    Random earth leakage problem

    For a few months now I have been experiencing random earth leakage problems - earth leakage switch tripping for no apparent reason. For a while it appeared to be both random trips and when plugging in a charger power brick for a laptop.

    I have now spent several thousand rands on replacing all sorts of things based on advice from sparkles, eg gate motor, pool pump, all day/night switches, plus I have had the garage/workshop rewired with a new DB and own earth leakage breaker because some of the problems occurred when the garage lights were switched on each day! Each of these faults was detected using a 'megger' (?).

    Interestingly I find that this still occurs BUT still trips in the house and not at the new EL breaker, despite all the feed from the house now via the new switch.

    I cannot find a sparky who can get me past this point.

    I understand that the combined effect of power bricks and ups units (I have several ups units powering essential systems in the office) can create a background earth leakage level that makes the el breaker trip at very low additional el loads?

    I would appreciate some diagnostic advice as this is now driving me nuts!
  • murdock
    Suspended

    • Oct 2007
    • 2346

    #2
    if it is a heineman 60 amp unit dated 2006 - 2008 i can understand...i have been having huge problems with heinemen 60 amp earth leakage units...to a point that i now longer install heineman earth leakage units....and the joke..heineman only offer a 1 year warranty...i wonder why.

    i had a simmilar problem in december...i managed to find the problem...a wire which was no longer used...but not diconnected...i managed to find all the other little issues in the house...like water in light fittings...gate motor and pool pump...must have been from all the rain we had...once all the little faults whre found...the earth leakage unit still tripped...i replaced the earth leakage unit with a different make and havent had a call sinc...i did test the new earth leakage unit with an earth leakage tester and it did trip at 25 mA

    an insulation resistance tester(commonly refered to as a "megger" which is a brand of insulation resitance testers ) is used to find insulation resistance issues...

    fluorescent light fittings are a common problem when connected to an earth leakage units...when they ignite (start up) they cause tripping issues...bad idea to have them connected to an earth leakage unit...but in saying that...all sabs regs must be adhered to at all times.


    sounds to me like the sparky has connected the new earth leakage in series...which is incorrect...it must be connected in parallel...believe it or not but this is a common practice...a quick way to determine whether the sparky knows what he is doing or not...

    i sympathise with you trying to find a good sparky...there are hundreds if not thousands of them out there but when it comes to anything more than chasing walls and connecting plugs...there are only a few good ones left.

    Comment

    • Dave A
      Site Caretaker

      • May 2006
      • 22818

      #3
      Has the earth leakage unit in the house been replaced?

      Nuisance earth leakage tripping sure is a PITA. Part of the problem is the fault that is causing the tripping never gets enough juice to really advertise where it is while on the earth leakage unit. My sparkies use the term "blow the fault clear." It involves taking the suspect circuits off earth leakage so that when the fault blows, it blows properly!

      Obviously needs to be done with due regard for safety issues, and I'm probably going to take some flack for even suggesting it - but sometimes it is the only way to find the fault.
      Participation is voluntary.

      Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

      Comment

      • AndyD
        Diamond Member

        • Jan 2010
        • 4951

        #4
        Originally posted by BillH
        For a few months now I have been experiencing random earth leakage problems - earth leakage switch tripping for no apparent reason. For a while it appeared to be both random trips and when plugging in a charger power brick for a laptop.
        There's no reason a laptop power supply would cause earth leakage, they're usually Class II appliances and don't even have an earth connection.

        Originally posted by BillH
        I have now spent several thousand rands on replacing all sorts of things based on advice from sparkles, eg gate motor, pool pump, all day/night switches, plus I have had the garage/workshop rewired with a new DB and own earth leakage breaker because some of the problems occurred when the garage lights were switched on each day! Each of these faults was detected using a 'megger' (?).
        Assuming the electrician removed the garage subDB from the RCD (earth leakage breaker) in the house when he fitted a new RCD in the subDB then this rules out the garage as being the problem. If the garage is still supplied via the main RCD in the house then without discrimination it's a lottery which one would trip fiirst to a fault in the garage.

        Originally posted by BillH
        I cannot find a sparky who can get me past this point.
        This seems to be your problem. You need someone who's capable of localising and fixing this problem. You're going to have to get past the cheapest price mentality and find a good capable electrician and pay him his extortionate labour rate to find the problem.

