    COC and test report

    After many hours of reading the new ed 3.1 regs ... I realised that Annexure A is missing.

    There is a test report which includes medical and hazardous locations ... but no actual COC in accordance with 7(1) of the electrical installation regulations 2009.

    Which I have noted in another thread ... the "test report" (not inspection report)

    DO you still need a COC as per Annexure 1 or do you just issue a test report ?

    I am still issuing the old 4 page yellow document and nobody seems to object. I still have a2 books of them from back when I bought a pile of them.

    So when a customer contacts you for a COC ... do they just get a test report ?
    Comments are based on opinion...not always facts....that's why people use an alias.
  • sytcee
    Junior Member
    • Nov 2012
    • 16

    #2
    Where I work, we do not accept the old test report in the 4 paged COC.

    Sent from my SM-N986B using Tapatalk

    Comment

    • ians
      Diamond Member

      • Apr 2010
      • 3943

      #3
      I am master electrician and I have never seen any COC other than the 4 pages ... how scary is that ... so a really stupid question how do people who dont even work in the industry know what a COC looks like ... and people wonder why this industry is in such a F$%^ mess

      Maybe whoever is responsible and I would assume it is the DOL ... should try a little public awareness ... thank goodness electricity is not dangerous.
      Comments are based on opinion...not always facts....that's why people use an alias.

      Comment

      • GCE
        Platinum Member
        • Jun 2017
        • 1483

        #4
        Originally posted by ians
        Maybe whoever is responsible and I would assume it is the DOL ... should try a little public awareness ... thank goodness electricity is not dangerous.
        I thought the change to COC and the requirements and implementation date where pretty much circulated and it is in the Foreword of SANS 10142-1

        The person signing the COC needs to ensure they stay up to date. Unfortunately none of us ever think to read the front pages of SANS until it gets pointed out.

        There has also been whispers coming out that the insurance industry is looking at insisting on a copy of the contractors public liability policy being attached to the COC before they will accept that COC . They want to know that they can sue and collect the money in the case of a fire etc.
        That could sort the industry out at double quick speed or at least ensure that each contractor is incurring the same expense/overhead on insurance.


        SANS 10142-1:2020
        Edition 3

        FOREWORD
        This South African standard was prepared by National Committee
        SABS/TC 067/SC 06, Electricity distribution systems and components –
        Installations, in accordance with procedures of the South African Bureau of
        Standards, in compliance with annex 3 of the WTO/TBT agreement.
        This document was approved for publication in July 2020.
        This document supersedes SANS 10142-1:2017 (edition 2).
        The test report in edition 2 may be used in parallel with the test report in
        edition 3 for a period of 12 months from the date of publication of edition 3.

        With the first edition of this part of SANS 10142, the standard was subdivided
        and now consists of the following parts, under the general title The wiring of
        premises:

        Comment

        • ians
          Diamond Member

          • Apr 2010
          • 3943

          #5
          Originally posted by GCE
          I thought the change to COC and the requirements and implementation date where pretty much circulated and it is in the Foreword of SANS 10142-1

          The person signing the COC needs to ensure they stay up to date. Unfortunately none of us ever think to read the front pages of SANS until it gets pointed out.

          There has also been whispers coming out that the insurance industry is looking at insisting on a copy of the contractors public liability policy being attached to the COC before they will accept that COC . They want to know that they can sue and collect the money in the case of a fire etc.
          That could sort the industry out at double quick speed or at least ensure that each contractor is incurring the same expense/overhead on insurance.


          SANS 10142-1:2020
          Edition 3

          FOREWORD
          This South African standard was prepared by National Committee
          SABS/TC 067/SC 06, Electricity distribution systems and components –
          Installations, in accordance with procedures of the South African Bureau of
          Standards, in compliance with annex 3 of the WTO/TBT agreement.
          This document was approved for publication in July 2020.
          This document supersedes SANS 10142-1:2017 (edition 2).
          The test report in edition 2 may be used in parallel with the test report in
          edition 3 for a period of 12 months from the date of publication of edition 3.

          With the first edition of this part of SANS 10142, the standard was subdivided
          and now consists of the following parts, under the general title The wiring of
          premises:
          Ok so how many people who are not electrician understand what is attached above ... in fact even better how many electricians reading this thread understand what is attached above and do you know what a COC looks like ?

          A test report with a a COC number at the top of the page as illustrated of page 260 on the new SANS ed 3.1 ?
          Comments are based on opinion...not always facts....that's why people use an alias.

          Comment

          • ians
            Diamond Member

            • Apr 2010
            • 3943

            #6
            Lets say I am a person wanting to know more about the COC ... hop onto google and ... It Looks exactly like the one I issue ... annexure 1 at the top ...the only difference is mine have numbers in the B 600 000 range and my COC's is a 4 page yellow document with a pile of other documents attached ... with all the pictures taken and a DB layout with a full description of the circuits and a layout of all the wiring and which circuit feed which outlet ... sometimes it could be 10 -15 pages.

