Welcome to The Forum SA. As a visitor you have read only access to the public content areas of this website. You will have to register as a member to access all content, post messages and network with our members. Membership is free and registering is quick and easy. You can click here to register now and become a member within minutes.
I was just reading through SANS 10142, and under annex P, Authority for issuing a test report and a Certificate of Compliance.
Which is installation is Two-phase, is it two phases from three phase system?
Yes, a two-phase system consists of 2 live phases, one neutral and an earth, as you say it's basically a 3-phase system that's missing one phase. It's not very often you see a 2-phase installation nowadays, I've come across only one in the last 15 years or so. Maybe they're more common in certain areas, I'm not sure TBH.
Am a bit confused here regarding Voltage drop calculation,
E.1.4 Circuit DB/C
Selected cable voltage drop to be repeated for each load point from the
previous load point. Amdt 5
From table 6.4(b) (voltage drop), for a 16 mm2 two-core cable single-phase a.c., the voltage drop is 2,8 mV/A/m
DB to C1 voltage drop = (2,8 x 10-3) x (5 x 15) x 10 = 2,10 V Amdt 5
C1 to C2 voltage drop = (2,8 x 10-3) x (4 x 15) x 8 = 1,34 V Amdt 5
C2 to C3 voltage drop = (2,8 x 10-3) x (3 x 15) x 8 = 1,01 V Amdt 5
C3 to C4 voltage drop = (2,8 x 10-3) x (2 x 15) x 6 = 0,50 V Amdt 5
C4 to C5 voltage drop = (2,8 x 10-3) x (1 x 15) x 9 = 0,38 V Amdt 5
Total voltage drop DB to C5 (red phase) = 5,33 V [1] Amdt 5
My question is: why should they multiple the current by 5 at C1, by 4 at C2, by 3 at C3, by 2 at C4 and by 1 and C5.
is this really right?
My total voltage drop is 1.722V
Last edited by Dave A; 14-Mar-13, 08:25 PM.
Reason: formatted superscript in formula
My question is: why should they multiple the current by 5 at C1, by 4 at C2, by 3 at C3, by 2 at C4 and by 1 and C5.
Point C1 is carrying 5 x 15A draw points, 1 at C1 and another 4 further down the line.
Similarly C2 is carrying 4 x 15A draw points.
From a "follow the logic" point of view, it might have been better if they started the point numbering from the furtherest point and worked back towards the supply point for these sorts of schematics. Of course from a signage point of view (if you were actually physically labelling each point) it makes more sense to number from point of supply...
We process personal data about users of our site, through the use of cookies and other technologies, to deliver our services, personalize advertising, and to analyze site activity. We may share certain information about our users with our advertising and analytics partners. For additional details, refer to our Privacy Policy.
By clicking "I AGREE" below, you agree to our Privacy Policy and our personal data processing and cookie practices as described therein. You also acknowledge that this forum may be hosted outside your country and you consent to the collection, storage, and processing of your data in the country where this forum is hosted.