How to CoC a changeover switch??

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • deejaypsy
    Full Member

    • Jun 2012
    • 69

    #1

    How to CoC a changeover switch??

    Please could someone explain what needs to be filled in on the CoC form in order to CoC a changeover switch?
    A standby generator has been wired into a changeover switch to switch between mains and generator in the event of a power failure.
    What readings do i have to put on the form in order to satisfy the CoC?
    Thanks a lot
    Simon
    We are not human beings undergoing a spiritual phase.....we are spiritual beings undergoing a human phase....
  • Lourens.dL
    Junior Member
    • Apr 2014
    • 23

    #2
    Don't think that you MUST include everything on the COC when you only certify one part.
    Of cause you must include everything related.

    I would think things like the earthing, PSC, Z'L, phase rotation is important.

    Make sure that you specify exactly what is included with the certificate and what is excluded.

    For instance the DB and circuits might be excluded from your certificate but it could mean more work for you if you offer to include it.

    Sent from my GT-I9500 using Tapatalk

    Comment

    • deejaypsy
      Full Member

      • Jun 2012
      • 69

      #3
      Yeah, thats what i figured.
      PSCC, Loop & Earthing.
      Not much else to test as i haven't worked on anything else.
      And then just to make it clear in the section that asks what the CoC covers, to state that it covers only the changeover switch installation.
      We are not human beings undergoing a spiritual phase.....we are spiritual beings undergoing a human phase....

      Comment

      • Sparks
        Gold Member

        • Dec 2009
        • 909

        #4
        The COC is for the new parts to the installation and is noted in the right-hand column. What you added must be indicated. Exclusions such as the original/existing installation must be excluded. You also need to indicate your alternative supply voltages and indicate that as such, in addition to the above stated replies.

        Comment

        • Leecatt
          Silver Member
          • Jul 2008
          • 409

          #5
          I hate to be the party pooper here but unfortunately The Regulations are quite specific about additions to an electrical circuit.
          In short, you may not issue an electrical certificate for the genny until you are absolutely 100% certain that the rest of the circuit complies and the only way to do that is to perform an inspection on the entire circuit and if not already done, issue a coc for the entire circuit.
          Effectively, once you issue an additional coc for any additional circuit or any alteration to an existing circuit, you take responsibility for the entire electrical circuit, something few people are aware of.

          Reference: OCCUPATIONAL HEALTH AND SAFETY ACT, 1993 ELECTRICAL INSTALLATION REGULATIONS

          Issuing of certificate of compliance
          9.
          (1) No person other than a registered person may issue a certificate of compliance.

          (2) A registered person may issue a certificate of compliance accompanied by the required test report only after having satisfied himself or herself by means of an inspection and test that
          (a)a new electrical installation complies with the provisions of regulation 5(1) and was carried out under his or her general control; or
          (b)an electrical installation which existed prior to the publication of the current edition of the health and safety standard incorporated into these Regulations in terms of regulation 5(1), complies with the general safety principles of such standard; or
          (c)an electrical installation referred to in paragraph (b), to which extensions or alterations have been effected, that
          (i) the existing part of the electrical installation complies with the general safety principles of such standard and is reasonably safe, and
          (ii) the extensions or alterations effected comply with the provisions of regulation 5(1) and were carried out under his or her general control.

          (3)If at any time prior to the issuing of a certificate of compliance any fault or defect is detected in any part of the electrical installation, the registered person shall refuse to issue such certificate until that fault or defect has been rectified: Provided that if such fault or defect in the opinion of the registered person constitutes an immediate danger to persons in a case where electricity is already supplied, he or she shall forthwith take steps to disconnect the supply to the circuit in which the fault or defect was detected and notify the chief inspector thereof.

          (4)Any person who undertakes to do electrical installation work shall ensure that a valid certificate of compliance is issued for that work.

          (5)No person may amend a certificate of compliance.
          Last edited by Leecatt; 26-Feb-15, 08:28 AM. Reason: Typos
          To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

          Comment

          • Sparks
            Gold Member

            • Dec 2009
            • 909

            #6
            In my book you have just added a new section to an existing one and as such the existing installation must be "reasonably safe"
            Your COC need also only cover the addition/alteration.

            Comment

            • deejaypsy
              Full Member

              • Jun 2012
              • 69

              #7
              I tend to agree with you Sparks.
              If you have added something to the installation then only that addition needs to be CoC'd, not the entire installation surely?
              If you were asked to add an extra plug to a kitchen circuit for example, and while you were installing this you noticed that there were illegal electrics elsewhere, then i am in agreement that you would point this out and tell the owner that you would need to inspect & rectify the rest of the installation in order to issue a CoC, as you could not just walk away knowing that there are illegal connections (even if they are not your own).
              But if the installation is reasonably safe from a visual perspective, then I would only CoC that extra plug that i was asked to install...
              Would you climb in the roof and check for open junction boxes, illegal wiring, etc, after completing your plug install, or would you visually inspect what is around you and make an assessment that what you see is reasonably safe, give your CoC for the plug and leave??
              Just wondering to what extent you need to continue through the installation if the mainboard and kitchen circuit looked legal...
              Thanx for your input.
              We are not human beings undergoing a spiritual phase.....we are spiritual beings undergoing a human phase....

