6 amp socket

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Gtfast
    Full Member

    • Apr 2016
    • 78

    #1

    [Question] 6 amp socket

    Hi

    I have noticed that unswitched 6 amp sockets have been extensively used to connect fixed roof fans in a building and fixed extractor fans in bathrooms .
    I don't see where the regulations permit the use of 6 amp sockets for these applications . The only place where I can find that 6 amp sockets are allowed are in lighting circuits as per the regulations.

    Is the connection of fixed appliances via 6 amp sockets not from older regulations
    Does one replace all the fixed appliance 6 amp sockets with 16 amp sockets or isolators.
  • Dave A
    Site Caretaker

    • May 2006
    • 22812

    #2
    Interestingly, the 6 amp socket satisfies the requirements of an isolating device.
    Participation is voluntary.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4946

      #3
      With or without one of these?

      Click image for larger version

Name:	lockout.jpg
Views:	1
Size:	11.2 KB
ID:	265038

      There's no reason or regulation I know of that would prevent a BS546 6A skt (aren't they actually 5A?) from being used on any appliance on any circuit as long as the load current and OCPD are suitable.
      _______________________________________________

      _______________________________________________

      Comment

      • Gtfast
        Full Member

        • Apr 2016
        • 78

        #4
        Hi All
        See reg 6.15.2.1 which says socket outlets rated aat less than 16 amp shall not be used unless otherwise allowed. The only place I can see 6 amp sockets are allowed is with lights.With fixed appliances it is not specified.
        Andy what is the red device.Thanks

        Comment

        • AndyD
          Diamond Member

          • Jan 2010
          • 4946

          #5
          It's a padlockable lockout device for a plug to allow safe isolation so nobody can plug the item back in whilst you're working on it.
          _______________________________________________

          _______________________________________________

          Comment

          • Gtfast
            Full Member

            • Apr 2016
            • 78

            #6
            Ok now I can see the device better. I was looking on my cell phone .
            Thanks

            Comment

            Working...