Referenced from SANS 10142-1 (ed 3.1)
b) suitable protection shall be installed; and
c) where, for practical reasons, the supply to the installation cannot be
automatically disconnected by an earth fault current of double the rated
current (or higher) of the main protective device, as an alternative, an earth
fault detection and disconnecting device can be installed at the point of
control of the installation. The earth fault detection and disconnecting
device shall be so installed that they operate at a current related to the
earth loop impedance which will limit prospective touch voltages under
short-circuit fault conditions to 25 V for a period not exceeding 5 s.
NOTE 1 These requirements can easily be achieved by using an earth leakage
device that has a rated earth leakage tripping current (rated residual current) IΔn not
exceeding 300 mA. Devices provided with a time delay of, for example, 0,1 s, will
ensure discrimination with earth leakage protection devices in final circuits.
NOTE 2 Separate earth fault protection could consist of sensitive earth leakage
protection, which might not always be practicable where large currents are involved.
b) suitable protection shall be installed; and
c) where, for practical reasons, the supply to the installation cannot be
automatically disconnected by an earth fault current of double the rated
current (or higher) of the main protective device, as an alternative, an earth
fault detection and disconnecting device can be installed at the point of
control of the installation. The earth fault detection and disconnecting
device shall be so installed that they operate at a current related to the
earth loop impedance which will limit prospective touch voltages under
short-circuit fault conditions to 25 V for a period not exceeding 5 s.
NOTE 1 These requirements can easily be achieved by using an earth leakage
device that has a rated earth leakage tripping current (rated residual current) IΔn not
exceeding 300 mA. Devices provided with a time delay of, for example, 0,1 s, will
ensure discrimination with earth leakage protection devices in final circuits.
NOTE 2 Separate earth fault protection could consist of sensitive earth leakage
protection, which might not always be practicable where large currents are involved.