            An Electrical Certificate of Compliance (ECOC) is a legal document that verifies an electrical installation is compliant with regulation.
            Comments are based on opinion...not always facts....that's why people use an alias.

            Comment

            • ians
              Diamond Member

              • Apr 2010
              • 3943

              #7
              Looks exactly the same as the one I have been issuing since I was a member of the ECA more than 20 years ago ... back when Chris Gregory was the chairman and Brian Bilton was the technical advisor

              Need a Electrical Certificate of Compliance?(Based in Benoni) What is it ,How much?You need to know! Home or Business. EBS Services Tel 078-701-0613 more...
              Comments are based on opinion...not always facts....that's why people use an alias.

              Comment

              • ians
                Diamond Member

                • Apr 2010
                • 3943

                #8
                Looks the same ...

                Once your solar PV or backup system has been installed, it’s important to ensure that a Certificate of Compliance (CoC) is issued. Basically, this document checks that the electrician who performed the installation has complied with the rules and regulations that are in place to assure a safe installation.
                Comments are based on opinion...not always facts....that's why people use an alias.

                Comment

                • ians
                  Diamond Member

                  • Apr 2010
                  • 3943

                  #9
                  Originally posted by GCE
                  There has also been whispers coming out that the insurance industry is looking at insisting on a copy of the contractors public liability policy being attached to the COC before they will accept that COC . They want to know that they can sue and collect the money in the case of a fire etc.
                  That could sort the industry out at double quick speed or at least ensure that each contractor is incurring the same expense/overhead on insurance.

                  [/I]
                  The companies I deal with request public liability insurance ... medical clearance ... safety induction before entry to the sites ... Tax clearance certificates ... Safety manuals for work to be carried out on site ... Proof of ownership of test equipment ... the list just goes on and on ... and yet I still have to deal with semi skilled being dropped of who have no idea about safety lockout procedures etc ... and COC's which are not worth the yellow ink used to print the legal document and in many cases in the past are registered with the "hand of safety" ... maybe this issue is a lot bigger than a yellow piece of paper.
                  Comments are based on opinion...not always facts....that's why people use an alias.

                  Comment

                  • ians
                    Diamond Member

                    • Apr 2010
                    • 3943

                    #10
                    his makes me feel old ...

                    Comments are based on opinion...not always facts....that's why people use an alias.

                    Comment

                    • sytcee
                      Junior Member
                      • Nov 2012
                      • 16

                      #11
                      Originally posted by ians
                      After many hours of reading the new ed 3.1 regs ... I realised that Annexure 1 is missing.

                      There is a test report which includes medical and hazardous locations ... but no actual COC in accordance with 7(1) of the electrical installation regulations 2009.

                      Yes, correct. Ed 3 did not intend on changing EI nor can a Standard supercede a Reg. The Reg is still as of EI of 2009.

                      Which I have noted in another thread ... the "test report" (not inspection report)

                      DO you still need a COC as per Annexure 1 or do you just issue a test report ?

                      Indeed, one still needs a one pager COC as per Annex 1 of the Electrical Installation Regulations of 2009 and that has not been changed.

                      I am still issuing the old 4 page yellow document and nobody seems to object. I still have a2 books of them from back when I bought a pile of them.

                      The correct thing would be to use the COC, which Annex 1 and attach New Test report as per Ed 3.

                      So when a customer contacts you for a COC ... do they just get a test report ?
                      Annex 1 of the EI and the new test report as per Ed 3. Operational as at 1 August 2021 , 12 months from publication of the 2020 Ed 3.

                      A note

                      Indeed, there is a room for improvement in information dissemination regarding changes to these standards. It's a challenge to us in the industry to have forums and platforms where we try to make sense of these changes.

                      Unfortunately, writing and researching about OHS is a bit limited, there is need for conscientisation from supply utilities, users including estate agents as well as competent persons.

                      We need to write [emoji871] more about it outside confines of the Associations.

                      Not sure if I have used this App quote appropriately ... [emoji2]

                      Sent from my SM-N986B using Tapatalk

                      Comment

                      • sytcee
                        Junior Member
                        • Nov 2012
                        • 16

                        #12
                        Originally posted by sytcee
                        Annex 1 of the EI and the new test report as per Ed 3. Operational as at 1 August 2021 , 12 months from publication of the 2020 Ed 3.

                        A note

                        Indeed, there is a room for improvement in information dissemination regarding changes to these standards. It's a challenge to us in the industry to have forums and platforms where we try to make sense of these changes.

                        Unfortunately, writing and researching about OHS is a bit limited, there is need for conscientisation from supply utilities, users including estate agents as well as competent persons.

                        We need to write [emoji871] more about it outside confines of the Associations.

                        Not sure if I have used this App quote appropriately ... [emoji2]

                        Sent from my SM-N986B using Tapatalk
                        Ow well, I included my responses in the quote. [emoji3064]. Sorry.

