    Load shedding from 12pm - 2 pm ... my earth leakage unit tripped again ... went and had a look at the recorder ... let me put it to you like this ... best you check your insurance is going to pay for damages to electronic equipment.

    You need to install surge protection ... a trip connect ... a surge arrestor at each plug point ... a contactor with a delay timer and every other protective device that you can think of ... yes it is that bad.

    It seems the grid cant handle the load switching ... I am sure eskom have installed relay which switch off the power first them energise the new area being powered ... it looks to me like the grid cant handle the switching .. .what they should have in place is a ripple relay system like they did in the old days ... it was mounted inside every ones DB.
    Comments are based on opinion...not always facts....that's why people use an alias.

    Comment

    • adrianh
      Diamond Member

      • Mar 2010
      • 6328

      #32
      Can't you just install a device to delay the Mains reconnect for a couple of minutes?

      Comment

      • ians
        Diamond Member

        • Apr 2010
        • 3943

        #33
        I changed the settings to dips and swells ... 939 events recorded so far ... all dips ... as low as 151 VAC

        I have been putting some thought into this problem...

        I am at the end of the line (last house on the feed)

        load shedding kicks in ... power switches off .. .the ripple runs down the line and I collect it.

        The power switches on ... the arc on the contact on the load shedding relay as it flashes trying to make contact ... once again a ripple effect down the line.

        But now we have detected a new problem ... voltage dips ... 939 dips recorded since I switched settings on the PQA ... the lights flicker every time I switch on an appliance ... what I think has happened ... there is now a loose connection at the pole or further up stream caused by the load shedding off and on.

        If I look at the trend ... the problem started as the the power switched on after the last stage of load shedding ... it got really bad at 7 pm last night ...dropping as low as 151 VAC for a period of time.

        since then all night you can see the random dips ... destroying my electronic devices.
        Comments are based on opinion...not always facts....that's why people use an alias.

        Comment

        • ians
          Diamond Member

          • Apr 2010
          • 3943

          #34
          I decided to go check the power line feeding my house with the thermal camera ... imagine that a hot spot on the neutral wire ... it looks like a bad connection on the airdac connector.
          Comments are based on opinion...not always facts....that's why people use an alias.

          Comment

          • Justloadit
            Diamond Member

            • Nov 2010
            • 3518

            #35
            Could also be a damaged/pitted contact on the supply switching circuit breakers
            Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
            Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

            Comment

            • ians
              Diamond Member

              • Apr 2010
              • 3943

              #36
              Sine wave is not flat topping anymore ... no more flickering lights ... no more transients on the wave form ... no more tripping earth leakage.

              The electricity department arrived today while I was on site ... wife showed him where the hot spot was ... cut back the wire and replaced the fuse.

              My concern is why is it the fuse and wiring keep burning ... this is not the first time the fuse and wiring has been repaired.

              Besides replacing the fuse and tails ... the light supply cable on the pole burnt off and landed on the the steel arm ... and we all know what happened.
              Comments are based on opinion...not always facts....that's why people use an alias.

              Comment

              • MZOMUHLE
                Email problem
                • Nov 2021
                • 4

                #37
                Earth Leakage trips everytime loadshedding ends

                What the second electrician recommanded is the only way to solve your issue. Remember we do have flow of current in small amount even if line power is switched off. Elevated voltages contribute to that as well even some times loose connections on your nuetral lines.My suggestions.

                Comment

                • GCE
                  Platinum Member
                  • Jun 2017
                  • 1483

                  #38
                  Originally posted by ians

                  My concern is why is it the fuse and wiring keep burning ... this is not the first time the fuse and wiring has been repaired.

                  Besides replacing the fuse and tails ... the light supply cable on the pole burnt off and landed on the the steel arm ... and we all know what happened.
                  Overhead lines are generally aluminum conductors along with aluminum clamps , they use copper wiring directly onto the aluminum instead of using a copper to aluminum lug - There is a reaction between the 2 materials which causes that corrosion and loose connection

                  Comment

                  • ians
                    Diamond Member

                    • Apr 2010
                    • 3943

                    #39
                    Originally posted by GCE
                    Overhead lines are generally aluminum conductors along with aluminum clamps , they use copper wiring directly onto the aluminum instead of using a copper to aluminum lug - There is a reaction between the 2 materials which causes that corrosion and loose connection
                    They use a clamp to hook the copper tail to the ally bundle conductor ... its not a direct connection. The thermal image I took indicated a bad connection at the connector. Maybe they put it on the wrong way.

