Saturday at home, installing an inverter

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • tec0
    Diamond Member

    • Jun 2009
    • 4624

    #166
    Click image for larger version

Name:	1.jpg
Views:	1
Size:	13.6 KB
ID:	264632

    **************************
    edit


    Built-in intelligent battery charger prolongs battery life
    Battery saving function prevents the batteries from going flat when not in use
    Low battery disconnect function automatically disables inverter when batteries reach minimum charge
    Fossil fuel and pollution free
    Input power : 24 Volt DC

    FBIT2000.pdf
    FBI2000W.pdf
    pricecheck

    **************************

    This is the FBI2000W inverter/uninterruptible Power Supply AKA UPS unit build by ELLIES and available at a cost of about R8550 (give or take) for the unit. You get two 12 Volt 100 Amp batteries "depending on model and distributor and specifications. It is cool looking system and is like a normal UPS we all love and know form the PC world.

    This unit is able to handle a second set of batteries or so i am told. So it works just fine BUT there are a few things you need to know about this system.

    First and foremost is the running cost. It will consume about 129 Watts of power while charging (again based on this model others may be more or even less) Batteries will set you back about R1600 to about R2500+ depending on make or model.

    Secondly it has two settings. The one is called "Narrow" and the other is called "Wide" Now the trick here is you need to identify what you want it to do. If you want to run. The "Narrow" setting is used for "tube lights, energy saving lamps Television set" NOTE NOT SUITABLE TO MEET HIGH POWER MOTORS and they even warn you about a PC... The mode runs within 170-280Vac

    Now the second setting "Wide" is recommended for things like "lamps and or a fan" The mode runs within 90-280Vac and is not as sensitive or so the manual claims.

    Now on a high load you will get a couple of hours but according to the box and manual on lower loads it will last longer. Now my power load will be in the 240 watt range so i am not to worried.

    But base on the info i got i will be installing a second system just for my Freezer and refrigerator and this one will be used for my basics.

    Last thing when you turn it on it will make a fizzing noise and if it switches to the inverter the fans kicks in and does make a noise.

    Cool thing is the power consumption my generator can charge this system with ease and that to me is a big plus.

    hope this helps
    Last edited by tec0; 26-Jun-15, 11:46 PM.
    peace is a state of mind
    Disclaimer: everything written by me can be considered as fictional.

    Comment

    • Justloadit
      Diamond Member

      • Nov 2010
      • 3518

      #167
      At 129Watts consumption for battery charging, it is going to take approximately 12 hours to reach 80% of battery capacity if your 2 batteries are discharged by 50%, and the another 12 hours will be trickle charge mode to get 100% capacity.
      Running your genny for that long, you might as well connect the loads directly to the genny.
      Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
      Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

      Comment

      • tec0
        Diamond Member

        • Jun 2009
        • 4624

        #168
        Originally posted by Justloadit
        At 129Watts consumption for battery charging, it is going to take approximately 12 hours to reach 80% of battery capacity if your 2 batteries are discharged by 50%, and the another 12 hours will be trickle charge mode to get 100% capacity.
        Running your genny for that long, you might as well connect the loads directly to the genny.
        I noticed something but want to make sure before i post it here, I think it is regulating itself but i am not sure yet so i want to test it with tomorrow's load-shedding and see how much it will pull for charging thereafter. But this is not fact yet so let me first get firsthand data for us. I have a suspicion that it might actually consume more power if the batteries are drained. I added the above in the edit section "Built-in intelligent battery charger" the word intelligent may well suggest that this may be the case but because i don't know yet i cannot say it is 100% true.

        I rather test it and give you my actual readings that way we know fact from fiction.
        Last edited by tec0; 26-Jun-15, 11:52 PM.
        peace is a state of mind
        Disclaimer: everything written by me can be considered as fictional.

        Comment

        • tec0
          Diamond Member

          • Jun 2009
          • 4624

          #169
          Ok it is self-regulating and pulls about 200 Watt "give or take" i cannot get a clean reading from my power monitor but it appears to be 200 Watts. It does go down as the batteries gets charged. That said i had lights i watched the news, did computing had my creature comforts. In total i consumed 271 Watts of power from the system. It wasn't that loud, it didn't get hot. I am happy with the product. But i will be adding a second bank of two 12 volt 100 Amp batteries very soon. Because today we where without power for basically from 10 AM to about 9 PM not due to load-shedding... something went wrong according to local news.

          By using my generator for my refrigeration and my inverter "at night" i cannot complain.
          peace is a state of mind
          Disclaimer: everything written by me can be considered as fictional.

