Ok in regards to the EIR why would marking the earthing terminal as N/A be acceptable as reasonably safe?
Reason I am asking this is as it is a requirement from 2006 to have said earthing terminal installed. I can understand if the installation was done prior to the publication of said standard as per 6.11.5 (amdt 6 & 8 , 2006 & 2012) that it's valid to argue that it would not be required as it is the same with old (bobbin) wiring used, but where alterations done the installation should then be treated as to the latest standards.
Also unclear as to why the opening notes of Section 5 SANS10142-1 has anything to do with this, if you could also please explain?
5 Fundamental requirements
All commodities in an electrical installation shall be installed in
accordance with the requirements in this part of SANS 10142 and with
the manufacturer’s instructions, where applicable. Amdt 8
NOTE 1 This clause contains the general safety principles applicable to electrical
installations. Amdt 5; amdt 8
NOTE 2 The manufacturer’s instructions may contain more stringent
requirements. Amdt 8
Reason I am asking this is as it is a requirement from 2006 to have said earthing terminal installed. I can understand if the installation was done prior to the publication of said standard as per 6.11.5 (amdt 6 & 8 , 2006 & 2012) that it's valid to argue that it would not be required as it is the same with old (bobbin) wiring used, but where alterations done the installation should then be treated as to the latest standards.
Also unclear as to why the opening notes of Section 5 SANS10142-1 has anything to do with this, if you could also please explain?
5 Fundamental requirements
All commodities in an electrical installation shall be installed in
accordance with the requirements in this part of SANS 10142 and with
the manufacturer’s instructions, where applicable. Amdt 8
NOTE 1 This clause contains the general safety principles applicable to electrical
installations. Amdt 5; amdt 8
NOTE 2 The manufacturer’s instructions may contain more stringent
requirements. Amdt 8






Comment