                    The fluke is still recording double figure transients and some really distorted the wave forms.

                    The earth leakage has stopped tripping.

                    It's time to do a loop impedance test back to the transformer.
                    Comments are based on opinion...not always facts....that's why people use an alias.

                    Comment

                    • Leecatt
                      Silver Member
                      • Jul 2008
                      • 406

                      #40
                      Returning to the original question, my customer had a CBI Earth leakage 3ka which was found to be off whenever the loadshedding finished. I've replaced it with a ACDC 6ka unit and the problem has gone away. Been 3 weeks now.

                      Sent from my SM-A705FN using Tapatalk
                      To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

                      Comment

                      • ians
                        Diamond Member

                        • Apr 2010
                        • 3943

                        #41
                        As the LED supplies will tell you when you return a lamp thats doesnt offer the 50 000 hours as promises ... its a eskom thing ... I have a feeling that the CBI E/L unit has sensitive electronics.

                        The bottom line is load shedding is destroying electronic components ... maybe not today or tomorrow ... that's why I contacted my insurance company to verify that I had cover ( which apparently I don't ... only "lightning" damage).

                        To save myself the additional monthly cost to specify each items in the house ... I am going the ellies plug with built in insurance .. that way offering a little protection with cover.

                        Will make a note for items not specified and wait till we experience a lightning storm like we had the other night and attempt to recover my losses.

                        It is sad to think medical aid and insurance has become industries where you need to dot your i and cross the t ... and you have to learn to play the same game.

                        We talk business profits and losses ... yet if I think back of my biggest financial losses (close to R2M) ... due to bad choices with brokers and cover ... my bad debt for a 30 year old business is no where near that ... there must be more millionaire clubs in the insurance industry than any other industry ... it would be interesting to compare to the pharmaceutical industry.
                        Comments are based on opinion...not always facts....that's why people use an alias.

                        Comment

                        • Derlyn
                          Platinum Member
                          • Mar 2019
                          • 1761

                          #42
                          Pharma wins hands down.
                          Bill Gates says it's the best investment he has ever made.

                          Peace out .. Derek

                          Comment

                          • rodga
                            Junior Member
                            • Nov 2021
                            • 10

                            #43
                            Hi All
                            Was meaning to reply to this thread over the break, but you know how it goes... no load shedding, no problem lol

                            Originally posted by Derlyn
                            I personally don't think it's going to solve the problem.
                            Your 2 earth leakages are still going to be subjected to the same incoming supply which is the suspected cause of the trip. Installing an extra earth leakage is only going to solve the problem if the problem can be re created with the mains switch thus proving that the fault is actually on the installation.
                            Anyway, It will be interesting to know the outcome.

                            The trip connect does basically the same as the fridge safe unit.
                            One will still require a contactor irrespective of which one you use.

                            Spec sheet of fridge safe unit:
                            http://e-systems.co.za/System/FabSheets/4FEAFG16.pdf

                            A tv safe unit can also be used. In my opinion, a better option.

                            The spec sheet of the tv safe unit:
                            http://e-systems.co.za/System/FabSheets/2FEATVG16.pdf

                            Keep us posted.

                            Peace out .. Derek.

                            Edited 17.51 to include tv safe specs.
                            Derek do you agree that the fridge safe unit protects against undervoltage and the tv safe from overvoltage?
                            Would the trip connect unit or the Fridge Guard unit from @justloadit not provide better protection ie under and over voltage protection?

                            Eitherway, I have just ordered a fridge and tv safe unit (had a voucher) but I think the din style trip connect would make for a neater installation - I have 4 modules space left in my board.


                            Is this the correct type of contactor to get?


                            Still would need to get someone in the centurion are to do the instalation for me, if there are any leads?

                            Comment

                            • Derlyn
                              Platinum Member
                              • Mar 2019
                              • 1761

                              #44
                              Hi Rodja. Agreed, but either one will serve the purpose. They both have a time delay before switching on and that's whats needed. A normal delay on timer also does the trick. The first time I saw this was someone using a delay on timer and contactor and it solved his problem.

                              Peace out .. Derek Stuart.

                              Comment

                              • Derlyn
                                Platinum Member
                                • Mar 2019
                                • 1761

                                #45
                                Sorry forgot to mention. That contactor should be fine. You can also use a 3ph rated 25A contactor and parrallel the 3 contacts.