        Originally posted by BillH
        I understand that the combined effect of power bricks and ups units (I have several ups units powering essential systems in the office) can create a background earth leakage level that makes the el breaker trip at very low additional el loads?
        Firstly there's no such thing as background earth leakage. There's just earth leakage.... period. Earth leakage is usually measured in milliamps unless there's a lot of it and then it might be measured in amps.

        Secondly class2 appliances (double insulated) such as cellphone and laptop chargers would have zero earth leakage. A UPS usually has a chassis with an earth so with the UPS it's possible to have a low insulation problem resulting in earth leakage. It is unlikely however and would easily be proved using a Mega tester.

        Originally posted by BillH
        I would appreciate some diagnostic advice as this is now driving me nuts!
        My immediate diagnosis is that you need a decent electrician otherwise your prognosis is looking bleak.

        RCD nuisance tripping is one of the more difficult problems to solve.
        Start with sorting out the easy stuff and only then get complicated if necessary.
        1 Ramp test both RCD devices.
        2 IR test all circuits on the main DB and fix anything with an IR value of less than 2 MΩ.
        3 Do same with Sub DB in garage.
        4 Check both DB's for circuits with borrowed or crossed neutrals.

        One thing you can do is keep a log of every time the RCD trips. Note the time of day, exactly what appliances are running and any other circuit breakers that trip at the same time.

        Can you attach photos of the inside of the main and garage DB's?
        Can you tell us whether the RCD resets first time after it trips?
        The more info you can give the better.



        Originally posted by murdock
        fluorescent light fittings are a common problem when connected to an earth leakage units...when they ignite (start up) they cause tripping issues...
        If fluorescent light have low IR readings then they're faulty. A fluorescent light should present no earth leakage even during ignition cycle.

        Originally posted by Dave A
        My sparkies use the term "blow the fault clear." It involves taking the suspect circuits off earth leakage so that when the fault blows, it blows properly!
        Not sure what 'blow the fault clear' means but the phrase is exciting in a very scary sort of way.
        _______________________________________________

        _______________________________________________

        Comment

        • BillH
          Junior Member
          • Jan 2012
          • 15

          #5
          Thanks very much for your response. I can respond to the issues you raise as follows:

          The earth leakage switches are both Heineman but I have no idea as yet re their manufacturing date. Will look tomorrow. I was not aware that there are other makes? Can you recommend what I should buy?

          The fluorescent lights did not trip today - first time for a while after the sparky said he found loose connections in the switch yesterday.

          The only trip I have had today was when I plugged one of my microscopes (I am a biologist) into a multi-plug. Not sure how this could happen as this only powers the lamp and it's a new scope.

          Multiplugs are so necessary but seemingly problematical. Is it possible to buy good quality multiplugs that have an in-built trip switch?

          The sparky did not disconnect the sub-board feed from the trip switch in the house. I assume this is what you mean by in series? I did ask him why I assumed he would have by-passed the house trip. He indicated that this was how it should be done.

          I would really like to find a knowledgeable electrician. The guy I am using now was recommended by Geyserwise, before that I was using a "reputed" Somerset west company who eventually just stopped coming back. They have not been cheap either, plus they have recommended a lot of expensive replacements of stuff that turned out to have not been the problem.

          I am open to any recommendations for a good sparky in the cape town area - or an electrical engineer who does fault finding!
          Last edited by BillH; 06-Jan-12, 08:42 AM.

          Comment

          • BillH
            Junior Member
            • Jan 2012
            • 15

            #6
            Yes, it was replaced quite early in the process.

            Comment

            • BillH
              Junior Member
              • Jan 2012
              • 15

              #7
              Thanks for your time to respond so comprehensively.

              I found a USA forum where someone found that different laptop power bricks tripped his circuits from different points in his house. This is exactly what I have been experiencing. The forum responder said that this was common and that with many such units plugged in renders the earth leakage more sensitive. Seemed logical at the time - some transformers give quite a buzz if you touch the wall socket end when disconnecting?

              I urgently need to find a good electrician who can fault-find in a scientific manner?

              We have kept logs for a while but could not link the faults to any appliance switching on or off. We have three types of occurrence: entirely random, plugging in a charger or the garage light issue. The random could be ants or geckos but we cannot find where if this is the case. Maybe a frayed wire underground somewhere.

              Thanks again!

