  • murdock
    Suspended

    • Oct 2007
    • 2346

    #16
    use a bootlace ferrol...which should become a standard for all connections which have screws directly onto the wires like the ones issued with stove islolators

    Comment

    • natal21
      Email problem
      • Oct 2011
      • 12

      #17
      As far as I knew every pipe feeding a light unless ending in a adapter screwed into the light , had to be ended off in a box. By law

      Comment

      • murdock
        Suspended

        • Oct 2007
        • 2346

        #18
        Originally posted by natal21
        As far as I knew every pipe feeding a light unless ending in a adapter screwed into the light , had to be ended off in a box. By law
        give us the code reference or description...

        Comment

        • Sparks
          Gold Member

          • Dec 2009
          • 909

          #19
          I've also used non-existing regs as an excuse to teach someone a more acceptable work ethic. If it works why not?

          Comment

          • AndyD
            Diamond Member

            • Jan 2010
            • 4946

            #20
            Hmmm, I'm not sure making up regs to suit the situation is a good idea, even to promote good work ethic.
            _______________________________________________

            _______________________________________________

            Comment

            • natal21
              Email problem
              • Oct 2011
              • 12

              #21
              page 196 6.16.1.9
              6.16.1.9 Unless part of the appliance or self contained in their own
              enclosure, control components of fixed appliances that form part of the fixed
              installation, including their input terminations and associated protective
              switchgear that are not mounted in the distribution board, shall be
              incorporated in a suitable enclosure(s) that comply with the requirements of
              6.6.1 and 6.6.4. Enclosure(s) shall be
              a) non-flammable,
              b) located as near to the appliance(s) as is practicable,
              c) permanently installed,
              d) such that they cannot be opened without the use of a tool, and
              e) readily accessible.

              now light fittings are a fixed appliance

              page149 4.8 wiring thru building elements

              if wiring passes through a building element including a ceiling it shall be non flammable enclosure or wireway

              only by putting as box flush with the ceiling and screwing the light fitting to the box can you have an enclosure, or of course put the pipe through and into the light fitting

              so accordingly I still say no exposed wiring in the ceiling

              Comment

              • murdock
                Suspended

                • Oct 2007
                • 2346

                #22
                i just need to get this straight...so you telling me every single light fitting you install has a box above the light where the light is terminated or a pipe which is flush with the ceiling?

                do you do twin + e installations?

                Comment

                • natal21
                  Email problem
                  • Oct 2011
                  • 12

                  #23
                  use a screw in gland as an entry point, not gonna argue with you , feel free to do your installations as you see fit but the question was about exposed wiring not twin and earth

                  Comment

                  • natal21
                    Email problem
                    • Oct 2011
                    • 12

                    #24
                    sorry forgot to answer your question , but we don't do flush pipes to ceiling, every light ends in a loop in box when we do pipe and wires and the boxes vare all fastened to a batten so they sit flush with the ceiling when its installed.

                    Comment

                    • Sparks
                      Gold Member

                      • Dec 2009
                      • 909

                      #25
                      Couple of crossed lines here. The supply circuitry is not included in: "page 196 6.16.1.9
                      6.16.1.9 Unless part of the appliance or self contained in their own
                      enclosure, control components of fixed appliances that form part of the fixed
                      installation, including their input terminations and associated protective
                      switchgear that are not mounted in the distribution board, shall be
                      incorporated in a suitable enclosure(s) that comply with the requirements of
                      6.6.1 and 6.6.4. Enclosure(s) shall be
                      a) non-flammable,
                      b) located as near to the appliance(s) as is practicable,
                      c) permanently installed,
                      d) such that they cannot be opened without the use of a tool, and
                      e) readily accessible."
                      It specifically states:control components; terminations and switchgear.

                      The main thing here which we all agree on it seems is not quite "open wiring" but rather "exposed conductors" are a no-no. If the installation is old enough to have "open wiring" and that wiring is still as installed with all the cleats in place and no sagging, illegal joints, the correct spacing etc. and the insulation resistance readings are >1MOhm then I see no reason to fail the installation based on the fact that it is "open wiring". In most cases I have found the readings much better than T/E

                      Even T/E needs to be installed as per guidlines, not just loosely thrown over the beams where it is easier to work with.

                      Comment

                      • Dave A
                        Site Caretaker

                        • May 2006
                        • 22810

                        #26
                        Originally posted by Sparks
                        If it works why not?
                        Because it'll bite you in the ass one day. Rumour and misinformation seems to have a knack for spreading faster than the dry truth.

                        I had one about a month ago - a purchaser of a property we'd issued the COC on had been told a whole pile of tripe by another electrician. The on-site meeting (with SANS codes firmly to hand) to clarify was actually a pleasant experience (at least for me ). Biting my tongue and taking the pile of abuse that was hurled at me as I was working on setting up that meeting was definitely not a pleasure.

                        I don't think the pleasure in the end was worth the pain in the beginning, and I'm pretty sure the other electrician wasn't to enamored with the experience either.

                        Play it straight as you can, I reckon. There's enough BS in this world without adding to it intentionally.
                        Participation is voluntary.

                        Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                        Comment

                        • Dave A
                          Site Caretaker

                          • May 2006
                          • 22810

                          #27
                          Oh - there's a "next page" I hadn't read when I made the previous reply...

                          I've got a question:

                          Originally posted by Sparks
                          6.16.1.9 Unless part of the appliance or self contained in their own
                          enclosure, control components of fixed appliances...
                          At the risk of showing my ignorance, isn't this section requiring enclosures relating to the control components, protective switch gear etc. rather than the fixed appliance itself?

                          If yes, I don't see how it is relevant to light point terminations.
                          Participation is voluntary.

                          Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                          Comment

                          • Sparks
                            Gold Member

                            • Dec 2009
                            • 909

                            #28
                            It specifically states:control components; terminations and switchgear with reference to "fixed appliances" which is what a light fitting is. But yet again the actual words can be brought in to it.

                            Wires /conductors?
                            Light fittings/ luminaires?
                            spade/shovel?
                            Last edited by Sparks; 19-Oct-11, 07:22 AM. Reason: incomplete

                            Comment

                            • Dave A
                              Site Caretaker

                              • May 2006
                              • 22810

                              #29
                              At the risk of being difficult, when it comes to input terminations, surely that is the input terminations to the control components et al.

                              Then there's the matter that lights are not just "ordinary" fixed appliances - they're luminaires.

                              In support of my point, consider 6.16.1.4 which states:
                              Where a fan or heater is included in a luminaire, the luminaire is regarded as a fixed appliance....
                              Participation is voluntary.

                              Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                              Comment

                              • Sparks
                                Gold Member

                                • Dec 2009
                                • 909

                                #30
                                So you would find acceptable the connection of a "light fitting" where the ceiling rose is amiss and the joints are below the ceiling? :-)

                                Comment