Saturday at home, installing an inverter

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • tec0
    Diamond Member

    • Jun 2009
    • 4624

    #136
    Originally posted by IMHO
    Video as promised.

    For some reason the forum says it is an illegal file and will not show preview.

    Here is the direct link.

    https://www.youtube.com/watch?v=Sib9...ature=youtu.be
    Love your UPS hack, excellent and your question is a damn good one. I spoke to a guy from Battery Centre and he told me my charger was killing my batteries now they are selling a charger that can charge deep cycle battery and it will cost me about R1250 for it. Now thing is with your normal UPS and i think you knew this already so sorry for repeating it. There is no real why to stop it from charging your battery because by design it just stupidly charge the battery to death "had a few UPS's" and if you check the voltages on them you will see that even when the battery hits 14 volts it just continue to charge.

    I have no clue how you will get around that yet.... That said YOU DID THE HACK! and not many can say that

    excellent post
    Last edited by tec0; 09-Jun-15, 08:42 AM.
    peace is a state of mind
    Disclaimer: everything written by me can be considered as fictional.

    Comment

    • daveob
      Email problem

      • Feb 2008
      • 655

      #137
      Originally posted by IMHO
      Here is the demo on the working and ammeter. I see that for a split second the amps is going into 30 amp. How long should it be over 30 amp to blow the fuse?
      Hi IMHO

      Hope you don't mind me chipping in here.

      Video looks good. Well Done.

      Had a look at the last few posts here and you seem to be rightly concerned about overcharging the batteries.

      I see that you have 2 main possibilities here :

      option 1 :
      control the charging by the UPS.

      You would need to identify the circuitry that charges the batteries.

      Then monitor the battery voltage and when it reaches the required level, say 14V or whatever the ideal voltage is, then disable the charging from the UPS.

      Battery voltage can be easily monitored using a micro processor ( like an atmega328 IC chip ). The IC runs using 5V which can be supplied by the battery using a linear voltage regulator, and then connect the battery to an analog input pin using a voltage divider.

      The voltage divider ( consists of 2 small R3 resistors and a capacitor ) basically scales the battery voltage down to a level that the IC can read. The IC can measure from 0V to 5VDC. So if your absolute max voltage on the battery under charge will be, lets say 20V to be on the safe side, then we need to scale the voltage down to 25% of the source ( battery ) and feed the scaled down voltage to the IC. The analog input pin of the IC has a 0 to 1023 scale, so is reasonably accurate.

      So the IC would see 20V source as 1023 on it's analog scale ( 5V at the IC from the voltage divider ), 15V as 767 ( 3.75V ), 10V as 511 ( 2.5V )

      Once you have that working, that same IC can control a transistor, which in turn controls a Solid State Relay, or opto-coupler, or any other device to turn the UPS charging system on or off.

      The downside here is that you have no control over the charge rate.
      Plus side of having the IC here is that you can also use it to monitor the voltage of the batteries when the UPS has no mains supply, and is discharging.

      You may find your UPS will discharge the battery to, lets say ( just for an example ), 10V. But your battery supplier says you should not discharge below 11V to ensure the battery lasts 5 years longer.

      So the voltage divider to the IC is used to monitor the battery voltage during discharge, and if it gets to a certain level, say 11.05V, then you disable the SSR or relay that connects the battery to the UPS. Yes, your appliances lose power, but your batteries live to fight another day.


      Option 2 :
      Disable the charging of the batteries by the UPS and charge them using a separate independent charger that is designed for different charge rates.

      There are a number of designs out there that will monitor battery voltage ( as described above ) and use PWM to control the charge and charge rate to the batteries, ranging from full power charge upto certain voltages, then reducing charge rate to a trickle or 'maintenance' charge.

      Just my 2c worth.
      Watching the ships passing by.

      Comment

      • daveob
        Email problem

        • Feb 2008
        • 655

        #138
        Actually, having just thought about that, I think it also important to point out that in so many cases, people are spending small fortunes on systems to ensure that they have power when the outage hits - but little or no thought or concern about what happens when the power is restored.

