on a part-time basis.

                            Comment

                            • Yiks
                              Email problem
                              • Apr 2012
                              • 3

                              #59
                              Thanks a million for your selflessnes,hopefuly this will help me bigtime as I'm also trying to get my accreditation.

                              Yiks.

                              Comment

                              • CollenD
                                Junior Member
                                • Mar 2012
                                • 18

                                #60
                                Thanks so much brother, yo help is gr8ly appreciated.

                                Comment

                                Working...