    Originally posted by Derlyn
    Hi Rodja. Agreed, but either one will serve the purpose. They both have a time delay before switching on and that's whats needed. A normal delay on timer also does the trick. The first time I saw this was someone using a delay on timer and contactor and it solved his problem.

    Peace out .. Derek Stuart.
    Ah yes ofcourse. Might as well get the over/under volt protection while im at it.

    Comment

    • rodga
      Junior Member
      • Nov 2021
      • 10

      #47
      So I contacted clearline to ask about the time delay settings on the Trip-Connect 1F unit - its 10 sec or 5 minutes only, the tech guy mentioned that there is a newer programmable unit that will not require a contactor either, so I have ordered that instead. Will also fit better in the little space left in the db.

      Features: - Over current protection, over voltage protection, under voltage protection can disable one , two or three of them. - Voltage and Current Accuracy 0.5% - It’s own power consumption


      Click image for larger version

Name:	12-01036 - Marketing 1.jpg
Views:	1
Size:	27.4 KB
ID:	266129

      Comment

      • rodga
        Junior Member
        • Nov 2021
        • 10

        #48
        Originally posted by rodga
        So I contacted clearline to ask about the time delay settings on the Trip-Connect 1F unit - its 10 sec or 5 minutes only, the tech guy mentioned that there is a newer programmable unit that will not require a contactor either, so I have ordered that instead. Will also fit better in the little space left in the db.

        Features: - Over current protection, over voltage protection, under voltage protection can disable one , two or three of them. - Voltage and Current Accuracy 0.5% - It’s own power consumption


        [ATTACH=CONFIG]8456[/ATTACH]
        Just to update. I installed the above unit last week and everything is working 100% now. No more trips when load shedding ends and no having to wake up at 2/4am to switch the power back on.

        Thanks for the help that everyone provided. Much appreciated.