        There have been numerous mentions of routers that work erratically. The mains power is all over the place when it comes back on and everyone starts up at the same time. So if you're getting 180VAC into the router transformer that expects 200 - 240VAC, then the 12VDC output may not be 12V and the router starts doing weird things.

        Or the TV set and sound system that you paid +R12k for that is subject to wild voltage swings on power up.

        Or this pride & joy battery system. What happens when the power comes back on. Does the UPS immediately disconnect the battery and router the mains to the devices plugged into the UPS ? Most likely the case. What effect does voltage changes have on the charging circuit ?

        The solution is to install a device that can :
        1. prevent the mains power from being supplied down the line.
        2. monitor the incoming mains voltage until it is above a set value ( eg. 200VAC ) and below 240VAC.
        3. Start a timer ( eg 5 minutes, 15 min, etc )
        4. delay the supply of mains power downline until the timer has expired ( unless the override button is pressed )

        That way, you get to minimise the startup impact on your equipment.
        Watching the ships passing by.

        Comment

        • tec0
          Diamond Member

          • Jun 2009
          • 4624

          #139
          So basically micro controlling will become the norm here, I was thinking about a Arduino Uno, they can handle a lot of inputs and there are shields available for modification and the program IDE have a look at arduino. There is also a heavily supported library for it so copying and pasting code may well be an option "depending"

          I am planning home automation with it... I am sure a Google will give you results on how to make smart chargers and all the rest. There is a ton of stuff on YouTube.

          hope it helps a little
          peace is a state of mind
          Disclaimer: everything written by me can be considered as fictional.

          Comment

          • daveob
            Email problem

            • Feb 2008
            • 655

            #140
            Originally posted by tec0
            So basically micro controlling will become the norm here, I was thinking about a Arduino Uno, they can handle a lot of inputs and there are shields available for modification and the program IDE have a look at arduino. There is also a heavily supported library for it so copying and pasting code may well be an option "depending"

            I am planning home automation with it... I am sure a Google will give you results on how to make smart chargers and all the rest. There is a ton of stuff on YouTube.

            hope it helps a little
            Look at the Mega2560 instead. Has 54 I/O pins instead, and not that much more cost.

            Personally I use a Mega2560 for home automation ( 3 x gate control, alarm system, sms to cell on trigger, web based control of gates, alarm, smart sensor control ( eg disable indoor passives in living room area when kids break beams in passageway in the morning, etc ).

            Yes, you will find a lot of open source code based on Arduino for charge controllers, etc.

            Just remember that boards like the Arduino have a 'per pin' and 'total board' current limit, so outputs are basically limited to an LED or an NPN transistor ( which in turn can drive much bigger loads ).

            Once you have an Arduino, you can also use it to program a stand-alone atmega IC ( about R70 for atmega vs R350 for Uno ) so once your code is working, push it on to an atmega and reduce your hardware cost.

            ps .. when you make a board for the atmega IC, use an IC saddle ( type of socket that the IC clips into ). If you have a system problem, very easy to remove the IC brains and replace it with the spare that you made.
            Last edited by daveob; 09-Jun-15, 09:55 AM.
            Watching the ships passing by.

            Comment

            • tec0
              Diamond Member

              • Jun 2009
              • 4624

              #141
              Originally posted by daveob
              Look at the Mega2560 instead. Has 54 I/O pins instead, and not that much more cost.

              Personally I use a Mega2560 for home automation ( 3 x gate control, alarm system, sms to cell on trigger, web based control of gates, alarm, smart sensor control ( eg disable indoor passives in living room area when kids break beams in passageway in the morning, etc ).

              Yes, you will find a lot of open source code based on Arduino for charge controllers, etc.

              Just remember that boards like the Arduino have a 'per pin' and 'total board' current limit, so outputs are basically limited to an LED or an NPN transistor ( which in turn can drive much bigger loads ).

