page 196 6.16.1.9
6.16.1.9 Unless part of the appliance or self contained in their own
enclosure, control components of fixed appliances that form part of the fixed
installation, including their input terminations and associated protective
switchgear that are not mounted in the distribution board, shall be
incorporated in a suitable enclosure(s) that comply with the requirements of
6.6.1 and 6.6.4. Enclosure(s) shall be
a) non-flammable,
b) located as near to the appliance(s) as is practicable,
c) permanently installed,
d) such that they cannot be opened without the use of a tool, and
e) readily accessible.
now light fittings are a fixed appliance
page149 4.8 wiring thru building elements
if wiring passes through a building element including a ceiling it shall be non flammable enclosure or wireway
only by putting as box flush with the ceiling and screwing the light fitting to the box can you have an enclosure, or of course put the pipe through and into the light fitting
so accordingly I still say no exposed wiring in the ceilingComment
-
Couple of crossed lines here. The supply circuitry is not included in: "page 196 6.16.1.9
6.16.1.9 Unless part of the appliance or self contained in their own
enclosure, control components of fixed appliances that form part of the fixed
installation, including their input terminations and associated protective
switchgear that are not mounted in the distribution board, shall be
incorporated in a suitable enclosure(s) that comply with the requirements of
6.6.1 and 6.6.4. Enclosure(s) shall be
a) non-flammable,
b) located as near to the appliance(s) as is practicable,
c) permanently installed,
d) such that they cannot be opened without the use of a tool, and
e) readily accessible."
It specifically states:control components; terminations and switchgear.
The main thing here which we all agree on it seems is not quite "open wiring" but rather "exposed conductors" are a no-no. If the installation is old enough to have "open wiring" and that wiring is still as installed with all the cleats in place and no sagging, illegal joints, the correct spacing etc. and the insulation resistance readings are >1MOhm then I see no reason to fail the installation based on the fact that it is "open wiring". In most cases I have found the readings much better than T/E
Even T/E needs to be installed as per guidlines, not just loosely thrown over the beams where it is easier to work with.Comment
-
Because it'll bite you in the ass one day. Rumour and misinformation seems to have a knack for spreading faster than the dry truth.
I had one about a month ago - a purchaser of a property we'd issued the COC on had been told a whole pile of tripe by another electrician. The on-site meeting (with SANS codes firmly to hand) to clarify was actually a pleasant experience (at least for me
). Biting my tongue and taking the pile of abuse that was hurled at me as I was working on setting up that meeting was definitely not a pleasure.
I don't think the pleasure in the end was worth the pain in the beginning, and I'm pretty sure the other electrician wasn't to enamored with the experience either.
Play it straight as you can, I reckon. There's enough BS in this world without adding to it intentionally.Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene ServicesComment
-
Oh - there's a "next page" I hadn't read when I made the previous reply...
I've got a question:
At the risk of showing my ignorance, isn't this section requiring enclosures relating to the control components, protective switch gear etc. rather than the fixed appliance itself?
If yes, I don't see how it is relevant to light point terminations.Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene ServicesComment
-
It specifically states:control components; terminations and switchgear with reference to "fixed appliances" which is what a light fitting is. But yet again the actual words can be brought in to it.
Wires /conductors?
Light fittings/ luminaires?
spade/shovel?Comment
-
At the risk of being difficult, when it comes to input terminations, surely that is the input terminations to the control components et al.
Then there's the matter that lights are not just "ordinary" fixed appliances - they're luminaires.
In support of my point, consider 6.16.1.4 which states:
Where a fan or heater is included in a luminaire, the luminaire is regarded as a fixed appliance....Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene ServicesComment



Comment