              Comment

              • Leecatt
                Silver Member
                • Jul 2008
                • 409

                #8
                Originally posted by deejaypsy
                I tend to agree with you Sparks.
                If you have added something to the installation then only that addition needs to be CoC'd, not the entire installation surely?
                If you were asked to add an extra plug to a kitchen circuit for example, and while you were installing this you noticed that there were illegal electrics elsewhere, then i am in agreement that you would point this out and tell the owner that you would need to inspect & rectify the rest of the installation in order to issue a CoC, as you could not just walk away knowing that there are illegal connections (even if they are not your own).
                But if the installation is reasonably safe from a visual perspective, then I would only CoC that extra plug that i was asked to install...
                Would you climb in the roof and check for open junction boxes, illegal wiring, etc, after completing your plug install, or would you visually inspect what is around you and make an assessment that what you see is reasonably safe, give your CoC for the plug and leave??
                Just wondering to what extent you need to continue through the installation if the mainboard and kitchen circuit looked legal...
                Thanx for your input.
                Well its there in the regulations, in black and white, unless i'm reading it wrong?
                To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

                Comment

                • Sparks
                  Gold Member

                  • Dec 2009
                  • 909

                  #9
                  That's right, it says in the regulations: "9.(2)(c)(i) the existing part of the electrical installation complies with the general safety principles of such standard and is reasonably safe"
                  This does not imply a full inspection and ensuring that the whole installation complies as per reg 5(1).

                  Comment

                  • Leecatt
                    Silver Member
                    • Jul 2008
                    • 409

                    #10
                    Originally posted by Sparks
                    That's right, it says in the regulations: "9.(2)(c)(i) the existing part of the electrical installation complies with the general safety principles of such standard and is reasonably safe"
                    This does not imply a full inspection and ensuring that the whole installation complies as per reg 5(1).
                    It was explained to me that the only way that you can be sure that the existing installation complies with the general safety principles and is reasonably safe, is to inspect it. I mean that makes sense.
                    Furthermore, I was told that the only way you could prove that the existing installation complies with the general safety principles and is reasonably safe is by issuing a certificate.
                    Look at it this way, the regulation is clear that you will be taking responsibility for the entire installation, that much cannot be disputed, so why not inspect it all, and be sure your not going to end up in court?
                    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

                    Comment

                    • deejaypsy
                      Full Member

                      • Jun 2012
                      • 69

                      #11
                      Originally posted by Leecatt
                      It was explained to me that the only way that you can be sure that the existing installation complies with the general safety principles and is reasonably safe, is to inspect it. I mean that makes sense.
                      Furthermore, I was told that the only way you could prove that the existing installation complies with the general safety principles and is reasonably safe is by issuing a certificate.
                      Look at it this way, the regulation is clear that you will be taking responsibility for the entire installation, that much cannot be disputed, so why not inspect it all, and be sure your not going to end up in court?
                      Could you point out where it states that you will be taking responsibility for the ENTIRE installation if you were to, say, install only 1 extra light point in a 3 storey, 8 bedroom house??
                      Surely this interpretation of yours of the regs (and might i add, that the SA regs leave a lot to personal interpretation) is insane if you figure the costs involved to the client if this were true!
                      1 extra light point to install....R650....Coc for entire installation...couple of grand!!
                      You'd never get any work if you quoted this way!
                      I do understand your way of thinking and interpreting the regs, but it does not make any logical sense to issue a CoC for the entire installation if you are only working on a small part of it!
                      I would like the ECB or ECA to answer this question for us as they would be the guys pointing the finger if it were to go to court would they not??
                      We are not human beings undergoing a spiritual phase.....we are spiritual beings undergoing a human phase....

                      Comment

                      • Sparks
                        Gold Member

                        • Dec 2009
                        • 909

                        #12
                        "Reasonably safe" What is it? This question has been hanging in the air forever. The ELCB trips withing range, all socket oulets are protected, the geyser is earthed, the stove is earthed, all motor circuits have ELCB protection. What else is required to classify an installation as "reasonably safe? Is this a full inspection?

                        Comment

                        • ACEsterhuizen
                          Bronze Member

                          • Mar 2012
                          • 165

                          #13
                          Click image for larger version

Name:	can of worms.jpg
Views:	1
Size:	25.3 KB
ID:	264426

                          It should not be but it is.... I also interpret it the same as Leecat, but in most cases the financial hurdle is massive, and often just not possible.
                          Last edited by ACEsterhuizen; 01-Mar-15, 09:46 AM. Reason: more info

                          Comment

                          • ACEsterhuizen
                            Bronze Member

                            • Mar 2012
                            • 165

                            #14
                            Originally posted by Sparks
                            That's right, it says in the regulations: "9.(2)(c)(i) the existing part of the electrical installation complies with the general safety principles of such standard and is reasonably safe"
                            This does not imply a full inspection and ensuring that the whole installation complies as per reg 5(1).
                            Its true sparks but it does say: " complies with the general safety principles of such standard and is reasonably safe"

                            So firstly it HAS to comply with the general safety principle of such standards (sans 10142 is our standards) and the "general safety principles" are specifically referred to in our standards on page 69 of our regs:

                            "5 Fundamental requirements
                            NOTE This clause contains the general safety principles applicable to electrical
                            installations."

                            Comment

                            • Sparks
                              Gold Member

                              • Dec 2009
                              • 909

                              #15
                              Love the can of worms
                              With a full inspection you are required to throw the book at the installation.
                              To satisfy yourself that it is reasonable safe you are only required to see that there is not any imminent danger through normal daily usage of the installation.
                              Earth continuity readings, for example, to each and every socket outlet are not required if all the plugs are fed from a working ELCB
                              That would classify as "compliance".
                              If "compliance" were the aim "reasonably safe" would be redundant in the regs.