          Comment

          • Justloadit
            Diamond Member

            • Nov 2010
            • 3518

            #170
            Yep sounds like the charger pushes 200W so effectively it will charge you bank in 24 hours. Just remember that by adding more batteries, the charger may not be able to charge the full bank in 24 hours
            Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
            Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

            Comment

            • tec0
              Diamond Member

              • Jun 2009
              • 4624

              #171
              Originally posted by Justloadit
              Yep sounds like the charger pushes 200W so effectively it will charge you bank in 24 hours. Just remember that by adding more batteries, the charger may not be able to charge the full bank in 24 hours
              I am thinking about adding a second bank because it will help me a lot. At times our power is out for about 12 hours continuously normally the excuse is feeder cables and or theft. Regardless we cannot function anymore, our home became nothing more then a cold dark cave. So we are forced. I will be thinking about buying a second system rather. Same inverter but will be buying other type of batteries. The Batteries are still deep cycle batteries but over all cheaper and supplied by battery centre. They are also 12 Volt 100 AMP batteries

              I finally got a quotation for complete solar system. It runs towards the R59K mark. It is not a bad system pushing about 3000-Watts. It can also charge from both solar and mains and that is always a plus.

              Anyhow the system as it is now, I am happy with it... What i would like to add is a second system and perhaps keep the loads low on both.
              peace is a state of mind
              Disclaimer: everything written by me can be considered as fictional.

              Comment

              • blackknight72
                Full Member
                • May 2015
                • 26

                #172
                Originally posted by AndyD
                Did you set the battery type to flooded in the program menu? I think it's perameter 05 should be set to 'FLD' for lead acid baytteries but check in your manual. If it already is then try setting to 'user defined' and set the low alarm and other voltages manually later in the program.
                Hi Andy,

                Thank you for your earlier feedback.

                Today the electric contractor came to check the settings in the inverter again. According to him the setting was right. The batteries were checked twice and we're found not faulty. The inverter works normally in DC mode. However when power is back it shows the message that batteries are over charging. The contractor says the batteries are supposed to be 100 AH where as mine is 240ah. From what I can remember you were using 225Ah. Do you think this could be a problem? I was offered T125s in the place of T105s as they were not available and because of more or less same spec. I downloaded the user manual for Axpert inverter and it mentions the recommended battery amperage as 200Ah. I am so worried since I am not sure if the battery seller will replace it. Awaiting your input.

                Jay

                Comment

                • blackknight72
                  Full Member
                  • May 2015
                  • 26

                  #173
                  I picked up two issues while chatting to the contractor today evening. He was using 4AWG instead of 8 AMG for cabling. After installation apparently the inverter tripped while the kettle was switched on. Obviously he forgot to exclude that line. Can any of these lead to faults leading to battery over charging? having sleepless nights

                  Comment

                  • AndyD
                    Diamond Member

                    • Jan 2010
                    • 4951

                    #174
                    Originally posted by blackknight72
                    Hi Andy,

                    Thank you for your earlier feedback.

                    Today the electric contractor came to check the settings in the inverter again. According to him the setting was right. The batteries were checked twice and we're found not faulty. The inverter works normally in DC mode. However when power is back it shows the message that batteries are over charging. The contractor says the batteries are supposed to be 100 AH where as mine is 240ah. From what I can remember you were using 225Ah. Do you think this could be a problem? I was offered T125s in the place of T105s as they were not available and because of more or less same spec. I downloaded the user manual for Axpert inverter and it mentions the recommended battery amperage as 200Ah. I am so worried since I am not sure if the battery seller will replace it. Awaiting your input.

                    Jay
                    I think the reason they recommend 200Ah batteries is because of the capabilities of the charger but I've installed 3Kw Axpert inverters with paralleled double battery banks of T105's so I can't see how a single bank of 240Ah could be a problem.

                    Originally posted by blackknight72
                    I picked up two issues while chatting to the contractor today evening. He was using 4AWG instead of 8 AMG for cabling. After installation apparently the inverter tripped while the kettle was switched on. Obviously he forgot to exclude that line. Can any of these lead to faults leading to battery over charging? having sleepless nights
                    I'd suggest your battery wiring should be minmum of 35mm sq which, if you want to work in American Wire Gauge is very close to 2AWG. Peak DC current could be easily 100Amps with a 3kW 24v inverter for example.

                    Start at the beginning, outline exactly what system you have, please give inverter model number and the number of batteries and their exact configuration. Please also double check your stated 4AWG DC wiring is definitely what was installed. I'm not trying to run you around in circles I just want to rule out any possible basic causes before we go looking deeper.
                    _______________________________________________

                    _______________________________________________

                    Comment

                    • blackknight72
                      Full Member
                      • May 2015
                      • 26

                      #175
                      Originally posted by AndyD
                      I think the reason they recommend 200Ah batteries is because of the capabilities of the charger but I've installed 3Kw Axpert inverters with paralleled double battery banks of T105's so I can't see how a single bank of 240Ah could be a problem.