              Once you have an Arduino, you can also use it to program a stand-alone atmega IC ( about R70 for atmega vs R350 for Uno ) so once your code is working, push it on to an atmega and reduce your hardware cost.

              ps .. when you make a board for the atmega IC, use an IC saddle ( type of socket that the IC clips into ). If you have a system problem, very easy to remove the IC brains and replace it with the spare that you made.
              Yes you are right on every aspect... I am just lazy

              yes it is expensive and yes Arduino is limited. What I like about it is the ecosystem it plugs into. The Arduino Mega R3 for example is a really nice board. Also i like to use the 4 Channel Relay Board For Arduino and it just works actually... Never had problem with it You can always adapt to a solid-state relay if you need to or even go to heavy-duty contactor using relay logic... It is a bit old school but it gets the job done.
              peace is a state of mind
              Disclaimer: everything written by me can be considered as fictional.

              Comment

              • IMHO
                Email problem

                • Jan 2012
                • 540

                #142
                daveob, I would love to identify the charger circuit and hack it to float charge to 26 volt , or disable it all together. The problem is I am not an electronic boffin and do not know how to. I can Google and YouTube, but not knowing where the charging circuit is, stp me in my tracks. Can you help?






                ~Expenses will eat you alive! - My first Boss~

                Comment

                • IMHO
                  Email problem

                  • Jan 2012
                  • 540

                  #143





                  ~Expenses will eat you alive! - My first Boss~

                  Comment

                  • daveob
                    Email problem

                    • Feb 2008
                    • 655

                    #144
                    Originally posted by IMHO
                    daveob, I would love to identify the charger circuit and hack it to float charge to 26 volt , or disable it all together. The problem is I am not an electronic boffin and do not know how to. I can Google and YouTube, but not knowing where the charging circuit is, stp me in my tracks. Can you help?
                    Hi IMHO

                    Sorry, but I have to be able to admit that what you are asking is not my area of expertise, so I would not want to give you incorrect info or advice, knowing full well that it could lead to disaster.

                    I can tell you a little about the pics you posted from what I can see. WARNING : this is all what I think I see. I have NO formal training or qualifications in this field :

                    pic 1 : a lot of these boards are designed as generic / multi purpose boards, so you will find a few holes on the pcb with diagrams printed on them for parts that are not populated. Those would be for a different model.

                    pic 2 : see the round black cylindrical thingy with the 63v printed on the side ? WARNING WARNING WARNING WARNING - those have big teeth. It is a capacitor that is designed to store energy. They are used to absorb fluctuations in the current flowing through them, making your ups run smoother and 'cleaner'. They are also designed to discharge that same energy - and can do so VERY fast. And even if your board is disconnected from the mains, they still retain their energy. If you touch the contacts on a capacitor, or short them together, there will be a shock, or a lot of sparks. One of the main reasons why warning signs are posted on things telling you not to open them. Ask me, I know. Was working on modifying a disposable camera flash bulb for a swim timing system a while back, and accidentally touched a 300V capacitor. After the feeling returned, my arm was still tingling for a few days.

                    pic 3 : that huge thing is, I suspect, a step up transformer. Most likely takes 24VDC input ( higher current = thicker wires ) and outputs 220VAC ( lower current = thinner wires ).

                    pic 4 : the 4 black cubes in the middle are relays. From what I can see, most likely magnetic coil switching relays.

                    Assuming the big transformer is a step up, the relays likely cause the 24VDC from the battery to be connected to the step up transformer when the mains fails.

                    The round black component with the red wire through it, at the bottom right of the relays, is a current sensor. That would detect when the mains has failed, and would cause the relays to kick in.

                    pic 9 : the board mounted to the back of the case contains the rs232 comms plug, and the phone in / out plugs for surge protecting of the phone line. The 5 cable plug connects the comms board in the pic to the charge pcb. That comms board would have no effect on the charging of the batteries.