                        Sent from my SM-N986B using Tapatalk

                        Comment

                        • sytcee
                          Junior Member
                          • Nov 2012
                          • 16

                          #13
                          Originally posted by ians
                          I am master electrician and I have never seen any COC other than the 4 pages ... how scary is that ... so a really stupid question how do people who dont even work in the industry know what a COC looks like ... and people wonder why this industry is in such a F$%^ mess

                          Maybe whoever is responsible and I would assume it is the DOL ... should try a little public awareness ... thank goodness electricity is not dangerous.
                          It's a nightmare out there with even registered persons not sure of what to follow. Keeping up to date, as pointed out here below is not easy for everyone.

                          Estate Agents and Insurance Companies should do better.

                          Supply Authorities with the exclusion of Eskom should step up. Eskom have other issues to deal with and are officially incapacitated.

                          DoL is officially incapacitated.

                          Competent Persons should know that even the Standards can not protect them in case of legal liability, apparently.

                          Associations and Boards should be empowered

                          ECSA (Engineering Council) should close the existing lacuna in terms of recognition of Competent Persons especially Electrical Inspectors.

                          Researchers should authoritatively write and be open to critique and peer to peer reviews.

                          Otherwise, the mayhem will continue unabated!

                          Sent from my SM-N986B using Tapatalk

                          Comment

                          • sytcee
                            Junior Member
                            • Nov 2012
                            • 16

                            #14
                            Originally posted by GCE
                            I thought the change to COC and the requirements and implementation date where pretty much circulated and it is in the Foreword of SANS 10142-1

                            The person signing the COC needs to ensure they stay up to date. Unfortunately none of us ever think to read the front pages of SANS until it gets pointed out.

                            There has also been whispers coming out that the insurance industry is looking at insisting on a copy of the contractors public liability policy being attached to the COC before they will accept that COC . They want to know that they can sue and collect the money in the case of a fire etc.
                            That could sort the industry out at double quick speed or at least ensure that each contractor is incurring the same expense/overhead on insurance.


                            SANS 10142-1:2020
                            Edition 3

                            FOREWORD
                            This South African standard was prepared by National Committee
                            SABS/TC 067/SC 06, Electricity distribution systems and components –
                            Installations, in accordance with procedures of the South African Bureau of
                            Standards, in compliance with annex 3 of the WTO/TBT agreement.
                            This document was approved for publication in July 2020.
                            This document supersedes SANS 10142-1:2017 (edition 2).
                            The test report in edition 2 may be used in parallel with the test report in
                            edition 3 for a period of 12 months from the date of publication of edition 3.

                            With the first edition of this part of SANS 10142, the standard was subdivided
                            and now consists of the following parts, under the general title The wiring of
                            premises:
                            Precisely.

                            Additionally, I think Supply Utilities or DoL or AIA should be involved in approving every COC. A suggestion for there to be an amendment to the EI of 2009.

                            An approval must include an onsite inspection. Any disputes arising, be referred to the Chief Inspector or their delegated powers , knowing they can't handle all.

                            My suggestion...

                            Sent from my SM-N986B using Tapatalk

                            Comment

                            • ians
                              Diamond Member

                              • Apr 2010
                              • 3943

                              #15
                              The bottom line ... whoever is responsible for the registration of inspectors ... making the rules and regs and enforcing them should be responsible for making sure that there is adequate means of awareness ... be it training ... seminars etc ... it should not be left up to private ass. to manage ... if it is then ... "everyone" should have access to the information and a legal requirement that everyone is registered with that ass. ... credits be earned to retain your ability to sign a legal document ... just like they do with engineers.

                              Every single COC issued should be recorded on a central data base which can be accessed by authorised personal to investigate any queries or disputes ... this bullshyte that if the public have to pay for an investigation ... then the matters is handed to ass.

                              For the record how many registered electrical contractors are operating in SA at present ... how many illegal contractors ... how many registered with one or other ass. ... maybe these figue will hlep to understand the size of this problem.

                              To give you a little background ... I was member of the ECA for many many years ... I could see Brian eyes rolling back as he saw my number pop up on his phone ... I was all for doing everything 100 % to the book ... I qualified as an electrician at Olifantsfontein ... did all my NTC training course ... went to night school studied to become a installation electrician ... did the years of practical then applied to get my yellow card (installation electrician) ... working commercial wiring up shopping centres ... then moved on to maintenance ... once I got my yellow card I went back to tech and studied to become a master electrician ... wired up spray booths worked in hospitals ... sugar mills ... mondi ...sappi ... in Cape Town I did class 1 installation ... DB's control systems even the instrumentation art of the job ... my CV is like reading a book ... eventually once I gained enough experience and passed all the exams required ... I them applied to become a master electrician ... eventually I received my red card ... It made me feel proud that I had achieved what I set out to do after many years ... I did trade assessments for a couple of years ... now its just embarrassing to be an electrician.

                              The way I see it if you going to manage the industry and take on the responsibility of managing the industry ... at least try do a better job ... the electrical industry is joke.