6 amp socket
  • Gtfast
    • Apr 2016
    • 78
    [Question] 6 amp socket
    I have noticed that unswitched 6 amp sockets have been extensively used to connect fixed roof fans in a building and fixed extractor fans in bathrooms .
    I don't see where the regulations permit the use of 6 amp sockets for these applications . The only place where I can find that 6 amp sockets are allowed are in lighting circuits as per the regulations.
    Is the connection of fixed appliances via 6 amp sockets not from older regulations
    Does one replace all the fixed appliance 6 amp sockets with 16 amp sockets or isolators.
    • 22812
    Interestingly, the 6 amp socket satisfies the requirements of an isolating device.
      • 4927
      With or without one of these?
      There's no reason or regulation I know of that would prevent a BS546 6A skt (aren't they actually 5A?) from being used on any appliance on any circuit as long as the load current and OCPD are suitable.
      • Gtfast
        • Apr 2016
        • 78
        Hi All
        See reg 6.15.2.1 which says socket outlets rated aat less than 16 amp shall not be used unless otherwise allowed. The only place I can see 6 amp sockets are allowed is with lights.With fixed appliances it is not specified.
        Andy what is the red device.Thanks
          • 4927
          It's a padlockable lockout device for a plug to allow safe isolation so nobody can plug the item back in whilst you're working on it.
          • Gtfast
            • Apr 2016
            • 78
            Ok now I can see the device better. I was looking on my cell phone .