                      I'd suggest your battery wiring should be minmum of 35mm sq which, if you want to work in American Wire Gauge is very close to 2AWG. Peak DC current could be easily 100Amps with a 3kW 24v inverter for example.

                      Start at the beginning, outline exactly what system you have, please give inverter model number and the number of batteries and their exact configuration. Please also double check your stated 4AWG DC wiring is definitely what was installed. I'm not trying to run you around in circles I just want to rule out any possible basic causes before we go looking deeper.

                      Hello Andy,

                      Many thanks for your response.

                      I am using Axpert 3KW MKS plus 24 volt inverter with four 240Ah (Trojan T125) 6volt batteries connected in series with a fuse to protect the batteries based on your input. I asked the electrician to put up a mini DB to for the essential circuit. However while the inverter was connected and undergoing testing a kettle was switched on which was not bypassed and hence the machine tripped. Apparently it worked for an hour without issues.

                      The electrician acknowledges that he has used only ' flexible DC cable' instead of any of the recommended AWG wires. Could this be a factor leading to faulty charging?

                      The model number of the inverter is SOL-I-AX--3MPLUS24.

                      Hope this information is adequate.

                      Comment

                      • AndyD
                        Diamond Member

                        • Jan 2010
                        • 4951

                        #176
                        A kettle could quite easily cause overload, kettles are a high load especially if they're these new fast boil types. Overload is not likely to damage the inverter, I've run my Axpert into every type of overload possible including a range of short circuit faults and it's not shown any signs of damage so I doubt very much the kettle caused the issues.

                        I can't see anything wrong off-hand with the setup you mention, I'd suggest being absolutely methodical, recheck and remake every battery and fuse termination to start with.
                        _______________________________________________

                        _______________________________________________

                        Comment

                        • blackknight72
                          Full Member
                          • May 2015
                          • 26

                          #177
                          Originally posted by AndyD
                          I think the reason they recommend 200Ah batteries is because of the capabilities of the charger but I've installed 3Kw Axpert inverters with paralleled double battery banks of T105's so I can't see how a single bank of 240Ah could be a problem.

                          I'd suggest your battery wiring should be minmum of 35mm sq which, if you want to work in American Wire Gauge is very close to 2AWG. Peak DC current could be easily 100Amps with a 3kW 24v inverter for example.

                          Start at the beginning, outline exactly what system you have, please give inverter model number and the number of batteries and their exact configuration. Please also double check your stated 4AWG DC wiring is definitely what was installed. I'm not trying to run you around in circles I just want to rule out any possible basic causes before we go looking deeper.
                          Andy, Thank you so much for the response.

                          The system is as follows.

                          Axpert 3KW MKS plus 24 volt
                          Model number SOL-I--AX--3MPLUS24
                          Batteries four 240Ah batteries (T125) connected serially with a fuse
                          Cabling: 'flexible DC wiring' (not any of the AWG rated) he says it is a thick cable.
                          A mini DB was put to isolate essential circuits to the inverter.

                          Batteries checked twice by the contractor and the battery supplier and found to have no faults.
                          settings checked for battery by installer and he couldn't see any issues.

                          Works normal on DC. Shows fault code 3 when AC is back after a brief delay.This is where we stand now.

                          Comment

                          • blackknight72
                            Full Member
                            • May 2015
                            • 26

                            #178
                            Just now noted your earlier response. The seller has agreed to change the inverter for a new one. I am trying it tomorrow. Hoping for the best.

                            Comment

                            • AndyD
                              Diamond Member

                              • Jan 2010
                              • 4951

                              #179
                              I really think it's a very very slim chance that the problem is being caused by the batteries being 240Ah. If the installer really can't find the problem then either he needs to install another similar inverter to see if the fault persists or not or try 4 different batteries on the existing system in order to localise the fault to either the inverter or the batteries and cabling.
                              _______________________________________________

                              _______________________________________________

                              Comment

                              • tec0
                                Diamond Member

                                • Jun 2009
                                • 4624

                                #180
                                update, we had a long power-out yesterday, no problems really system lasted for 5 hours and had power left in the end. was pulling 240 watts "got LED lights" installed that took the demand down a bit. My TV consumes 115 Watts of power but i will be downing it soon. Looking for a better TV. my hope is to get it to an even 200 watts.

                                Generator took care of my refrigeration... I will not be adding batteries to this system i am planning on building a second system rather that will have 2 banks of batteries... Batteries I am looking to use are 6Volts but pushes 150 AMPS. Just want to confirm that the charger would be able to handle it first.
                                peace is a state of mind
                                Disclaimer: everything written by me can be considered as fictional.

                                Comment

                                Working...