                    Pic 9 also looks like the mains in to the UPS are connected directly to the output sockets on the UPS. That means the mains, when present, will flow directly from the input to the output. Only when the mains fails, will the pcb connect the battery to the transformer and output 220V to the output sockets.

                    pic 10 : the notably thicker wires are probably the wires from the battery to the board, and / or from the board to the transformer. They are thicker so that they can carry more current. ( ignoring AC and DC for now, 1A @ 220V would be 220Watts, but 220W @ 24V = 9 amps. Amps = current, so higher current needs thicker wires.
                    Same logic is used for solar PV panels. Connect in series to increase voltage = lower current = thinner wiring needed from panels to charge controller.

                    pic 11 : shows an IC ( chip ). This is most likely something like an atmega or pic chip that is programmed with the 'logic' for the board and controls what it does.
                    The item at the top left that is bolted to the silver heat sink would be either a FET or a voltage regulator. There are some small capacitors close by ( the light brown 'blob' components ) and these are typically used to smooth the output of the voltage regulator. It should have numbers printed in the voltage reg. something like 7805 ( the '05' indicates that it supplies 5VDC output ) and would be used to regulate the voltage that the IC chip needs to run.
                    The round black component at the bottom left with the hole in the top is a piezo buzzer. Very low current but very noisy and irritating beeper when the UPS is running. I dropped a spot of pratleys quickset on the top of mine and it is a lot quieter.

                    Sorry, but I know this does not really help you one bit, but hope it does give you some idea of what those components are.

                    If you really want to do mods to this board, you may want to look at some of the electronics forums, of put a job up on fiverr ( $5 ) for someone to source you a wiring diagram / schematic and to tell you what to modify.
                    Watching the ships passing by.

                    Comment

                    • AndyD
                      Diamond Member

                      • Jan 2010
                      • 4946

                      #145
                      Originally posted by daveob
                      Actually, having just thought about that, I think it also important to point out that in so many cases, people are spending small fortunes on systems to ensure that they have power when the outage hits - but little or no thought or concern about what happens when the power is restored.

                      There have been numerous mentions of routers that work erratically. The mains power is all over the place when it comes back on and everyone starts up at the same time. So if you're getting 180VAC into the router transformer that expects 200 - 240VAC, then the 12VDC output may not be 12V and the router starts doing weird things.

                      Or the TV set and sound system that you paid +R12k for that is subject to wild voltage swings on power up.

                      Or this pride & joy battery system. What happens when the power comes back on. Does the UPS immediately disconnect the battery and router the mains to the devices plugged into the UPS ? Most likely the case. What effect does voltage changes have on the charging circuit ?

                      The solution is to install a device that can :
                      1. prevent the mains power from being supplied down the line.
                      2. monitor the incoming mains voltage until it is above a set value ( eg. 200VAC ) and below 240VAC.
                      3. Start a timer ( eg 5 minutes, 15 min, etc )
                      4. delay the supply of mains power downline until the timer has expired ( unless the override button is pressed )

                      That way, you get to minimise the startup impact on your equipment.
                      I did make a thread about this a while ago because it's something that's often not taken into consideration at the design stage of a back-up system and it affects the entire spec including the battery requirements and the selaction of appropriate inverters etc.

                      Another solution to add to the 4 you mentioned is to replace the power supplies on any devices such as routers, alarms, PABX's etc if the original has a tight band of voltage requirement. I did this with my Netgear router, the original power supply plug was the heavy transformer type and was rated for operation between 220-240 volts, I purchased an equivalent switch mode type supply with a wider voltage band of 100-250 volts and it solved a lot of random conectivity and networking problems I was having.
                      _______________________________________________

                      _______________________________________________

                      Comment

                      • tec0
                        Diamond Member

                        • Jun 2009
                        • 4624

                        #146
                        Ok what inverter to use, i am told that some inverters can actually damage the refrigerator? I am asking this because I am getting into contact with a supplier that sells a 9000 Watt system for R36k That is not bad because it is a complete working system. Thing is I don't know the makes and parts so in the end I am stepping on a real risk of getting shot in the foot...

                        Questions I will be asking.
                        How strong are the Solar panels?
                        Can the inverter be used on electronics like TV, DVD player, PC Refrigerator and Freezer?
                        How long will everything last under load?
                        Can the batteries be charged from a second source "like generator"?

                        Please add your question here...
                        peace is a state of mind
                        Disclaimer: everything written by me can be considered as fictional.

                        Comment

                        • daveob
                          Email problem

                          • Feb 2008
                          • 655

                          #147
                          Originally posted by AndyD
                          I did make a thread about this a while ago because it's something that's often not taken into consideration at the design stage of a back-up system and it affects the entire spec including the battery requirements and the selaction of appropriate inverters etc.