              Comment

              • BillH
                Junior Member
                • Jan 2012
                • 15

                #8
                I forgot to add that the earth leakage resets immediately.

                Comment

                • BillH
                  Junior Member
                  • Jan 2012
                  • 15

                  #9
                  Hi again,

                  In response to the make of earth leakage switch, they are not Heineman (my mistake) but are marked "CBi". Most of the other breakers on the boards are SAMITE, with one or two Heineman switches left over from the original DB when we built the house 30 years ago.

                  Is the CBi make OK?

                  Comment

                  • BillH
                    Junior Member
                    • Jan 2012
                    • 15

                    #10
                    Ok, today (Friday), had a random trip around 08:00 and the garage lights again tripped the house RCD and not the new one in the garage!

                    Comment

                    • garthu
                      Gold Member

                      • Dec 2008
                      • 595

                      #11
                      You gonna have your hands full with this one...I'm not a pro on this so leave it to the likes of AndyD/Dave etc but wanted to chuck this in anyway as have had a load with it with the rains. Related to water anyway? Rain, sprinklers, bath emptied. Sure you considered it but just offering.

                      AndyD... love the comment..
                      Not sure what 'blow the fault clear' means but the phrase is exciting in a very scary sort of way.
                      It does hey! Need to be around to see this one... kinda like an exciting Guy Fawkes eve
                      Garth

                      Electric fence Installation : www.midrand-electronics.co.za
                      Free Classified Adds : www.bgone.co.za

                      Comment

                      • Sparks
                        Gold Member

                        • Dec 2009
                        • 909

                        #12
                        You bet it can be scary. Too many youngsters here for me to suggest it but now the cat is out the bag. I just hope they are at least carefull when trying it. I have read this thread from the beginning and it appears all the bases have been covered. In light of the fact that the power tripped with the 'scope I suspect it could be a "imported" multiplug. The finest quality I love as much as a bicycle pedal. I am however also considering the scope itself does it perhaps have a transformer and then finally, is there perhaps a incorrectly installed SPD? As for CBI, they are all I use.
                        As was mentioned, the best for you here is to note what is plugged in at the time of tripping.
                        In closing, do not throw the geyser out before checking. Some idiots actually do wire them through the ELCB

                        Comment

                        • Dave A
                          Site Caretaker

                          • May 2006
                          • 22818

                          #13
                          Originally posted by garthu
                          AndyD... love the comment..
                          Not sure what 'blow the fault clear' means but the phrase is exciting in a very scary sort of way.
                          It does hey! Need to be around to see this one... kinda like an exciting Guy Fawkes eve
                          Probably sounds more dramatic than it is - certainly not Guy Fawkes level. What you're trying to achieve is a fault current limited by the over-current protection rather than the piddling 30 mA or so you get on earth leakage protection. It makes the flash-over point easier to identify (especially in the dark), or permanent (carbon tracked or fused).

                          We normally go this way when we've identified an underground cable fault, but the client doesn't want to run to the cost of a thumper test or replacement of the cable without clear, unarguable evidence - and they're not happy with a marginal insulation result using a meggar. Take the cable off earth leakage, put earth leakage protection on the demand end, and with the next rain the fault really blows.

                          However, we did have one where we'd pinned the problem down to a lighting circuit. It turned out the surfex cabling had a series of tiny pin holes in it - literally only visible with a magnifying glass - and I doubt we would have found exactly what the problem was any other way than watch for the flash.
                          Participation is voluntary.

                          Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                          Comment

                          • BillH
                            Junior Member
                            • Jan 2012
                            • 15

                            #14
                            OK, sparky came back today to connect the new RCD in parallel, but this was a miserable failure as he could not get it right and ended up with everything tripping. We are now back where we started with a new RCD that doesnt do anything?

                            Anyone know of an electrician who knows what they are doing??

                            Comment

                            • AndyD
                              Diamond Member

                              • Jan 2010
                              • 4951

                              #15
                              I've come across those damn 5 into 1 multi-plug adapters where the indicator neons in the switches were wired between the switched live coming off the switch and the earth. Each multiplug showed about 2.5 MΩ @ 500volts test and three of them was enough to cause nuisance tripping.

                              The thing with earth leakage is that unless the circuits are all on individual RCBO's it's a cumulative fault so a lot of small IR problems dotted around an installation all mount up to appear as one big problem at the single RCD.