                          Another solution to add to the 4 you mentioned is to replace the power supplies on any devices such as routers, alarms, PABX's etc if the original has a tight band of voltage requirement. I did this with my Netgear router, the original power supply plug was the heavy transformer type and was rated for operation between 220-240 volts, I purchased an equivalent switch mode type supply with a wider voltage band of 100-250 volts and it solved a lot of random conectivity and networking problems I was having.
                          Hi AndyD

                          I recall that thread. Although I agree with your solution and how the problem was solved, my first concern would be the fact that this 'proves' that the mains supply after an outage is most certainly not clean or stable. I have a basic home entertainment system - nothing fancy - TV, DVD, sound, PVR, VHS ( yes, VHS ), TV games, etc, but combined it probably easily costs in excess of R20K.

                          So while the R600 router is now working ( working = operational, not protected from accelerated electronics wear and tear ), the R20K entertainment system is still subject to 'severe electrical abuse'.

                          This is partly why I started working on my solution. The prototype is done and working, and I am now waiting for PC Boards to be produced.

                          Essentially the "Mains Delay" unit will block mains power to the EC ( entertainment center ) until the mains voltage is consistently in the 210 - 240V range, and then the "Mains Delay" unit has an internal timer to wait a preset number of minutes ( eg 5, 10, 15 minutes ).
                          Only after the timer has run, will the mains be switched on to the EC.

                          The minimum voltage spec, as well as the number of minutes to wait, is set by the user with the buttons on the side of the "Mains Delay" unit.

                          Another very good use for this is on power tools and industrial equipment.

                          Saw another post ( might have been part of your original post ) about a power tool having been left on at the start of outage, and serious hazard when power comes back on. Am thinking grinders, drills, soldering irons, etc.

                          Simply install this unit at the plug point, set the 'time delay' to '0', and once the power is restored it will block the mains power to the equipment until the user presses the button on the unit.

                          That was originally added to the design because I was tired or the missus complaining ( twice !! ) that all the PVR auto-tune and recording settings were lost when the PVR rebooted, unless you 'cancel' the Scan during the PVR bootup.

                          Another perfect place for this is on the supply to my UPS.

                          UPS is great when the mains fails, but on restore, the batteries are 'switched off' and mains supply, no matter how dirty and nasty, is sent directly to my PC. Had 2 PCs in the last 18 months that popped when power came back on.

                          Bottom line is, as you say, put some serious thought into protecting your equipment. Not just when the power dies, but more importantly what it is subject to when the mains returns.
                          Watching the ships passing by.

                          Comment

                          • daveob
                            Email problem

                            • Feb 2008
                            • 655

                            #148
                            Originally posted by tec0
                            Ok what inverter to use, i am told that some inverters can actually damage the refrigerator? I am asking this because I am getting into contact with a supplier that sells a 9000 Watt system for R36k That is not bad because it is a complete working system. Thing is I don't know the makes and parts so in the end I am stepping on a real risk of getting shot in the foot...

                            Questions I will be asking.
                            How strong are the Solar panels?
                            Can the inverter be used on electronics like TV, DVD player, PC Refrigerator and Freezer?
                            How long will everything last under load?
                            Can the batteries be charged from a second source "like generator"?

                            Please add your question here...
                            Hi tec0

                            I would be looking at info like :
                            1. what voltage are the panels ?
                            2. configuration : Series or Parallel.
                            3. what size wire is needed from panels to charge controller.
                            4. what are the battery specs.
                            5. what is the efficiency rating of the inverter ?
                            6. what is the normal and max output of the inverter ?
                            7. how many batteries, and series or parallel ?
                            8. Cooling
                            9. Ventilation
                            10. can the controller also accept input from a wind turbine ?
                            11. where does it dump power when batteries are charged ? Can this be connected to a water heater / pool heater element ?
                            12. what is the battery charging schema ? what is the max voltage / amp sent to the battery. when does it step down as the battery approaches fully charged and at what values, how does it maintain charge ?

                            As a general run of thumb, you can work on the following :

                            assuming 2 x 12V 105aH deep cell batteries, connected in series.
                            So you get a 24V x 105aH power source.
                            24V x 105aH = 2520 watts of power. But that is from fully charged to absolutely completely dead - dead as in destroyed )
                            So you get the battery specs, and find the absolute maximum discharge limit.
                            Remember that hitting that max limit will mean the life span of the batteries is seriously reduced.
                            So maybe you decide to work with a 50% discharge limit.
                            So 2520 watts x 50% = 1260 watts ( usable battery power ).
                            Next it has to pass through the inverter.
                            Cheaper inverter = less efficient.
                            Lets say it is average quality, and eff. is 75% ( so you lose 25% of the energy in the inverter conversion )
                            1260 watts x 75% = 945 watts. btw, that other 25% does go somewhere - heat from the inverter = ventilation requirements.

                            So you can look at the specs on your appliances and work out just how long you can run things for with that amount of power.

                            Personally, I would not run anything with a motor from an inverter ( unless it is a true pure sine wave inverter, but thats $$$$$s ) . It is not good for the motor. AndyD would likely be able to better explain why.
                            Also I would not connect anything that is power hungry, has an element of any kind, etc.

                            A lot of the suitability of this system is going to depend very heavily on the batteries. Their replacement cost is a huge chunk of the cost of the system. Make sure you know everything about those batteries, discharge rates, limits, etc before you part with your cash.

                            Get an independant price for the replacement of the batteries, and factor this into your 'total cost or ownership' as they will need replacing. How often ? depends on usage and abuse. I would probably estimate around 5 years. Sounds long, but if you have 4 batteries x R1500 each = R6000 = average R 1200 per year additional cost. Battery specs will say a life span of something like 10 years. Yes, 10 years - in IDEAL situations, perfect charging schema, minimum discharge rates, etc. This is the real world - half their number.

                            In case you didn't know, batteries have different life expectancy based on rate of discharge.
                            Pull that 1260 watts from the battery in 10 minutes every day, and the battery might last 1 year.
                            Pull same 1260 watts from the battery over 2 hours every day, and it may last 10 years.

                            Look carefully at the specs.

                            2c


                            ps .. you mentioned 9000w

                            Is that 9000w total battery X 50% discharge limit X 75% inverter efficiency = USABLE 3375 watts ? Big difference.

                            9000 w would be around 8 batteries ( 8 batteries x 12v = 96V x 100aH = 9600W x 50% x 75% = 3600 usable )

                            If it is 9000w usable, it would need :
                            9000 usable = 9000 / 75% / 50% = 24000W / 100aH / 12V = 20 batteries.

                            Replacement cost =
                            8 x R 1500 = R 12000
                            or
                            20 x R 1500 = R 30000

                            Based on just the replacement cost of the batteries, it is highly unlikely that the system you are looking at for R36K, including panels, charger, etc, contains 20 deep celll batteries.

                            Chances are it has 6 or 8 batteries, making the usable watts around 3600W - a lot less than the 9000 watts.

                            Ask lots of questions without letting on that you know what you know. If the answers you get are not adding up to what you know, then chances are everything you're being told is 'subject to exageration'.
                            Watching the ships passing by.

                            Comment

                            • IMHO
                              Email problem

                              • Jan 2012
                              • 540

                              #149
                              Originally posted by daveob

                              Another perfect place for this is on the supply to my UPS.

                              UPS is great when the mains fails, but on restore, the batteries are 'switched off' and mains supply, no matter how dirty and nasty, is sent directly to my PC. Had 2 PCs in the last 18 months that popped when power came back on.
                              .
                              Excellent . I lost 4 power supplies to my PABX and eventually the R40K PABX as well.

                              Edit: From behind a UPS.

                              PPS: Maybe the fact that the UPS's batteries was shot and switched on and off the whole time when the AC fail had something to do with it...
                              ;-)
                              ~Expenses will eat you alive! - My first Boss~

                              Comment

                              • IMHO
                                Email problem

                                • Jan 2012
                                • 540

                                #150
                                daveob, i did n fiverr request, thanks for the tip. Did not know about the fiverr concept.
                                ~Expenses will eat you alive! - My first Boss~

                                Comment

                                Working...